Quote:
Originally Posted by Jurassic Spark You can export a PME supply to an outbuilding providing that the outbuilding in question has no structural steel metalwork. If it has, a TT supply feeding an RCD protected CU is required, all structural steel is to be bonded and an earth rod installed. The danger with PME is if the neutral conductor fails, extraneous metalwork is used as the return path for the supply. |
i agree,
By structural steel he is of course talking about any extraneous conductive path, which would typically be structural steel or an incoming water supply
If you are going under ground and using SWA, connect the armour at the supply end only
not sure about the RCD though, if you are coming ioff an RCD protected supply anyway you shouldnt put one in the garage (unless you are going to discriminate)
If coming straight of a NON RCD protected MCB then yes put one in the garage
Never heard of the distance before, I have always considered the presence of extraneos conductive paths as the deciding factor as to whether or not to export