Hi could someone please explain why you cant export a PME over 20 metres?

And what are the dangers of doing so?

Cheers

harry98 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 19-05-2008   #2 (permalink)
wayne
Respected Member
 
Join Date: Feb 2008
Posts: 918
View wayne's Photo Album
Default Re: Exporting PME

where does that come from? i ask out of genuine curiosity ?
wayne is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 21-05-2008   #3 (permalink)
harry98
Junior Member
 
Join Date: Apr 2008
Posts: 15
View harry98's Photo Album
Default Re: Exporting PME

I got told of someone that you cant export PME over 20 metres, so say if you had a garden shed 50 metres away you would have to put a TT earthing system in.

The question is though, how come?

Cheers
harry98 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 24-05-2008   #4 (permalink)
Jurassic Spark
Member
 
Join Date: Apr 2008
Posts: 71
View Jurassic Spark's Photo Album
Default Re: Exporting PME

You can export a PME supply to an outbuilding providing that the outbuilding in question has no structural steel metalwork. If it has, a TT supply feeding an RCD protected CU is required, all structural steel is to be bonded and an earth rod installed. The danger with PME is if the neutral conductor fails, extraneous metalwork is used as the return path for the supply.
Jurassic Spark is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 24-05-2008   #5 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: Exporting PME

Quote:
Originally Posted by Jurassic Spark View Post
You can export a PME supply to an outbuilding providing that the outbuilding in question has no structural steel metalwork. If it has, a TT supply feeding an RCD protected CU is required, all structural steel is to be bonded and an earth rod installed. The danger with PME is if the neutral conductor fails, extraneous metalwork is used as the return path for the supply.
i agree,

By structural steel he is of course talking about any extraneous conductive path, which would typically be structural steel or an incoming water supply

If you are going under ground and using SWA, connect the armour at the supply end only

not sure about the RCD though, if you are coming ioff an RCD protected supply anyway you shouldnt put one in the garage (unless you are going to discriminate)

If coming straight of a NON RCD protected MCB then yes put one in the garage

Never heard of the distance before, I have always considered the presence of extraneos conductive paths as the deciding factor as to whether or not to export
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 24-05-2008   #6 (permalink)
Jurassic Spark
Member
 
Join Date: Apr 2008
Posts: 71
View Jurassic Spark's Photo Album
Default Re: Exporting PME

Hi Shakey. If the supply to an outbuilding is going to be TN-S, then I'd put the RCD at the supply end because you'd have a continuous earth from the house to the outbuilding via the armouring and maybe a spare cable conductor. If the supply is PME and you're not connecting the armouring at the outbuilding, the RCD wouldn't work as they'd be no return earth path for fault current. Provided that you can guarantee a disconnection time of 0.4s or less, the cable can be protected by an MCB.
Jurassic Spark is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 25-05-2008   #7 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: Exporting PME

Quote:
Originally Posted by Jurassic Spark View Post
Hi Shakey. If the supply to an outbuilding is going to be TN-S, then I'd put the RCD at the supply end because you'd have a continuous earth from the house to the outbuilding via the armouring and maybe a spare cable conductor. If the supply is PME and you're not connecting the armouring at the outbuilding, the RCD wouldn't work as they'd be no return earth path for fault current. Provided that you can guarantee a disconnection time of 0.4s or less, the cable can be protected by an MCB.
sorry, hate to say you are wrong, but you are wrong

If you have made the garage into a TT, and its less than 1667 ohms, the RCD in the house just sees an imbalabce between line and neutral, and trips off

The fact that the fault current flows to earth through the electrode in the garage is irrelelvent to the RCD
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 25-05-2008   #8 (permalink)
harry98
Junior Member
 
Join Date: Apr 2008
Posts: 15
View harry98's Photo Album
Default Re: Exporting PME

So if you have to TT an outbuilding that has structural steel why dont you have to TT any building that has structural steel?

Cheers
harry98 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 25-05-2008   #9 (permalink)
Had8Lives
Member
 
Join Date: Apr 2008
Posts: 54
View Had8Lives's Photo Album
Default Re: Exporting PME

Any steel structure should be bonded to the main earth, if the PME supply is within the Structural steel buliding then there's no need for an extra earth :-O
Had8Lives is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 26-05-2008   #10 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: Exporting PME

like the man said, we are within the equipotential zone, we are talking about exporting outside the zone

 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Running PME (TNCS) outdoors? TheFullHitSpark General Electrical Discussion 18 25-10-2008 09:46 AM
PIR Industrial units, Extended PME. skiandy Wiring, Theories and the Regulations 4 24-09-2008 08:22 AM
Advice: Mix of 1 and 3 phase on PME the-moog General Electrical Discussion 2 04-09-2008 11:00 AM

Google Search
Google

All times are GMT +1. The time now is 11:23 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38