Hello electrically minded forummers! I foolishly today decided to replace an old plastic two way light switch downstairs with a metal flush fitting two way plate and I'm buggered. The two way switch at the bottom of the stairs controls via the left switch the downstairs light and via the right switch the upstairs landing light. The upstairs landing light is also serviced by a single switch upstairs on the landing. What I can't understand is how to wire it correctly to get it working like before.

The back of the new two way switch I have is labelled as such:

SWITCHLAYOUT.jpg


The wires I have coming out of the wall are as follows:

Left hand side: Red Blue Yellow

Right hand side: Black Red

Any ideas chaps?
 
The 2 core cable (red and black) will be for the downstairs light, so you need to connect 1 wire into common (usually the feed) and the other into L1 (usually the switch wire). and for the 2 way for the landing light, connect the red of the 3 core cable inot the commen and the blue and yellow, in L1 or L2 one in each, eg commen red, L1 blue L2 yellow.

Any more questions fire away
 
Last edited by a moderator:
Mark, know what your saying, but that's assuming the upstairs light switch is wired correctly.

Basically, check what colour is in the common upstairs. whatever it is, put the same colour in the common in the switch downstairs, for the two colours that are left, put one in L1 and one in L2. The blue and yellow should have red sleeving/tape on them at both ends

Foe the red and black for the downstairs light, common and L1, like Mark said

job done.

Also in case you werent aware, there should be an earth cable in the switch box, this should be connected to the earth point on the light switch. an earth bond should also be put between this point and the earth point on the switch box (assuming its a metal pattress). This is not strictly required if you have at least one fixed lug in the pattress, but most sparks would do it anyway.
 

Reply to Wiring two way switch in the Canada area at ElectriciansForums.net

Similar Threads

Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
785
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
389
Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
569
Hi All, Would be grateful for some advice. Would like to add an additional light (Undercabinet 8W LED Batten light) to a two-way light switch...
Replies
7
Views
587
Hi everyone. I bought one of those smart switches, specifically the Kasa 3 way kit (HS210 KIT). But when I opened my 3 way dumb switches I see...
Replies
0
Views
616

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock