Default consumer unit change/move

I have been asked to plan a consumer unit change and the owner wants it sited within reach in case of nuisance tripping etc and her not being able to climb up steps etc.

I plan to take all existing circuit wiring into an adaptable box with din mounted terminals and making an easily accesible joint box between old and new wiring and then running trunking down to the new board (possibly in singles for ease fully idented of course)

for the ring circuits would it be ok to wire in 1 single conductor (double the csa obviously)

Sorry if its a stupid question, please dont flame me also is this what everyone else would do??

montybaber is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-08-2008   #2 (permalink)
sparkyork
Respected Member
 
sparkyork's Avatar
 
Join Date: Jun 2008
Location: york
Posts: 623
View sparkyork's Photo Album
Default Re: consumer unit change/move

hi matey, id defo go for the adaptable box and everything else you mentioned, sept for the single core for the ring? i think id be tempted to keep the ends of the ring at the consumer unit for general testing purposes and not to confuse anybody else that works on it in the future.

rich
sparkyork is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-08-2008   #3 (permalink)
montybaber
Respected Member
 
montybaber's Avatar
 
Join Date: Aug 2008
Posts: 404
View montybaber's Photo Album
Default Re: consumer unit change/move

Thanks..was thinking the same tbh just thought that as the box is literally gonna be 2 ft max above the consumer unit it was an acceptable point for testing and dissconnecting etc.

Really will not mean too much more work though so i'll keep it seperate thanks for your help
montybaber is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-08-2008   #4 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: consumer unit change/move

Quote:
Originally Posted by montybaber View Post
Thanks..was thinking the same tbh just thought that as the box is literally gonna be 2 ft max above the consumer unit it was an acceptable point for testing and dissconnecting etc.

Really will not mean too much more work though so i'll keep it seperate thanks for your help
i would keep them seperate as well, otherwise you would effectively have a ring on the end of a radial,

additionally, at the point you changed from (presumably) 4mm singles to 2.5 tw&E, would you not need to put protection in because of the change in cable size
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-08-2008   #5 (permalink)
montybaber
Respected Member
 
montybaber's Avatar
 
Join Date: Aug 2008
Posts: 404
View montybaber's Photo Album
Default Re: consumer unit change/move

Quote:
Originally Posted by Shakey View Post
i would keep them seperate as well, otherwise you would effectively have a ring on the end of a radial,

additionally, at the point you changed from (presumably) 4mm singles to 2.5 tw&E, would you not need to put protection in because of the change in cable size
thanks for your help

well I thought as long as the radial circuit is wired in a cable with a sufficiant current carrying capacity then one single conductor would'nt be a problem, and of course as a ring arrangement the two smaller csa cables are more than adequate in size to carry the same current as the single conductor so no I wouldnt have thought protection is neccesary

but like I said for the sake of running a couple of extra cables it is'nt worth worrying about
montybaber is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 09-08-2008   #6 (permalink)
wayne
Respected Member
 
Join Date: Feb 2008
Posts: 918
View wayne's Photo Album
Default Re: consumer unit change/move

Quote:
Originally Posted by Shakey View Post
i would keep them seperate as well, otherwise you would effectively have a ring on the end of a radial,

additionally, at the point you changed from (presumably) 4mm singles to 2.5 tw&E, would you not need to put protection in because of the change in cable size
so are you saying the" 4mm is on the original 32a mcb and at the box put another 32a mcb"???
wayne is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 10-08-2008   #7 (permalink)
Jumbonipondon_squilobidon
Member
 
Join Date: May 2008
Posts: 32
View Jumbonipondon_squilobidon's Photo Album
Default Re: consumer unit change/move

I've got another question with regards changing a DB. If the conductors from the circuits needed extending in the new board would you use in-line crimps or terminal (chock) block?? Any other thoughts???
Jumbonipondon_squilobidon is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 10-08-2008   #8 (permalink)
Cirrus
Guest
 
Posts: n/a
View Cirrus's Photo Album
Default Re: consumer unit change/move

I always use through crimps personally.
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 10-08-2008   #9 (permalink)
Gazza D
Junior Member
 
Join Date: Aug 2008
Posts: 8
View Gazza D's Photo Album
Default Re: consumer unit change/move

I use through crimps too, but get yourself a decent ratchet crimper!
Gazza D is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 10-08-2008   #10 (permalink)
tony.towa
Respected Member
 
tony.towa's Avatar
 
Join Date: Jul 2008
Location: Warwickshire
Posts: 539
View tony.towa's Photo Album
Default Re: consumer unit change/move

I'm with Cirrus and Gazza D, through crimps and decent ratchet.

Will this open up the discussion on crimping solid cables again?

tony.towa is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
consumer unit upgrade CUDABOY General Electrical Discussion 11 17-09-2008 01:32 PM
Consumer Unit Change. spud4dd Inspection, Testing and Certification of Electrical Installations 3 27-08-2008 03:39 PM
Electric Shower & Consumer Unit within my flat Southsider General Electrical Discussion 11 04-08-2008 10:46 PM
Consumer Unit (RCD Triping) londonelec General Electrical Discussion 20 28-07-2008 10:52 PM
Replacing a consumer unit. Johnocd Wiring, Theories and the Regulations 4 07-03-2008 06:17 PM

Google Search
Google

All times are GMT +1. The time now is 07:08 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38