Old 28-02-2008   #1 (permalink)
mike
Junior Member
 
Join Date: Feb 2008
Posts: 15
View mike's Photo Album
Default 50mm deep

hi. ive been told than on the new regs that cables less than 50mm deep in the wall have to be rcd protected. does any know if this includes where you know there are cables like above switches. thanks

mike is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 28-02-2008   #2 (permalink)
LukeScotty
Administrator
 
LukeScotty's Avatar
 
Join Date: Jul 2007
Location: South Yorkshire
Posts: 724
View LukeScotty's Photo Album Send a message via MSN to LukeScotty
Default Re: 50mm deep

isn't it, if the cables arent 50mm deep, then mechinical protect it, or rcd it or both. An electrician may know they could be cables above the switch, but what about a home owner drilling through the wall to hang his pants on?

If You Build It, They Will Come n If it aint broken don't fix it!
LukeScotty is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 28-02-2008   #3 (permalink)
Cirrus
Guest
 
Posts: n/a
View Cirrus's Photo Album
Default Re: 50mm deep

I've just seen the NIC DVD on this tomight and basically it says that if the cables are less than 50mm deep they must be RCD protected - UNLESS in trunking and then you do not have to place on an RCD
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 28-02-2008   #4 (permalink)
mike
Junior Member
 
Join Date: Feb 2008
Posts: 15
View mike's Photo Album
Default Re: 50mm deep

really seems a bit over the top does any one konw what size rcd? hope its not 30ma
mike is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 28-02-2008   #5 (permalink)
Cirrus
Guest
 
Posts: n/a
View Cirrus's Photo Album
Default Re: 50mm deep

Yup - 30mA
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 28-02-2008   #6 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: 50mm deep

Basically:

buried cable less than 50mm deep:-

within safe zone:30mA

within safe zone WITH earthed metallic protection (SWA, earthed conduit - NOT capping) - no RCd required (for cables)

Outside safe zone: 30mA WITH earthed metallic protection

Outside safe zone: must be earthed metallic covering (not allowed without)

Of course, if the cables feed sockets of 20A of less for use by ordrinary persons, or bathroom electrics, or equipment outside equipotnetial zone: RCD 30mA

UNLESS specifically labelled socket (ie Freezer only)

surface mounted CABLES do not need RCD but of course the circuit they are supplying may do (as above, bathrooms etc)

Obviously this will pretty much 'bin' the 100mA protection against fire RCD for TT's as well!
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-02-2008   #7 (permalink)
mike
Junior Member
 
Join Date: Feb 2008
Posts: 15
View mike's Photo Album
Default Re: 50mm deep

thanks for that, but what do you mean by safe zone?
mike is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-02-2008   #8 (permalink)
Grae79
Senior Member
 
Grae79's Avatar
 
Join Date: Jan 2008
Posts: 245
View Grae79's Photo Album
Default Re: 50mm deep

like the twilight zone but less weird...

safe zones extend horizontally & vertically from wiring accessories (sockets/switches), the width of the zone relates to the length/width of the applicable accessory.

also have a safe zone of 150mm (6") at the top and corners of walls.

Last edited by Grae79; 29-02-2008 at 07:11 PM. Reason: Automerged Doublepost
Grae79 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-02-2008   #9 (permalink)
mike
Junior Member
 
Join Date: Feb 2008
Posts: 15
View mike's Photo Album
Default Re: 50mm deep

I see. if knowing the cables are not 50mm deep on a existing instalation, should i put in a rcd or just put in a rcbo on the circuit i workrd on?
mike is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-02-2008   #10 (permalink)
Cirrus
Guest
 
Posts: n/a
View Cirrus's Photo Album
Default Re: 50mm deep

Until June you don't have to do anything but when the 17th comes in then, you gotta do it.

 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Google Search
Google

All times are GMT +1. The time now is 10:45 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38