Default Re: CU Max Height According to Building Regs

the db i just put in would need the floor digging out to make it fit!!!(24 three phase ways)
do i have to build a ramp out front if i get any building work done on my house???
wayne is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 28-07-2008   #12 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: CU Max Height According to Building Regs

well its all boll**s

i mean lets say you fit a fan in the bathrrom, you should fit a double pole isolator so you should have isolation for maintenance,

but you have to install the isolator low enough for a disabled person in a wheelchair to operate it

erm.....how do they get up the fan to clean it

and like you say, great, they can isolate the lighting circuit, but how do they get up there to change the lamp in the ceiling rose

and before you start with 'offending disabled people' and they 'have the same rights as everyone else', my wife has had MS for a number of years, so believe me, I know what its about!
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-07-2008   #13 (permalink)
dixon9
Member
 
Join Date: Jul 2008
Posts: 67
View dixon9's Photo Album
Default Re: CU Max Height According to Building Regs

Still not convinced by the replies (with all due respect).

I understand that we have to conform to new regs and requirements - and they say max heights of 0.45 and 1.2m for sockets and CU´s (centre of the CU). If we are providing new installations or new circuits or new extensions to circuits then they must conform (no matter the inconvenience).

There is probably a bit of connundrum here between Part P, Part M and the 17th? What does the 17th say on this?
dixon9 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-07-2008   #14 (permalink)
benji
Member
 
Join Date: Jun 2008
Posts: 43
View benji's Photo Album
Default Re: CU Max Height According to Building Regs

weve got some MG 24w tp dbs with cts for metering & 160a tp contactor in bottom compartment controlled via em.stops,the bloody things are 1.5mtr high and take two to lift
yours benji
benji is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-07-2008   #15 (permalink)
sparkymark
Junior Member
 
Join Date: Jul 2008
Posts: 10
View sparkymark's Photo Album
Default Re: CU Max Height According to Building Regs

it wont apply for a commercial/industrial building as M regs only applies to dwellings (see page 68 of electricians guide to the building regs). db's in comm/ind should only be touched by the maintainance dept so wouldn't require them to be lower down
sparkymark is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-07-2008   #16 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: CU Max Height According to Building Regs

Quote:
Originally Posted by dixon9 View Post
Still not convinced by the replies (with all due respect).

I understand that we have to conform to new regs and requirements - and they say max heights of 0.45 and 1.2m for sockets and CU´s (centre of the CU). If we are providing new installations or new circuits or new extensions to circuits then they must conform (no matter the inconvenience).


There is probably a bit of connundrum here between Part P, Part M and the 17th? What does the 17th say on this?
no Dixon, sorry you are wrong

new circuits and new extensions do NOT need to conform

The approved documents to both Part M and Part P expressly say that; it is quite acceptable to mount them at a height inkeeping with the existing property

even in build it does not apply to the kitchen and garage

and part p and the 17th have nothing to do with each other!
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 30-07-2008   #17 (permalink)
dixon9
Member
 
Join Date: Jul 2008
Posts: 67
View dixon9's Photo Album
Wink Re: CU Max Height According to Building Regs

Quote:
Originally Posted by Shakey View Post
no Dixon, sorry you are wrong

new circuits and new extensions do NOT need to conform

The approved documents to both Part M and Part P expressly say that; it is quite acceptable to mount them at a height inkeeping with the existing property

even in build it does not apply to the kitchen and garage

and part p and the 17th have nothing to do with each other!
Well yes Shakey, I´m quite aware that the 17th and Part P or Part M aren´t directly connected!

Although ín the real world a domestic spark would need to be aware of part p, some sections of part M and the 17th, yes?!

I came across this on the web - interesting stuff and it pretty much backs up what I´m saying re "connundrum" above. (You will find that Part M has been ammended now anyway according to the author). The conclusions seem to be; it is not clear, CU height on new builds BUT best practice to put the CU at the new height:


Steve Dyson explains why most new housebuilds fail to meet Part P and Part M of the Building Regulations.


When it comes to mounting consumer units, Part P and Part M of the Building Regulations have left many in the industry confused.

Traditionally, the consumer unit is positioned either high up on the wall out of eye line, in the downstairs toilet or perhaps in a cupboard under the stairs. Judging by much of the new build that we see, most people clearly still believe that this is where it should stay.

Unfortunately this does not meet with the requirements of either Part P or Part M. In fairness the legislation is hardly clear on the matter.

Part P section 1.6 states that: “Wall-mounted socket outlets, switches and consumer units should be located so that they are easily reachable where this is necessary to comply with Part M. Approved Document M shows ways of complying.”

This seems to be clear enough. Unfortunately, if you then refer to Part M, there is no overt mention of consumer units, hence the muddied waters. Here you need to dig deep, and it is probably not a surprise that few bother. If you want to comply with the Building Regulations, however, you must.

Section 8 of Approved Document M, which applies to new dwellings, includes the objective of “assisting people whose reach is limited to use the dwelling more easily, by locating wall-mounted switches, socket outlets and other equipment at suitable heights, so that they are easily reachable for use.”

The NICEIC indicates that “other equipment” includes circuit breakers and therefore the consumer units that they are sited in.

Suitable heights for switches and socket outlets are between 0·45 m and 1·2 m from the finished floor level.

However, a more limited height range of 0·75 m to 1·2 m above finished floor level is recommended for simple push button controls, isolator switches and circuit breakers that require limited dexterity. So the maximum height should be 1200 mm to the centre of the switches and controls. If you are using a multi-row enclosure, then all the devices must be within these height ranges.

In fairness, this clearly complies with the spirit of Part M. Consumer units should be accessible so that people can operate circuit breakers in an emergency and for the routine testing and resetting of RCDs. This means that they must be in reach as defined by Part M.

“It is time for the industry to be aware of all Part M requirements”




In addition, they should not be installed in a lockable cupboard – which is, after all, hardly accessible. Any consumer unit that complies with BS EN 60439-3 and has switches that are located behind a cover is fit for purpose.

The NICEIC also makes the point that consumer units must be accessible for safe working. Regulation 15 of the Electricity at Work Regulations 1989 states that to avoid injury “…adequate working space, adequate means of access and adequate lighting shall be provided at all electrical equipment on which, or near which, work is being done in circumstances which may give rise to danger.”

For a consumer unit, such work should include the measurement of maximum prospective fault current, a test that may give rise to danger. It should therefore be mounted at a height that allows adequate access for such work to be carried out safely.

Mounting a consumer unit at a suitable height for inspection, testing and maintenance is also necessary for compliance with the accessibility requirements of Regulations 131-12-01 and 513-01-01 of BS 7671.

You will note that this article only refers to new build. You do not need to move a consumer unit to Part M heights for a house rewire or for building an extension. It might, however, be considered best practice to do so.

One final point, if a consumer units is fitted in the garage, then it must also comply with Part P and Part M. You should choose a position where it’s unlikely to be damaged. Back walls are generally better than side walls.

It is time for the industry to be aware of all Part M requirements and to at least draw the main contractor’s attention to its legal obligations. The fact that this might cause some builders inconvenience is not an argument.

Arguments about aesthetics are not a barrier to complying with the regulations. Indeed, many boards have modern aesthetic designs. If a board sticking out of the wall will cause a hazard then install a flush fit unit.

Many of the issues which are currently surrounding Part M are due to be clarified by the end of this year. In the meantime, make sure that you at least draw attention to the regulations.

According to one recent blog, an electrician told the NICEIC inspector who rejected a consumer unit installation to shove Part M. While this may have been satisfying, it carries no legal weight.

Steve Dyson is Hager’s product manager for LV distribution
dixon9 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 30-07-2008   #18 (permalink)
kiwisparks
Junior Member
 
Join Date: Jul 2008
Posts: 1
View kiwisparks's Photo Album
Talking Re: CU Max Height According to Building Regs

I recently read a EDF document,dated 12/07,recommending a meter height of between
1.8m and 450mm,(it makes the the CU a handy step to read the meter!!)
In my early days i always flushed in the CU at eye level,in my case 1.8m,completely out of harms way,i could never understand anyone putting them down under bench height in a cubboard,maybe because i had trouble getting in to it!!.....KS
kiwisparks is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 30-07-2008   #19 (permalink)
wayne
Respected Member
 
Join Date: Feb 2008
Posts: 918
View wayne's Photo Album
Default Re: CU Max Height According to Building Regs

dixon9,
thank you for the info
wayne is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 30-07-2008   #20 (permalink)
sparkyork
Respected Member
 
sparkyork's Avatar
 
Join Date: Jun 2008
Location: york
Posts: 623
View sparkyork's Photo Album
Default Re: CU Max Height According to Building Regs

yeah lot of good info there, cheers.

if i can just confirm something, ive got my nic inspection on the 22nd august and theyve got a consumer unit to look at, it was a direct replacement i did and it is located in a kitchen cupboard, low down. hoping this nic man int gonna start ranting about part m? shouldn do tho should he?!

also ive got a 3 ph board to install soon and looking today the only logical place for it is above a door frame (6ft 6 ish) and then continuing up another 4 ft to the top of the board, is this acceptable?

cheery

sparkyork is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Differences between OSG and Big regs book DanBrown Wiring, Theories and the Regulations 6 13-09-2008 09:29 AM
help with building regs marty1234 General Electrical Discussion 10 12-09-2008 02:06 PM
Downlighters & Building Control Reg Man General Electrical Discussion 3 14-06-2008 05:31 PM
Height of light switch DanBrown Wiring, Theories and the Regulations 18 18-03-2008 11:04 PM
Building Reg M - Socket n switch height?? LukeScotty Wiring, Theories and the Regulations 3 09-01-2008 11:38 PM

Google Search
Google

All times are GMT +1. The time now is 11:46 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38