Default Question about sharing Neutral..

Hi All, Just registered here as I have a question about the installation of an electrical oven.

I am now living overseas, but the principle is pretty much the same as in the UK.

I have recently laid 2 x 3x2.5mm cables for the installation of a new oven with induction hob. As I believed both units connected to a normal 3-phase oven connection. (I had no 5x2.5mm available)

Now it turns out, that the induction plate, has a normal 3 phase connection, but the Oven itself requires a seperate normal plug socket.

so I have 6 x 2,5mm wires now available to complete this.

My plan is to connect the induction hob using the normal 3 phases, Neutral and Earth, using 5 of the available wires. Then using the remaining wire for the plug socket for the oven, and sharing the Neutral and Earth between the 3 phase hob and the single phase socket.

Is there any risk I am overloading neutral doing this ?


The oven is 2.2kw and the Induction Hob is 7.2kw.


Hope someone can help, look forward to hearing from you.

atomic is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 21-07-2008   #2 (permalink)
wayne
Respected Member
 
Join Date: Feb 2008
Posts: 918
View wayne's Photo Album
Default Re: Question about sharing Neutral..

in the uk its one neutral to one circuit you have two circuits there ,however is this question for overseas if so whats their regs?
wayne is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 21-07-2008   #3 (permalink)
rumrunner
Guest
 
Posts: n/a
View rumrunner's Photo Album
Default Re: Question about sharing Neutral..

Quote:
Originally Posted by wayne View Post
in the uk its one neutral to one circuit you have two circuits there ,however is this question for overseas if so whats their regs?
I wouldnt think the neutral does much anyway .best thing do it turn it all on and test current in neutral ,i dont think it will be very much
have fun
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 22-07-2008   #4 (permalink)
atomic
Junior Member
 
Join Date: Jul 2008
Posts: 3
View atomic's Photo Album
Default Re: Question about sharing Neutral..

Thanks for the answers, I haven't a clue what the regs are, but I am sure, like you say, its one neutral per circuit.

I also don't expect much weight to be on neutral, but unfortunately can't test it yet as the new hov/oven hasn't arrived, and when it does it will be too late to change the cable.

At least nobody has written back "YOU CAN'T DO THAT, ITS A TERRIBLE IDEA" so I feel partly re-assured

Regards

Atomic.
atomic is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 22-07-2008   #5 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: Question about sharing Neutral..

Quote:
Originally Posted by atomic View Post
Thanks for the answers, I haven't a clue what the regs are, but I am sure, like you say, its one neutral per circuit.

I also don't expect much weight to be on neutral, but unfortunately can't test it yet as the new hov/oven hasn't arrived, and when it does it will be too late to change the cable.

At least nobody has written back "YOU CAN'T DO THAT, ITS A TERRIBLE IDEA" so I feel partly re-assured

Regards

Atomic.
Is the hob wired as single phase hobs of each of the three phases, or they actually three phase elements? If so, they will be star connected and there will be no (or neglible) neutal current.

even if not, you can apply diversity to the hob, so 7.2kw is about 2.5kw per phase (roughly) so about 10 A per phase. But of course not all phases can peak at the same time, so you still find your neutral current is preety low. 2.5 is roughly 27A (with no correction factors,) so you are well within

So

A. You wont oveload the cable
B. Cant say if its 'legal' against your regs, but would almost certainly be against ours because of the borrowed neutral
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 25-07-2008   #6 (permalink)
mjvor
Junior Member
 
Join Date: Jul 2008
Posts: 3
View mjvor's Photo Album
Default Re: Question about sharing Neutral..

I have to disagree with shakey
Only single core PVC single phase has a rating of 27A clipped direct.

You have 2nr 3 core cables which abroad will typically be wired through conduit
This at 3 phase only has a rating of 20A (table 4D2A col 5) which then has to be derated by 0.8 for a group of 2 = 16A

Without diversity you could get 21A at 220V (2.4kw + 2.2kw = 4.6kw).

With diversity though, which you can legitimately use, this will be much less so I would say the cables won't get too hot. They should all be wired back to a 20A TP circuit breaker. Using one neutral for the 2 items does not class as a borrowed neutral provided both circuits connect to one circut breaker. A borrowed neutral is where two separate circuits with separate fuses/CBs share a neutral.

Mike
mjvor is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 25-07-2008   #7 (permalink)
wattsup
Senior Member
 
Join Date: Jun 2008
Posts: 236
View wattsup's Photo Album
Default Re: Question about sharing Neutral..

A shared n is not the same as borrowed as above, so long as the breaker controls the shared n, no problem. 3-phase ovens, the ones i've seen anyhow, are not truely 3-phase, elements are single phase, they just have a 3-phase supply. You should be able to tell from the connection terminals. Just power the whole thing up and use tongue tester to load test.
wattsup is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 25-07-2008   #8 (permalink)
rumrunner
Guest
 
Posts: n/a
View rumrunner's Photo Album
Default Re: Question about sharing Neutral..

Hi
Most industrial ovens ive worked on have been wired as "4 wire star" which is the old bs way of doing it ,euro stuff might be different,and if it is 3 seperate neutrals ,which i think is uncommon then that means he needs 8 cores plus cpc so i think it must be conventional wiring
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 25-07-2008   #9 (permalink)
Bane
Respected Member
 
Join Date: Jan 2008
Posts: 908
View Bane's Photo Album
Default Re: Question about sharing Neutral..

Well...I think it's a terrible idea.
Bane is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 26-07-2008   #10 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: Question about sharing Neutral..

Quote:
Originally Posted by mjvor View Post
I have to disagree with shakey
Only single core PVC single phase has a rating of 27A clipped direct.

You have 2nr 3 core cables which abroad will typically be wired through conduit
This at 3 phase only has a rating of 20A (table 4D2A col 5) which then has to be derated by 0.8 for a group of 2 = 16A

Without diversity you could get 21A at 220V (2.4kw + 2.2kw = 4.6kw).

With diversity though, which you can legitimately use, this will be much less so I would say the cables won't get too hot. They should all be wired back to a 20A TP circuit breaker. Using one neutral for the 2 items does not class as a borrowed neutral provided both circuits connect to one circut breaker. A borrowed neutral is where two separate circuits with separate fuses/CBs share a neutral.

Mike
erm....I know what a borrowed neutral is thanks

the way he was describing it, using the 'spare cable' for the supply to the socket, and using the three phase supplies neutral for the return, I assumed he was going to put the socket cable on a seperate CPD, in which case it WOULD be a borrowed neutral.

If he was taking the lot of a three phase breaker, and just tapping off one of the phases for the socket, then he wouldnt be needing the extra cable

and i did say it was 27A 'roughly with no correction factors'


Last edited by Shakey; 26-07-2008 at 01:56 PM.
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
borrowed neutral aaronstuart General Electrical Discussion 6 18-09-2008 04:43 PM
Voltage Converter (basic question!) CKsam General Electrical Discussion 11 09-06-2008 10:13 AM
Another ceiling light question. Unclebill General Electrical Discussion 8 27-01-2008 10:22 PM
2391 : 19#Exam Sample Question (Short Question) LukeScotty Electrical NVQ's & Courses 2 31-12-2007 01:23 PM
2391 : 21#Exam Sample Question (Short Question) LukeScotty Electrical NVQ's & Courses 1 09-12-2007 01:15 AM

Google Search
Google

All times are GMT +1. The time now is 07:44 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38