Old 14-08-2008   #21 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

Quote:
Originally Posted by alancp View Post
shakey, i understand about the 1667 ohms bit, but, shouldnt it be lower than that (exact figure not known at mo) to do away with an unreliable earth path??
depends what you mean by 'do away with'

No value would allow you to do away with an unreliable earth

Or are you refering to the value of 200 ohms for TT earth electrodes?

This is the max value at which it could be condidered a 'stable reading', but is not a max value as far as the RCD is concerned

there is no 'leeway' for an unreliable earth
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 15-08-2008   #22 (permalink)
Dinosaur
Member
 
Join Date: Jul 2008
Posts: 64
View Dinosaur's Photo Album
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

No Earth path - No electric shock???????????
Dinosaur is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 15-08-2008   #23 (permalink)
tony.towa
Respected Member
 
tony.towa's Avatar
 
Join Date: Jul 2008
Location: Warwickshire
Posts: 539
View tony.towa's Photo Album
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

Technically an RCD will operate without any form of earth path being installed. It operates. as stated in other answers, by monitoring the phase and neutral and reacting to an imbalance between them. Normally this imbalance is as a result of an "earth fault" be it to a back box, cpc, or as a result of external influences like moisture. It is possible to have a created imbalance, for example where wall lights have been installed and the live is taken from the lighting circuit and the neutral is taken from a socket on the final ring circuit protected by an RCD (16th edition style split load board with protected and unprotected ways). By switching the wall lights on an imbalance is created on the final ring circuit which will trip the RCD. Whilst not a common fault it is a typical "lash up" job by a "Barry the Bodger".
tony.towa is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 16-08-2008   #24 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

Quote:
Originally Posted by tony.towa View Post
Technically an RCD will operate without any form of earth path being installed. It operates. as stated in other answers, by monitoring the phase and neutral and reacting to an imbalance between them. Normally this imbalance is as a result of an "earth fault" be it to a back box, cpc, or as a result of external influences like moisture. It is possible to have a created imbalance, for example where wall lights have been installed and the live is taken from the lighting circuit and the neutral is taken from a socket on the final ring circuit protected by an RCD (16th edition style split load board with protected and unprotected ways). By switching the wall lights on an imbalance is created on the final ring circuit which will trip the RCD. Whilst not a common fault it is a typical "lash up" job by a "Barry the Bodger".
yup, done a few like that Tony

"just installed a new circuit, RCD trips as soon as i switch it on"

Investigation finds that the guy didnt know there was seperate neutral bars

Doh!
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 16-08-2008   #25 (permalink)
greekislandlover
Senior Member
 
Join Date: Jun 2008
Posts: 134
View greekislandlover's Photo Album
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

Not sure certain CU manufacturers are aware of this fact either! I've found several new CU's to have the neutrals connected arbitrarily to whatever bar suits at the time of manufacturer.
greekislandlover is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 24-08-2008   #26 (permalink)
Carter
Senior Member
 
Carter's Avatar
 
Join Date: Aug 2008
Posts: 171
View Carter's Photo Album
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

Modern (current controlled) RCDs make the assumption that any imbalance in line and neutral currents must be flowing to earth (because generally there isn't anywhere else for it to go) they don't actually measure anything with reference to the main or cct cpc's. However it still doesn't remove the fact an earth path must be present or there would be no residual current and the device would not operate.
I think the older voltage controlled ELCBs sensed voltage on the cpc but they were effectively proscribed in 1981 as it was realised that a parallel earth path would render them inoperable under true fault conditons.

Ask your man to draw out the FULL fault path and ask him were exactly does he thinks that inconvenient stray, 'residual' "I delta n" tripping current is going.
Carter is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 16-09-2008   #27 (permalink)
weyboy
Junior Member
 
weyboy's Avatar
 
Join Date: Sep 2008
Posts: 12
View weyboy's Photo Album
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

Quote:
Originally Posted by ThrownRazor25 View Post
Hiya guys will an RCD or RCBO work if there is no earth in the house?A fellow worker said to me today that there is no need for an earth in a house if the board has an RCD or is controlled by RCBOs as they work on the inbalance of the live and neutral.

what about disconnection times?

weyboy is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Google Search
Google

All times are GMT +1. The time now is 09:41 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38