Electrical Forum - Electricians Forum - Electrical Talk - Electrical Courses - Electricians Training - Electrical Knowledge

Go Back   Electricians Forum | Electrical Forum | An electrical forum for electricians in the UK > General Electrical Forum Topics > Wiring, Theories and the Regulations
Forgot Password? Join Us!

Wiring, Theories and the Regulations Discussions on all electrical regulations in the UK. Including Part P, BS 7671, DPC BS7671:2008, BS 7671:2001 & 2004 Amendment No.2, IEE wiring regulations, 16th Edition and 17th Edition

Reply
 
LinkBack Thread Tools Display Modes
Old 05-06-2008   #1 (permalink)
YTSOxford
Junior Member
 
Join Date: Jun 2008
Posts: 24
View YTSOxford's Photo Album
Default wiring in stud walls...1st fix

have just taken my 17th regs the other day and have passed. That along with the Part P makes me now a 'domestic installer'. Thing is, I'm lacking on the practical side of the trade.

Does anyone know where the cables in studwork should be according to the 17th. I seem to remember from the course that the recommended that the cable have one side touching the plasterboard, running vertical from outlets. Something to do with the insulation affecting the wire temp. SO if I was to do this how would you move between the studwork horizontally, to other sockets?? wouldn't be notches surely??

YTSOxford is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 05-06-2008   #2 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: wiring in stud walls...1st fix

well the studwork is vertical, so if you want to go horizontal, you just drill the middle of any stud that you hit

I always run cables dowwn the centre of any noggins, why would you want it touching the plasterboard?
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 05-06-2008   #3 (permalink)
PAUL M
Respected Member
 
Join Date: May 2008
Posts: 505
View PAUL M's Photo Album
Default Re: wiring in stud walls...1st fix

have you passed the assesment process through nic,napit or elecsa yet.
PAUL M is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 06-06-2008   #4 (permalink)
conspiracy jews
Junior Member
 
Join Date: Jun 2008
Posts: 4
View conspiracy jews's Photo Album
Default Re: wiring in stud walls...1st fix

lol wtf, how old are you? your not anything like a 'domestic installer' & part p means **** all to a spark, its for kitchen & bathroom fitters. Its people like you who give time served sparks a bad name, you roll into a few weeks course and think ur a spark. makes me lol. hope ur being supervised too
conspiracy jews is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 06-06-2008   #5 (permalink)
YTSOxford
Junior Member
 
Join Date: Jun 2008
Posts: 24
View YTSOxford's Photo Album
Default Re: wiring in stud walls...1st fix

lol, right i can see this is the type of forum I have to keep checking back as to nopt get slated by the likes of the last person. Lets get the imature comments with out the way. I'm 26, and have been in the construction trade since 18. I took Alevels and realised Uni was a pointless route and since I have wife and kid, had to start earning some decent cash. Since times are getting harder I decided to reskill and as much as I respect the peiople who have taken the college and apprentice route, but I can't take years out of work...did I mention wife and kid???

The company I work for just do extensions and that is all i need to kno how to wire. I KNOW i'm by no means competent yet, as I have the qualifications and not the experience. SO I 'm trying to obtain knowledge on forums such as this and applying to local contractors to be electricians mate.

Paul, I am planning to apply for the 'happy clubs' as soon as I feel confident, so far its the building control route.

And with REGARDS TO MY Q, the reg is 523.7 in the 17th ed, and the reference method that i was wondering whether i should and how to achieve is 102. iuts to do with cables having a derating factor when totaly surrounded by insulation, which they would if 50mm in. where should i run them? Or am I looking into this too far? help appreciated
YTSOxford is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 06-06-2008   #6 (permalink)
PAUL M
Respected Member
 
Join Date: May 2008
Posts: 505
View PAUL M's Photo Album
Default Re: wiring in stud walls...1st fix

Best Of Luck With Building Control,been There Got The T Shirt Not A Pleasant Though Expensive Experience, If I Where You I Would Join One Of The "happy Clubs" As You Put It Asap.
PAUL M is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 06-06-2008   #7 (permalink)
Cirrus
Guest
 
Posts: n/a
View Cirrus's Photo Album
Default Re: wiring in stud walls...1st fix

Right, YTSoxford, I can assure you that this is NOT like other forums. We have a laugh and a joke and may rib each other, but the forum will not allow direct insults to be thrown by members so on that you can rely.
People will always have a difference of opinion when it comes to 'qualifications' so just take it with a pinch of salt. We all work in the trade and most of us enjoy what we do. Nothing gives anyone the right to shout down an electrician who just decides to fit kitchens for example. Why does this make them 'lower' down in the pecking order? I know sparks earning a grand a week every week just doing kitchens. Bet there are a lot of sparks who have been in the industry 30 years who can't make that sort of money in their working week.

You will find most of us on this forum to be helpful YTSoxford so my advice - ask away as you have been mate

Last edited by Cirrus; 06-06-2008 at 08:05 PM. Reason: typo
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 07-06-2008   #8 (permalink)
Spudmiester
Senior Member
 
Spudmiester's Avatar
 
Join Date: Mar 2008
Location: Yorkshire
Posts: 330
View Spudmiester's Photo Album
Default Re: wiring in stud walls...1st fix

Yes, we are not a bad bunch realy , but watch out for that Shakey guy !
Spudmiester is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 07-06-2008   #9 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: wiring in stud walls...1st fix

Quote:
Originally Posted by Spudmiester View Post
Yes, we are not a bad bunch realy , but watch out for that Shakey guy !
what have i done!!!!!!!!!

Quote:
Originally Posted by conspiracy jews View Post
lol wtf, how old are you? your not anything like a 'domestic installer' & part p means **** all to a spark, its for kitchen & bathroom fitters. Its people like you who give time served sparks a bad name, you roll into a few weeks course and think ur a spark. makes me lol. hope ur being supervised too
could you be any more ignorant and ill informed?

1. yes he is a domestic installer

2. If part p means nothing to you mate you should not be in this trade. Even if you only work industrial, you would have to know the requirements of Part P to know that they dont apply to you. If you work commercial, and did shops, pubs, resteraunts or anything with a domestic dwelling attatched then you could well fall under the auspices of Part P

3. It is NOT just for kitchen and bathrrom fitters. i am in the middle of teaching the EAL course at the moment. Got a guy sitting in front of me thats got 6 or 7 years experience as a mate, learnt all his stuff off his dad, who has been a spark since the year dot. He has no quals, but fu*k me can that boy throw cables on the wall. Kitchen and bathroom fitter? I would watch bemused as he buried a hammer in your head.

4. The chap who started this post never said he was a spark! He said was a domestic installer. READ THE POST. And what do you think a 'spark' is then sunshine? 'cos i dont have ANY installation quals, and people have said i am not a 'spark'. Still got 25 years experience and teach EAL, C&G 2377, 2381, 2382, 2391 & 2392 though

fancy going toe to toe on any 'spark' issues big man

bring it on

Last edited by Shakey; 07-06-2008 at 11:13 AM. Reason: Automerged Doublepost
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 07-06-2008   #10 (permalink)
Spudmiester
Senior Member
 
Spudmiester's Avatar
 
Join Date: Mar 2008
Location: Yorkshire
Posts: 330
View Spudmiester's Photo Album
Default Re: wiring in stud walls...1st fix

Just a joke Shakey, was going to put a smiley on but clicked wrong bit !

Spudmiester is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Y plan wiring help needed flying lee General Electrical Discussion 5 12-09-2008 11:25 PM
2nd fix charges AJ16 General Electrical Discussion 11 09-02-2008 07:54 PM

Google Search
Google

All times are GMT +1. The time now is 07:00 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38