I have a big place to work on here. Have come across a long lighting circuit where I need to repair/extend damaged end of the circuit. There are 8 PL type Florescent loads distributed evenly.
Due to the (measured & validated) R1+R2, since the circuit is probably ~>60M long in 1.5 T&E, I need to downgrade the ex. MEM C type 10A to a 6A, - and maybe go B type for extra margin. (And TBD fit a MEM RCD pod along with it).
Q) Would B type breaker in your learned opinions be a mistake with 8 off PL type 18W florescent loads (Is it likely to drop out on surge?)
Due to the (measured & validated) R1+R2, since the circuit is probably ~>60M long in 1.5 T&E, I need to downgrade the ex. MEM C type 10A to a 6A, - and maybe go B type for extra margin. (And TBD fit a MEM RCD pod along with it).
Q) Would B type breaker in your learned opinions be a mistake with 8 off PL type 18W florescent loads (Is it likely to drop out on surge?)