Old 06-08-2008   #1 (permalink)
kmarsden98
Junior Member
 
Join Date: Aug 2008
Posts: 5
View kmarsden98's Photo Album
Default socket outlets near a bath

hi i was wondering if any one could help a hotel that i do some electrical work for are updating their rooms they are putting baths in all the guest rooms all the rooms have 1 twin s/o in which are about 1 to 2Metres from the bath
does any one no what the regs are on existing sockets near a newly fitted bath do they have to be moved 3M away.
thanx

kmarsden98 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 07-08-2008   #2 (permalink)
daver
Junior Member
 
Join Date: Jul 2008
Posts: 7
View daver's Photo Album
Default Re: socket outlets near a bath

They have to be 3m away.
daver is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 07-08-2008   #3 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: socket outlets near a bath

Quote:
Originally Posted by kmarsden98 View Post
hi i was wondering if any one could help a hotel that i do some electrical work for are updating their rooms they are putting baths in all the guest rooms all the rooms have 1 twin s/o in which are about 1 to 2Metres from the bath
does any one no what the regs are on existing sockets near a newly fitted bath do they have to be moved 3M away.
thanx
they have to be 3m away AND meet all the other requirements, RCD protected etc
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 07-08-2008   #4 (permalink)
claire_r
Junior Member
 
Join Date: Aug 2008
Posts: 3
View claire_r's Photo Album
Default Re: socket outlets near a bath

is agreeing with everyone else...and 3m is a fair old way!!
claire_r is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 07-08-2008   #5 (permalink)
kmarsden98
Junior Member
 
Join Date: Aug 2008
Posts: 5
View kmarsden98's Photo Album
Default Re: socket outlets near a bath

thanks thought so told the owner of the hotel it cant be done as the room isnt even 3m long also advised removing all sockets from the room she going to try gettin another spark to do the job
kmarsden98 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 08-08-2008   #6 (permalink)
greekislandlover
Senior Member
 
Join Date: Jun 2008
Posts: 134
View greekislandlover's Photo Album
Default Re: socket outlets near a bath

Isn't she being a silly trollop???

OK, she might get one of our eastern european brethren living in a van for the summer, cash only and not paying tax/NI and the rest to do it, but what does that gain her?

She has a responsibility for Elf 'n' safety of her guests, and she also has to comply with conditions of insurance to continue to BE insured. No doubt she has to have a fire certificate, have gas and electrical PIR's up to date etc. or if something happens the insurance won't pay out to start with. Plus the Elf 'n' safety mob crawling everywhere to contend with.

Nobody is going to issue a PIR to say "Satisfactory" with sockets in a bathroom that are that close PLUS no RCD. So where does that leave her?? In potentially deep doo-doo I would guess.

She doesn't realistically have a choice BUT to make sure her premises comply with the regulations. Getting someone else to do the job might be difficult. But sometimes it's just best to tell them the score then walk away.
greekislandlover is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 08-08-2008   #7 (permalink)
jibspark
Senior Member
 
Join Date: Nov 2007
Location: Brighton
Posts: 151
View jibspark's Photo Album
Default Re: socket outlets near a bath

this might be a silly question BUT......

when you do have a socket 3M away can you just have an RCD SOCKET or does the whole circuit need to be RCD protected?

and i presume it doesnt have to be 3M away if its in a different room? i.e a lounge wall backing onto a bathroom wall etc..........

ive not long woken up so go easy!
jibspark is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 08-08-2008   #8 (permalink)
KFORDHUNTER
Member
 
Join Date: Jul 2008
Posts: 54
View KFORDHUNTER's Photo Album
Default Re: socket outlets near a bath

According to the regs if the cables are less than 50mm deep in the wall blah blah blah and not in earthed metallic conduit blah blah blah and not under the supervision blah blah blah or labelled for a specific item blah blah blah then yes they have to be rcd protected to bring them up to regs. I have taken and passed my 17th update and learnt one word, RCD RCD RCD RCD RCD RCD RCD RCD RCD RCD.

Oh and yes if there is a wall in between the bathroom and another room, the other room aint a bathroom, unless theres a bath in it of course, hope this helps mate.
KFORDHUNTER is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 08-08-2008   #9 (permalink)
jibspark
Senior Member
 
Join Date: Nov 2007
Location: Brighton
Posts: 151
View jibspark's Photo Album
Default Re: socket outlets near a bath

ok, so couldnt the hotel owner just relocate the sockets and ensure the on suite has a stud wall around it?
jibspark is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 08-08-2008   #10 (permalink)
dixon9
Member
 
Join Date: Jul 2008
Posts: 67
View dixon9's Photo Album
Default Re: socket outlets near a bath

Quote:
Originally Posted by jibspark View Post
this might be a silly question BUT......

when you do have a socket 3M away can you just have an RCD SOCKET or does the whole circuit need to be RCD protected?

Interesting question.

If so how does the dedicated cable from the CU to the bathroom stand in terms of the RCD located at the socket? Would the more limited upstream protection make this a no no?

dixon9 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Change single socket to a double Mattbot2 General Electrical Discussion 7 07-09-2008 08:40 PM
extra socket done to 16th sparkyork Inspection, Testing and Certification of Electrical Installations 12 19-08-2008 11:51 PM
Socket outlets under bath. YTSOxford Wiring, Theories and the Regulations 9 03-08-2008 05:03 PM
Height Of Electrical Socket And Switch Outlets ADAMSKI General Electrical Discussion 7 16-06-2008 10:36 AM
No Earth on socket dazza001 General Electrical Discussion 12 23-01-2008 08:08 PM

Google Search
Google

All times are GMT +1. The time now is 08:36 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38