Job - semi detached with a TT earthing arrangement.
I used the Z loop function on my MFT to check the earth at the DB. Reading 164 ohms - ok.
Same reading with earth reconnected.
However if I do the same test with the Zs RCD function, I get 204 ohms. Why? Do I have a MFT fault?
I need to use this function when testing individual circuits because the main switch is a 30mA RCD.
So far I've only had time to check the calibration sheets (all fine) and to do the same measurements on a TNC-S circuit, where both readings were the same (0.23 ohms).
Do I need to check the tester with a 200 ohm resistor or is there an obvious reason for the discrepency?
Cheers
Pete