Electrical Forum - Electricians Forum - Electrical Talk - Electrical Courses - Electricians Training - Electrical Knowledge

Go Back   Electricians Forum | Electrical Forum | An electrical forum for electricians in the UK > General Electrical Forum Topics > Wiring, Theories and the Regulations
Forgot Password? Join Us!

Wiring, Theories and the Regulations Discussions on all electrical regulations in the UK. Including Part P, BS 7671, DPC BS7671:2008, BS 7671:2001 & 2004 Amendment No.2, IEE wiring regulations, 16th Edition and 17th Edition

Reply
 
LinkBack Thread Tools Display Modes
Old 07-08-2008   #1 (permalink)
daver
Junior Member
 
Join Date: Jul 2008
Posts: 7
View daver's Photo Album
Default Diversity

Just a knowledge question really. Have only just qualified, so dont batter me down with my 2nd post

Just starting a job, which is 8 double bedded flats in an existing large house.
Was going to run 1 ring per flat but for ease, this is now 1 ring and 2 radials. 48A
1 Lighting 3.96A
1 Cooker 10.65A
So totalling with diversity 62.6A

16mm down to Incomer and a 63A Breaker.

The landlord has 1 lighting circuit, with emergency lights and smokes.

So my calculation is approx 510A

What will the electricity company have to supply for this?
Do they apply a diversity factor on the 9 feeds

Thanks in anticipation

Dave

daver is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 08-08-2008   #2 (permalink)
mpfisher@hotmai
Senior Member
 
mpfisher@hotmai's Avatar
 
Join Date: Jul 2008
Location: Leeds
Posts: 124
View mpfisher@hotmai's Photo Album
Default Re: Diversity

Hope you get more replies to this than ya last post mate!!!!
mpfisher@hotmai is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 08-08-2008   #3 (permalink)
daver
Junior Member
 
Join Date: Jul 2008
Posts: 7
View daver's Photo Album
Default Re: Diversity

1 reply to other, but looking grim mp.
daver is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 08-08-2008   #4 (permalink)
spark-doctor
Senior Member
 
Join Date: Aug 2008
Location: Dorset
Posts: 295
View spark-doctor's Photo Album
Default Re: Diversity

Some questions,
1) Are the supply cables going to be at a depth of less than 50mm?
2) What is the length of each run?
3) What is the installation method?
4) Are they in any insulation, if so, how deep?
5) You have not mentioned showers. I hope all 16 people will not want to use the bathroom at the same time (mind you, i have seen 28 Polish in a 4 bed house).
6) Cookers. Is it 1 per room
7) Smoke alarms.
8) Are you having coin meters.

I am sure there is more but i think you need to answer some of these first.

Last edited by spark-doctor; 08-08-2008 at 08:35 PM.
spark-doctor is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 08-08-2008   #5 (permalink)
daver
Junior Member
 
Join Date: Jul 2008
Posts: 7
View daver's Photo Album
Default Re: Diversity

1) Are the supply cables going to be at a depth of less than 50mm?
Boxed in, and clipped to wooden back board, but certainly deeper than 50 mm

2) What is the length of each run?
Straight up from hallway to each floor and CU, on that vertical plane. So longest will be 2 stories, so 2 longest are top floor. 16ft ceilings so aproxx 35ft to furthest

3) What is the installation method?
Clipped
4) Are they in any insulation, if so, how deep?
No Insulation
5) You have not mentioned showers. I hope all 16 people will not want to use the bathroom at the same time (mind you, i have seen 28 Polish in a 4 bed house).
Multipoint boiler
6) Cookers. Is it 1 per room
1 per flat, 2.6kw
7) Smoke alarms.
1 per flat
8) Are you having coin meters.
Meters in hallway, (not coin) but 9 individual.

I have done the diversity on the flats. It is down to Electric company now to Install.

I was just wondering what would be required, and would they apply diversity accross the 9 flats.

It was what sort of supply will they give the landlord. As normal 3 phase is only 80 or 100amp per phase

Just a knowledge question really.

Thanks again
daver is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-08-2008   #6 (permalink)
wayne
Respected Member
 
Join Date: Feb 2008
Posts: 918
View wayne's Photo Album
Default Re: Diversity

im sure some one will be along to help you shortly ,dave this is not my area
wayne is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-08-2008   #7 (permalink)
tony.towa
Respected Member
 
tony.towa's Avatar
 
Join Date: Jul 2008
Location: Warwickshire
Posts: 539
View tony.towa's Photo Album
Default Re: Diversity

Assuming that the existing supply is a standard single phase supply of 80 or 100amps the required supply will have to be upgraded. You will need to contact the suppliers and inform them of the required upgrade. You will receive back a load of forms to fill out and the total loading will be required on this. Full details of the proposed supply distribution within the installation should be provided to the suppliers and they will then arrange for the necessary supply to be installed. In the installation you describe the odds are that it will be three phase, however they will inform you of what they are to install. Whether they apply diversity or not is down to them however if you were to require 160 amps per phase they will normally install a 200amp supply and down rate the fusing. A word of warning, this will not be cheap.
tony.towa is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-08-2008   #8 (permalink)
daver
Junior Member
 
Join Date: Jul 2008
Posts: 7
View daver's Photo Album
Default Re: Diversity

Tony

Thanks for that. It was just to fill my head with more info. It is not my worry, I have told the landlord what is required and he has the forms already.
So, that is 9 supplies, 8 Gas and 8 water meters.

Its an expensive hobby developing property.

Cheers guys.
daver is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-08-2008   #9 (permalink)
tony.towa
Respected Member
 
tony.towa's Avatar
 
Join Date: Jul 2008
Location: Warwickshire
Posts: 539
View tony.towa's Photo Album
Default Re: Diversity

Nice you want to know that little bit more. When they have installed the new supply have a chat with the engineer and see if he will let you see the file. Some areas actually have all the spec on the installation file papers and so you should then be able to see how your area operates.

tony.towa is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Sizing DB and cable LOST319 General Electrical Discussion 3 01-05-2008 09:30 PM
diversity on a cooker ring kita Wiring, Theories and the Regulations 8 14-04-2008 09:47 PM
What size cooker feed? Cirrus Wiring, Theories and the Regulations 37 06-03-2008 03:59 PM
Working out Diversity? LukeScotty Wiring, Theories and the Regulations 4 14-01-2008 12:25 AM

Google Search
Google

All times are GMT +1. The time now is 10:42 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38