What is the point in carrying out zs on TT system other than verifying a loop.
We got an Ra of 14.8 but when all bonding is in place it comes down to 1.9 ohms for most circuits zs results. I just don't see the point if rcd protected .


Assuming this is not a wind up...

Forget the fact this is TT and rethink what a Zs test is for
 
On a 6A lighting circuit max zs is 6 odd ohms to disconnect a fault within specified time . On this TT system with 100mA rcd, our Ze is14 ohms soothe breaker won't trip within time, so relying in rcd.. Oh my god
 
On a 6A lighting circuit max zs is 6 odd ohms to disconnect a fault within specified time . On this TT system with 100mA rcd, our Ze is14 ohms soothe breaker won't trip within time, so relying in rcd.. Oh my god

I hope the 'Oh my god' signifies the end of your blonde moment!
 
I think this is a good question and one that deserves better treatment than most of the answers given so far.

So IMO a value obtained via an earth loop impedance test on a domestic TT installation, is pretty much academic when, as in most cases, an RCD has to be used for earth fault protection.

A measured Zs value usually bears very little resemblance to the equation Zs = Ze + (R1+R2), with Zs values obtained on many TT systems falling within the TN range due to parallel paths etc. So what significance does a Zs measurement have in a domestic TT system when an RCD has to be used for fault protection, apart from confirming the earth loop path is still in place once the installation is “live” and that the installation has good parallel earth paths?

The important bit is obtaining a correctly tested Ra/Ze value and confirming that the equation Ra x I delta n is < or equal to 50V, and that the final circuit R1+R2 values are ok. Although if an Ra/Ze test can’t be carried out, you could use a measured Zs instead of Ra/Ze in the 50V equation above.
 
No glen not have a good go, no no no , support what I am saying.

if you have ze of 14 ohms what is the point of doing zs test , as you know your readings are to high for protective device already.


Brains just ain't your friend last two days guys , AAA?
Note 2 again?
 
I think your missing the point of the question, or perhaps its me.
I thought i=p/u was asking what is the significance of a measured value of Zs on a final circuit in a TT installation. What is the reason for doing it in this instance and is it really necessary if earth fault protection is provided by an RCD and cannot be met within the stated time by an MCB.
 
The answer to ensure the reading is under 1667 or 500 Ohms depending on what RCD is in place. although the RA may be within parameters if the ZS is lets say for argument sake 1000 ohms and the RCD 100 ma then the spark needs to know this?
 
But, this can surely be determined via an acurate Ra measurement and an accurate R1+R2 measurement for each final circuit, at least I think this is what he's getting at.
 
True, however it is just as simple to ZS the circuit as well, that said note 2 of 411.5.1 says "where an RCD is used for for fault protection the circuit should also incorporate an overcurrent protective device in accordance with chapter 43" so if your selecting an overcurrent device then you may well test ZS to see if it would operate under fault conditions, the RCD could fail, if so you are relying on the other protective device. and if that didn't convince you then the schedule of results pages in our EICs or EICRs still have a column for ZS readings, I don't like calculating ZS, I like to test for it myself.
 
Agreed, I like to test it myself too, but an Ra plus R1+R2 of each final circuit will give a more accurate/stable assessment of the earth fault loop impedance and would not include parallel paths which may be removed at some point.
I've had Zs values on TT installs that fall easily within the TN bracket and would suggest that an RCD would not be required to meet disconnection times, but if these parallel paths were to be removed then obviously the tiny earth fault currents would not disconnect at any time. So how significant is a measured Zs in this instance?
 
Of course we also need to remember the regs regarding testing and inspecting circuits and verification of results before handing over a certificate to the customer, another reason to test ZS IMO
 
But Im pretty sure there is no requirement to actually test Zs, it can also be calculated using a measured Ze or Ra and a measured R1+R2 and still be compliant to BS7671.
 

Reply to Zs on TT in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
992
OLDBOY
O
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
471
Anyone come across this before? I was asked to do a Zs on a 3ph surge device; L1 was around 6 ohm, L2 & L3 around 0.11. Wired in singles from a...
Replies
1
Views
426
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock