I'm going to post this as a question rather than a statement as I've not got the regs with me, but aren't we now supposed to be ensuring either a proper TT earthing arrangement, or that the DNO fits a PME in situations where the original earthing arrangement was via the water main?

I believe it used to be classed as ok if the incoming water main was a private supply for x meters outside the property, but I'm pretty sure that this got removed at the last regs updating. I'm partly aware of this because our house is a TT system using the incoming water main as the earth, which was allowed in the regs when I checked a few years back as it was a private supply, but wasn't when I checked again a few months back, so we're now awaiting the DNO to fit a PME.

The reason for the change being the water companies are rapidly going round whole areas replacing the metal pipe with plastic, and the same with the gas, so as soon as they do that the house loses its earth connection. We've come across 2 houses in the last year where this had actually happened in the previous few months, and the Ze readings were well over the limit when we took them even with the bonding connected to water and gas. I'd expect that 90% of that whole estate had actually lost it's earth protection, which we did mention to the DNO, but apparently it's only their problem if they're supplying the earthing arrangements, and it's nobodies problem other than the householders if the original builders didn't pay for a PME connection.

I also thought the bonding to the water and gas pipes was supposed to be disconnected now when taking the Ze readings, presumably to pick up on situations where the water and gas pipes are supplying the earthing.

Happy to be corrected, but I'm pretty sure we double checked the regs on this quite thoroughly.


(fwiw, we're happy enough to leave it as is if the Ze is ok with the water connected, as long as the customer rings the DNO in our presence to arrange for a PME to be installed, but we've had to bang earth spikes in temporarily while waiting for the DNO to come out to fit a PME on the couple of occasions where the pipes had already been done).
 
Ben,

I seem to come across more than my fair share of TT systems where the "rod" is actually the incoming water pipe. Just make sure you can actually inspect the connection - if you can't find it then it's not really BS7671 compliant, regardless of its value. Unless of course it is documented as a maintenance free connection to rod / strip / plate etc..

If it's a new install you've done, then I'd suggest trying to get the reading down a bit. As already stated the NICEIC suggests values >100 Ohms may be unstable. Amazingly this actually agrees with BS7430 (code of practice for earthing) as below:

With I Delta n equal to 30 mA the resistance of the earth connection should not be greater than 100 ohms since a resistance in excess of this value may be unstable and therefore unsuitable.

And don't forget that not all RCDs in a TT install are necessarily rated at 30 mA, so you may need an even lower Ra (or Ze or whatever)

Sorry to correct you, but if an installation has no made earth electrode then you can't class it as a TT system. What your relying on is a bonding connection to an incoming service. If there is no chance of a PME service available from the DNO, then you need to make a made earth electrode, normally by means of a driven rod(s). Stability can usually be achieved by driving at least 2 X coupled 5/8'' rods to give you the depth. This will also in most cases give you a far superior Ra value than those given in BS7671 and BS7430...

Both 200 ohm and 100 ohm Ra values are pretty useless as far as providing any form of protection to a TT system, which is the main reason for the requirement of RCD devices on TT systems. Unfortunately RCD's are not the most reliable of protection devices. So i would always recommend the addition of a 100mA S type up-front unit (maybe as your main switch in a CU) as a back-up for a failed or faulty RCD/RCBO....
 
As Far as I am aware you can still use a private water supply pipe as an earth with the permission of the supply owner, the operative word here is PRIVATE, ie. as in not public , for the reasons you correctly state, gas has never, at least as far back as the 16thed. (may be earlier) been allowed for this purpose.
 
you could define it as you like, ze zs depends on where in the system you are, at origin, one sub main is a zs of another, which becomes a ze of another, on most paper work ra is the earth rod with the main earthing conductor, on its own. legal limit 200ohms. But i know in many places this can not be achived, most rcd's guarantee, they will operate at 1000 ohms
what happened to Zdb then?
 
you could define it as you like, ze zs depends on where in the system you are, at origin, one sub main is a zs of another, which becomes a ze of another, on most paper work ra is the earth rod with the main earthing conductor, on its own. legal limit 200ohms. But i know in many places this can not be achived, most rcd's guarantee, they will operate at 1000 ohms

If you can't achieve an Ra of 200 ohms, ...then something has to be very wrong!! lol!!!
 
As Far as I am aware you can still use a private water supply pipe as an earth with the permission of the supply owner, the operative word here is PRIVATE, ie. as in not public , for the reasons you correctly state, gas has never, at least as far back as the 16thed. (may be earlier) been allowed for this purpose.
I believe it changed in the last year or so, probably when the 17th edition update happened.

I had to check the 2 different versions of 17th to know that it had changed though IIRC, which I only did because it impacted on my house, and I knew for a fact that it used to be allowed.

I'll see if I get time to check though, as this is going to bug me now if I don't.
 
Doesn't really matter if it is still allowed or not, you can't in all honesty say that an installation relying on what is a bonding connection, is a TT system. A TT system requires a made electrode, be it by means of a rod, plate, Ufer, or other made electrode type...
 
I've just checked, and it's not changed at all - thinking about it, I think I have one of my electricians 17th edition update course to thank for thinking it had changed.

It does have a bit about precautions needing to be taken against it's removal, but I'd think this would be covered by the usual warning tag, so as long as that's in place I'd think it would be fine still.

sorry for questioning people on this.
 

Reply to Zs testing on TT in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
971
OLDBOY
O
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
843

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock