Old 09-06-2008   #1 (permalink)
ThrownRazor25
Junior Member
 
Join Date: Feb 2008
Posts: 11
View ThrownRazor25's Photo Album
Default Help!!!!!!!!!!!!!!!!!!!!!!!

Hiya guys will an RCD or RCBO work if there is no earth in the house?A fellow worker said to me today that there is no need for an earth in a house if the board has an RCD or is controlled by RCBOs as they work on the inbalance of the live and neutral.

ThrownRazor25 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-06-2008   #2 (permalink)
PAUL M
Senior Member
 
Join Date: May 2008
Location: dudley
Posts: 210
View PAUL M's Photo Album
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

Tell Your Mate He Is Talking Out His Ass,of Course You Have To Have An Earth,they Work By Detecting Earth Leakage.
PAUL M is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-06-2008   #3 (permalink)
ThrownRazor25
Junior Member
 
Join Date: Feb 2008
Posts: 11
View ThrownRazor25's Photo Album
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

Thats what i said to him bud but he was adamant cause he had done his 17th and ive no i started questioning myself.
ThrownRazor25 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-06-2008   #4 (permalink)
danzor
Senior Member
 
danzor's Avatar
 
Join Date: Feb 2008
Posts: 191
View danzor's Photo Album
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

I would question his 17th qual
danzor is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-06-2008   #5 (permalink)
Cirrus
Moderator
 
Cirrus's Avatar
 
Join Date: Sep 2007
Posts: 1,081
View Cirrus's Photo Album
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

Or any quals!!!
Cirrus is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-06-2008   #6 (permalink)
wayne
Respected Member
 
wayne's Avatar
 
Join Date: Feb 2008
Posts: 725
View wayne's Photo Album
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

the guy has the half baked opinion that sends us to the text boooks to check
wayne is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-06-2008   #7 (permalink)
LukeScotty
Administrator
 
LukeScotty's Avatar
 
Join Date: Jul 2007
Location: South Yorkshire
Posts: 568
View LukeScotty's Photo Album Send a message via MSN to LukeScotty
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

Quote:
Originally Posted by PAUL M View Post
Tell Your Mate He Is Talking Out His Ass,of Course You Have To Have An Earth,they Work By Detecting Earth Leakage.
correct me if i am wrong here, but its not that they detect the earth leakage persay, but of an imbalance of the neutral and line, due to current flowing via earth... ?

Luke

If You Build It, They Will Come!!!!!
LukeScotty is online now  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 10-06-2008   #8 (permalink)
MacSparky
Senior Member
 
MacSparky's Avatar
 
Join Date: Feb 2008
Posts: 115
View MacSparky's Photo Album
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

why do you need a seperate earth to make rcd,s and rcbo's work? an rcd will actuate at around 22-30 milliamps, either of the phase conductors could come loose and touch exposed metal work which would allow the cpd to work,(connected to cpc or not),..... surely as scotty mentioned its a minute inbalance that would trip them....earth leakage that is. Non rcd/rcbo cpd's would require cpc for sure. Hope i'm not missing the point here

Get off my planet...
http://www.mysportydate.com/

Last edited by MacSparky; 10-06-2008 at 08:38 AM.
MacSparky is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 10-06-2008   #9 (permalink)
Shakey
Senior Member
 
Join Date: Feb 2008
Posts: 1,028
View Shakey's Photo Album
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

everyone is a bit right - and some are a bit wrong here.

An RCD does not need an Earth per se, but needs an EARTH PATH

it is quite conceivable to have a house with no incoming earth, but there would be an alternaive path though the CPC to the MET, through the protective bonding and down to earth though any extraneous conductive paths (gas, water pipes etc)

as long as that path is 1667 ohms or less, the RCD would trip before the fault voltage reached the magical 50V, and even with a path of 7666 ohms or less would still trip.

Of course we need an earth path for CPD's to work correctly, but an RCD, with ANY path to earth as stated above, will trip off

and before anyone starts thumping the keyboard, I am NOT suggesting using an RCD means you dont have to have an incoming earth
Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 10-06-2008   #10 (permalink)
PAUL M
Senior Member
 
Join Date: May 2008
Location: dudley
Posts: 210
View PAUL M's Photo Album
Default Re: Help!!!!!!!!!!!!!!!!!!!!!!!

Quote:
Originally Posted by LScotty View Post
correct me if i am wrong here, but its not that they detect the earth leakage persay, but of an imbalance of the neutral and line, due to current flowing via earth... ?

Luke
yes i know that but if there no earth path what then.

PAUL M is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Google Search
Google

All times are GMT +1. The time now is 08:05 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

Note: this was added 27/02/08 and will improve with time.
External Links: Car Insurance : Hotels : Loans : Secured Loan : Sport Betting Systems

COMMUNITY SPONSORS

 Electrical Courses
Electrical Courses by Trade Skills 4U Electrical Training

Electrical Forum
Electrical Courses by Access Training Wales

Electrical Forum Sponsorship

SPONSORS WANTED

Our sponsors keep the forum free to use, please click their banners (above) and use the sponsors when you can. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference
Tiler News
Tiling Training
Tile Cutters
Tile Network
Plumbing Forum
Conservatory Suppliers
Tile Forum
Search Engine Optimisation
Tile Pages



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28