Default 17th edition board TT system high integrity board what size RCD front End?

What size Rcd should you use as main switch for a high integrity board on a 17th installation. 16th was a 100mA type S, could you use a 300mA RCD without the delay?
I understand if you use a split 17th edition board you don't need a front end RCD...

electro is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 21-06-2008   #2 (permalink)
Shakey
Senior Member
 
Join Date: Feb 2008
Posts: 1,027
View Shakey's Photo Album
Default Re: 17th edition board TT system high integrity board what size RCD front End?

Quote:
Originally Posted by electro View Post
What size Rcd should you use as main switch for a high integrity board on a 17th installation. 16th was a 100mA type S, could you use a 300mA RCD without the delay?
I understand if you use a split 17th edition board you don't need a front end RCD...
well if you installing to the 17th, assuming buried cables, socket outlets, bathrooms etc, then use use twin or triple 30mA RCD's, you wont need a front end RCD

the 30mA will provide additional protection and protection against fire

interesting how theres no mention of it in the 17th, cant wait for the OSG to come out!
Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 21-06-2008   #3 (permalink)
electro
Junior Member
 
Join Date: Apr 2008
Posts: 11
View electro's Photo Album
Default Re: 17th edition board TT system high integrity board what size RCD front End?

Hi shakey
I'm using is a high integrity board which allows three circuits to be none RCD which leads me to think it needs a RCD main switch. The high integrity board I'm using is 3 none RCD and 5+5 RCD.


regards
electro is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 21-06-2008   #4 (permalink)
Shakey
Senior Member
 
Join Date: Feb 2008
Posts: 1,027
View Shakey's Photo Album
Default Re: 17th edition board TT system high integrity board what size RCD front End?

what is a 'high integrity' board?

anyway, just treat every circuit as a normal circuit, regardless of it being a TT

if a circuit requires 30ma, because its got buried cables, socket outlets, or bathroom, then it needs 30mA, TT has nothing to do with it

so the non rcd protected ways can either be for surface mount cables (or protected cables), and if they still meet their disconnection times then you are ok, if not, just RCBO's

you should do this for your smokes anyway, unless you are gonna surface mount/ or put you lights and smokes on a seprate RCD to the sockets
Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 21-06-2008   #5 (permalink)
electro
Junior Member
 
Join Date: Apr 2008
Posts: 11
View electro's Photo Album
Default Re: 17th edition board TT system high integrity board what size RCD front End?

we have some medical equipment in bedrooms that we dont want on rcds. i think that part of the system should be protected against fire on a TT system?
electro is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 21-06-2008   #6 (permalink)
Shakey
Senior Member
 
Join Date: Feb 2008
Posts: 1,027
View Shakey's Photo Album
Default Re: 17th edition board TT system high integrity board what size RCD front End?

Quote:
Originally Posted by electro View Post
we have some medical equipment in bedrooms that we dont want on rcds. i think that part of the system should be protected against fire on a TT system?
yes it shoulf be protected against fire, which under the 16th was a 100mA RCd (s type if main switch), under the 17th its up to 300mA, but either way, it means an RCD, so the stuff in the bedrooms WOULD be an RCD

do the circtuits meet their disconnection times - I have worked on TT's with very low Ze (only a couple of ohms), so things like the lighting circuits still comply
, but if the Zs is too high (because of the earth spike) then you have no choice but to RCD it
Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 21-06-2008   #7 (permalink)
electro
Junior Member
 
Join Date: Apr 2008
Posts: 11
View electro's Photo Album
Default Re: 17th edition board TT system high integrity board what size RCD front End?

Nice one shakey thanks for your info. just one last question does the 300mA have to be a delay type to meet the discrimination from the 30mA downstream RCDs
electro is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 22-06-2008   #8 (permalink)
Shakey
Senior Member
 
Join Date: Feb 2008
Posts: 1,027
View Shakey's Photo Album
Default Re: 17th edition board TT system high integrity board what size RCD front End?

it would have to be a time delay if used as the main switch

Shakey is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Google Search
Google

All times are GMT +1. The time now is 05:55 AM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

Note: this was added 27/02/08 and will improve with time.
External Links: New York Hotels : Hotels : Loans : Mortgages : Debt Consolidation

COMMUNITY SPONSORS

 Electrical Courses
Electrical Courses by Trade Skills 4U Electrical Training

Electrical Forum
Electrical Courses by Access Training Wales

Electrical Forum Sponsorship

SPONSORS WANTED

Our sponsors keep the forum free to use, please click their banners (above) and use the sponsors when you can. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference
Tiler News
Tiling Training
Tile Cutters
Tile Network
Plumbing Forum
Conservatory Suppliers
Tile Forum
Search Engine Optimisation
Tile Pages



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29