Electrical Forum - Electricians Forum - Electrical Talk - Electrical Courses - Electricians Training - Electrical Knowledge

Go Back   Electricians Forum | Electrical Forum | An electrical forum for electricians in the UK > General Electrical Forum Topics > Wiring, Theories and the Regulations
Forgot Password? Join Us!

Wiring, Theories and the Regulations Discussions on all electrical regulations in the UK. Including Part P, BS 7671, DPC BS7671:2008, BS 7671:2001 & 2004 Amendment No.2, IEE wiring regulations, 16th Edition and 17th Edition

Reply
 
LinkBack Thread Tools Display Modes
Old 10-06-2008   #11 (permalink)
jeremy
Junior Member
 
Join Date: Jun 2008
Posts: 28
View jeremy's Photo Album
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

Tr25 you say he has done his 17th, 17TH what ??Joint before Breakfast!! (and I'm not talking crimped)Anything without an earth return becomes a special location that is not allowed under normal circumstances, ie domestic installations
jeremy is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 10-06-2008   #12 (permalink)
ThrownRazor25
Junior Member
 
Join Date: Feb 2008
Posts: 11
View ThrownRazor25's Photo Album
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

Listen mate im on your side lol.Hes a wee know it all twat who has done a 17th course and is spouting out all this crap all the time.trouble is he is so sincere about it half the guys at work are starting to believe him.He is adamant the new regs say that if the board is protected by an rcd or if individual circuits all have rcbos then there is no need for an earth because the rcd/rcbo will operate on the imbalance of live and neutral.
ThrownRazor25 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 10-06-2008   #13 (permalink)
Shakey
Respected Member
 
Join Date: Feb 2008
Posts: 1,045
View Shakey's Photo Album
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

Quote:
Originally Posted by ThrownRazor25 View Post
Listen mate im on your side lol.Hes a wee know it all twat who has done a 17th course and is spouting out all this crap all the time.trouble is he is so sincere about it half the guys at work are starting to believe him.He is adamant the new regs say that if the board is protected by an rcd or if individual circuits all have rcbos then there is no need for an earth because the rcd/rcbo will operate on the imbalance of live and neutral.
ok, I have explained how an RCD COULD work without an incoming earth with an extraneous path of 7666 ohms or less (but probably not in the required time), but that is an accidental by-product of there being no earth in the first place

How the hell does this guy think ADS will be achieved

I teach 17th edition, and this guy is talking utter tosh

he has no doubt misenterpreted something he was told on the course

along the lines of RCD protected circuits only needing a Zs of 1667 ohms or less for their 60898 MCB's etc etc

If you want to 'douse his flames' a little, ask him for the relevant regs numbers to back up his 'theories'
Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 11-06-2008   #14 (permalink)
Moog
Member
 
Join Date: May 2008
Location: midlands
Posts: 72
View Moog's Photo Album
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

Quote:
Originally Posted by LScotty View Post
correct me if i am wrong here, but its not that they detect the earth leakage persay, but of an imbalance of the neutral and line, due to current flowing via earth... ?

Luke
I agree it will trip if the phase and neutral currents are not the same, however I would not sign off an installation without an adequate earth path unless it was SELV for instance You sure this guy isn't on about bonding? not done my 17th conversion yet but there was take about there not being a requirement for bonding in bathrooms anymore

Last edited by Moog; 11-06-2008 at 04:40 AM.
Moog is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 11-06-2008   #15 (permalink)
Shakey
Respected Member
 
Join Date: Feb 2008
Posts: 1,045
View Shakey's Photo Album
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

Quote:
Originally Posted by Moog View Post
I agree it will trip if the phase and neutral currents are not the same, however I would not sign off an installation without an adequate earth path unless it was SELV for instance You sure this guy isn't on about bonding? not done my 17th conversion yet but there was take about there not being a requirement for bonding in bathrooms anymore
bit more complicated than that Moog, for bathrooms, but yeah, if all conditions are met, then no supplementary
Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 11-06-2008   #16 (permalink)
WarrenG
Junior Member
 
Join Date: Jun 2008
Posts: 7
View WarrenG's Photo Album
Exclamation Re: Help!!!!!!!!!!!!!!!!!!!!!!!

O.K. it seems that there is some agreement on the workings of an RCD on this post.

An RCD protects by constantly monitoring the current flowing in the live and neutral wires supplying a circuit or an individual item of equipment.

The supply and the load are both connected to EARTH

Under normal circumstances, the current flowing in the two wires is equal. When an earth leakage occurs due to a fault in the circuit or an accident with the equipment, an imbalance occurs and this is detected by the RCD, which automatically cuts off the power before injury or damage can result.

If there is an imbalance in a circuit protected by the RCD, the leakage current has got to be going somewhere. If there is no earth path to take the current to earth, what is going to take it there? a person who recieves a shock from live metal work?

I think your friend should study the 16th Edition before trying the 17th Edition.
WarrenG is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 12-06-2008   #17 (permalink)
Shakey
Respected Member
 
Join Date: Feb 2008
Posts: 1,045
View Shakey's Photo Album
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

Like I said Warren, there may be an 'accidental' earth path through any extraneous paths, which, if 7666 ohms or less, would still allow the RCD to trip, but it is most defintely NOT in the 17th that you dont need an inscoming earth because of it
Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 14-06-2008   #18 (permalink)
Had8Lives
Member
 
Join Date: Apr 2008
Posts: 48
View Had8Lives's Photo Album
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

I think your mate is confusing a Main supply earth and equipotential bonding. The 17th does not require you to install equipotential bonding to pipes such as a bath room basin as long as the circuits in the bathroom are protected by an RCD. Every installation must have a main earth.

Sorry, meant supplimentary bonding not equipotential.

Last edited by Had8Lives; 14-06-2008 at 09:40 PM. Reason: Automerged Doublepost
Had8Lives is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 26-06-2008   #19 (permalink)
wattsup
Senior Member
 
Join Date: Jun 2008
Posts: 142
View wattsup's Photo Album
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

Perhaps it's a double insulated house
wattsup is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 3 Weeks Ago   #20 (permalink)
alancp
Junior Member
 
Join Date: Jun 2008
Posts: 14
View alancp's Photo Album
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

shakey, i understand about the 1667 ohms bit, but, shouldnt it be lower than that (exact figure not known at mo) to do away with an unreliable earth path??

alancp is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Google Search
Google

All times are GMT +1. The time now is 05:22 AM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

Note: this was added 27/02/08 and will improve with time.
External Links: Adverse Credit Remortgage : Remortgages : Credit Card : Web Advertising : Car Loan

COMMUNITY SPONSORS

 Electrical Courses
Electrical Courses by Trade Skills 4U Electrical Training

Electrical Forum
Electrical Courses by Access Training Wales

Electrical Forum Sponsorship

SPONSORS WANTED

Our sponsors keep the forum free to use, please click their banners (above) and use the sponsors when you can. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference
Tiler News
Tiling Training
Tile Cutters
Tile Network
Plumbing Forum
Conservatory Suppliers
Tile Forum
Search Engine Optimisation
Tile Pages



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31