Electrical Forum - Electricians Forum - Electrical Talk - Electrical Courses - Electricians Training - Electrical Knowledge

Go Back   Electricians Forum | Electrical Forum | An electrical forum for electricians in the UK > General Electrical Forum Topics > Wiring, Theories and the Regulations
Forgot Password? Join Us!

Wiring, Theories and the Regulations Discussions on all electrical regulations in the UK. Including Part P, BS 7671, DPC BS7671:2008, BS 7671:2001 & 2004 Amendment No.2, IEE wiring regulations, 16th Edition and 17th Edition

Reply
 
LinkBack Thread Tools Display Modes
Old 22-07-2008   #1 (permalink)
LukeScotty
Administrator
 
LukeScotty's Avatar
 
Join Date: Jul 2007
Location: South Yorkshire
Posts: 724
View LukeScotty's Photo Album Send a message via MSN to LukeScotty
Default Quicky - 2382 question

where would i find this in the red book?

The correction factor for cables installed in free air with 70oC thermosetting insulation and an ambient temperature of 50oC is?

any help would be much appreciated,

regards


If You Build It, They Will Come n If it aint broken don't fix it!
LukeScotty is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 22-07-2008   #2 (permalink)
ccrowe
Junior Member
 
Join Date: Jul 2008
Location: Dorset
Posts: 19
View ccrowe's Photo Album
Default Re: Quicky - 2382 question

Table 4B1 on page 267.
ccrowe is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 22-07-2008   #3 (permalink)
LukeScotty
Administrator
 
LukeScotty's Avatar
 
Join Date: Jul 2007
Location: South Yorkshire
Posts: 724
View LukeScotty's Photo Album Send a message via MSN to LukeScotty
Default Re: Quicky - 2382 question

this is wat is confusing me, it says 70oC thermosetting insulation. the tables has "70oC thermoplastic" and "90oC thermosetting" so which one do i look under?

heres another one, too

The correction factor for cables installed in free air with 90oC thermosetting insulation and an ambient temperature of 40oC is

A: 0.76
B: 0.69
c: 0.96
D: 0.86

If You Build It, They Will Come n If it aint broken don't fix it!

Last edited by LukeScotty; 22-07-2008 at 05:54 PM. Reason: Automerged Doublepost
LukeScotty is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 25-07-2008   #4 (permalink)
mjvor
Junior Member
 
Join Date: Jul 2008
Posts: 3
View mjvor's Photo Album
Default Re: Quicky - 2382 question

The new table 4B1 is more limited than the old one.

I think the first questioin may have been a typing error - not unusual for C&G).

Your second question doesn't have the right answer - should be 0.91 - again another C&G error, but I think you copied it incorrectly as only one of the 4 answers (0.76) is a possible answer. They will only list 4 figures which you could get from the table.

However, you can get 90deg thermoplastic and 60deg thermosetting which the table doesn't address.

You need to just go on the temperature rating of the cable, not what it's made of.

The rating factor will allow enough current to heat the cable up to its maximum temp.

So if you have a 90deg thermoplastic in an ambient of 70deg then the rating will be 0.58 which will get it to 90deg

P296 gives ratings and factors for 60deg and 90deg flexible cords whether thermoplastic or thermosetting

Mike

mjvor is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Voltage Converter (basic question!) CKsam General Electrical Discussion 11 09-06-2008 10:13 AM
Question about Napit..?? hungy5 General Electrical Discussion 12 18-05-2008 09:32 PM
the most simple question evo666 General Electrical Discussion 18 25-03-2008 08:48 AM
Basic lighting controls question. mhmd_01 General Electrical Discussion 13 24-03-2008 10:52 AM
2391 : 19#Exam Sample Question (Short Question) LukeScotty Electrical NVQ's & Courses 2 31-12-2007 01:23 PM

Google Search
Google

All times are GMT +1. The time now is 09:07 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38