Default Domestic Bathroom Isolators 'Under Your Control'

Hi Guys

Here is a bit of a conundrum that we are constantly having battles with during new domestic builds with various clients. The query is the siting of fan isolators and shower isolators for mechanical maintenance.

Our local NIC/EIC engineer and we agree, that fan isolators and shower isolators should be placed on the inside of the bathroom (in the correct zones obviously) so that it is under the control of the person who may carry out maintenance on a fan or shower unit in the future. The argument being that if the isolator is fitted on the outside it is not under your control, especially if the bathroom door gets closed, and anyone else in the house at the time could potentially turn the switch on without you knowing about it. I know you can get lockable isolators but are not very nice in a domestic environment.

All we can not find in any of our referance books is 'under the control for maintenance'. Does this mean the isolator should be in line of sight? Can anyone clarify this?

To make things worse I called NIC/EIC technical. They said all should be placed on the outside no matter what. I challenged this refering to 'under control'. The less than helpful guy then said just padlock off the consumer unit and place a sign saying electrician working. Also I could lock the front door to prevent people entering the house and be safe this way. Great answers! When I persisted and finally told him what our area engineer says he could see both sides of the argument and said don't know then mate. It is open to deabte.

We have a couple of customers who want isolators on the outside because it is their preferance and they are paying etc.

What do you all think?

smoking_muzzle is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 03-08-2007   #2 (permalink)
LukeScotty
Administrator
 
LukeScotty's Avatar
 
Join Date: Jul 2007
Location: South Yorkshire
Posts: 724
View LukeScotty's Photo Album Send a message via MSN to LukeScotty
Default Re: Domestic Bathroom Isolators 'Under Your Control'

hello smoking muzzle, welcome to the website,

Personally, I'd put the isolator on the outside on the bathroom. And a nice looking one too, couldn't be doing with one which looks like a commercial building. If you think there would be a problem with it being turned on during maintence and maybe turned on. I think the electrician would do what he thinks best, maybe putting a bit of elecy tape on the switch. But to be honest with your question people have different opinions with different things and do different methods. So I don't think you'll get a solid answer. See what others come up with. I don't see the problem of putting the isolator switch inside the bathroom in the correct zones either.
LukeScotty is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 11-08-2007   #3 (permalink)
shedfull
Junior Member
 
Join Date: Aug 2007
Posts: 11
View shedfull's Photo Album
Default Re: Domestic Bathroom Isolators 'Under Your Control'

For isolation for maintenance you'd think the isolator should be close to the equipment to be isolated like a cooker sw,

just looked at the site guide

pg 35, 5.3 (ii) be suitably located in a readily accessible position 462-01-02

'nuff said I think, you're right.................still they are payin' an its their bathroom
shedfull is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 11-08-2007   #4 (permalink)
LukeScotty
Administrator
 
LukeScotty's Avatar
 
Join Date: Jul 2007
Location: South Yorkshire
Posts: 724
View LukeScotty's Photo Album Send a message via MSN to LukeScotty
Default Re: Domestic Bathroom Isolators 'Under Your Control'

nice one shedfull for the information you looked up for us.
LukeScotty is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 07-09-2007   #5 (permalink)
-X-
Junior Member
 
Join Date: Sep 2007
Posts: 5
View -X-'s Photo Album
Default Re: Domestic Bathroom Isolators 'Under Your Control'

Lock out devices are a wonderful invention...

They are the answer..

You do all have and use them ??
-X- is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 07-09-2007   #6 (permalink)
phil333
Junior Member
 
Join Date: Aug 2007
Location: bournemouth
Posts: 6
View phil333's Photo Album
Default Re: Domestic Bathroom Isolators 'Under Your Control'

i suppose, if the bathroom is upstairs or a bungalow you could have the switch next to the fan in loft space?
if not, then i would place a lockable isolator outside the bathroom.

Did the NIC/EIC explain why you could not have an isolator in the bathroom?

maybe you could have it high level with a notice on the switch 'electrical isolator for maintenance purpose '???
phil333 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 20-09-2007   #7 (permalink)
fatboy
Junior Member
 
Join Date: Sep 2007
Posts: 2
View fatboy's Photo Album
Default Re: Domestic Bathroom Isolators 'Under Your Control'

As always common sense rules the waves. Putting the isolator where you think it is safe for any one to work on it but still satisfies (In your opinion) the regulations is the best option. The rgulations like so many things is open to interpretation. That is what you need to do. If it is not clear to you then it is not clear to all. Go with what you feel is right and you probably wont go far wrong. Common sense
fatboy is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-09-2007   #8 (permalink)
mercanlandy
Junior Member
 
mercanlandy's Avatar
 
Join Date: Sep 2007
Posts: 8
View mercanlandy's Photo Album
Default Re: Domestic Bathroom Isolators 'Under Your Control'

Hi, regarding the position it open to debate but what about disability access. Is a fan isolator switch ok to site at ceiling level (as most are between the door frame and ceiling ).
or should it be lower so disabled persons can switch it off in case of a panic attack ?
mercanlandy is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 01-10-2007   #9 (permalink)
LukeScotty
Administrator
 
LukeScotty's Avatar
 
Join Date: Jul 2007
Location: South Yorkshire
Posts: 724
View LukeScotty's Photo Album Send a message via MSN to LukeScotty
Default Re: Domestic Bathroom Isolators 'Under Your Control'

phil333, I think you cants have a "switch" isolator inside a bathroom full stop. It has to be on the outside. and mecanlandy regards to the disability access. In my opinion the isolator is for a skilled person "electrician" and to be honest with you, you don't really come across a physically impaired persons whos in a wheel chair whos an skilled electrician. So having your isolater high up in the air is ok. (i think, if any one can correct me, please do)

If You Build It, They Will Come n If it aint broken don't fix it!
LukeScotty is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 11-01-2008   #10 (permalink)
Minky
Junior Member
 
Join Date: Dec 2007
Posts: 19
View Minky's Photo Album
Default Re: Domestic Bathroom Isolators 'Under Your Control'

There is no problem installing the isolator switch for the bathroom fan in Zone 3 of the bathroom,even on the ceiling,if you wish.
Since most new build ceilings are 2.4m (to allow for plasterboard length),then installing above 2.25m and in zone 3 then all should be fine.
Maybe NIC guy need to get his tape measure calibrated!! hehe.

Minky is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
remote control security lighting control salisbury spark General Electrical Discussion 8 19-10-2008 01:16 PM
EAL Domestic Electrical Installer ktech Electrical NVQ's & Courses 3 17-09-2008 07:39 PM
Downlighters & Building Control Reg Man General Electrical Discussion 3 14-06-2008 05:31 PM
domestic installation course advice rich77 Electrical NVQ's & Courses 0 26-04-2008 05:55 PM
Fan in Bathroom Darius-parky Wiring, Theories and the Regulations 8 09-04-2008 10:29 PM

Google Search
Google

All times are GMT +1. The time now is 11:45 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38