Default Re: What size cooker feed?

Quote:
Originally Posted by Grae79 View Post
did u pluck that off the top of ur head Easy?
What the diversity bit?
EasyFox is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-02-2008   #12 (permalink)
Cirrus
Guest
 
Posts: n/a
View Cirrus's Photo Album
Default Re: What size cooker feed?



Eh?
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-02-2008   #13 (permalink)
Bane
Respected Member
 
Join Date: Jan 2008
Posts: 908
View Bane's Photo Album
Default Re: What size cooker feed?

Quote:
Originally Posted by Grae79 View Post
did u pluck that off the top of ur head Easy?

No. He asked me.
Bane is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-02-2008   #14 (permalink)
Cirrus
Guest
 
Posts: n/a
View Cirrus's Photo Album
Default Re: What size cooker feed?

 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-02-2008   #15 (permalink)
Bane
Respected Member
 
Join Date: Jan 2008
Posts: 908
View Bane's Photo Album
Default Re: What size cooker feed?



He did. Ask him.
Bane is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-02-2008   #16 (permalink)
rumrunner
Guest
 
Posts: n/a
View rumrunner's Photo Album
Default Re: What size cooker feed?

Sorry CIRRUS NOT WISHING TO DISAGREE BUT I CANT SEE WHY YOU CANT USE MINERAL FOR DOMESTIC WORK ,IVE USED IT FOR LISTED BUILDINGS AND FOR COMERCIAL KITCHINGS AND AS LONG AS IT IS INSTALLED CORRECTLY IS THE BEST JOB YOU CAN HAVE ,I WOULD DO IT ANYWAY AND BILL WHOEVER
ATVBITWWW
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-02-2008   #17 (permalink)
Cirrus
Guest
 
Posts: n/a
View Cirrus's Photo Album
Default Re: What size cooker feed?

nah, MI is old hat now and only used in chemical situations / petrol stations etc. There is no way anyone would consider using it on domestic nowadays
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 01-03-2008   #18 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: What size cooker feed?

Easyfox is right with his diversity calcs

dont you guys use this as standard?????

i have lost count of the number of sparks i have had to explain this too, what is even more surprising is the number of them that GENiUNELY hadnt heard of it before.

And why 10mm?

or even 6mm?

or even 4mm for that matter??????

if theres no BS1363 outlet in the CCU, by Ib In Iz you could put it on a 25A 60898 and run in 2.5 assuming method 1 (27A)

even 4mm could be considered as 'throwing excessive copper' at the problem!!!!!

ho, hum. we live and learn!

Last edited by Shakey; 01-03-2008 at 09:57 AM.
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 01-03-2008   #19 (permalink)
Grae79
Senior Member
 
Grae79's Avatar
 
Join Date: Jan 2008
Posts: 245
View Grae79's Photo Album
Default Re: What size cooker feed?

go for it....be able to cook some wee roast tats on the 2.5 when you're making sunday dinner.

where do you get the 25A 60898's from?
Grae79 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 01-03-2008   #20 (permalink)
Cirrus
Guest
 
Posts: n/a
View Cirrus's Photo Album
Default Re: What size cooker feed?

Well, the standard is to use 6mm in domestic situations and this is why the council spec 6mm with 10mm for larger cookers. We have to use 10mm as a matter of course on our showers too. We don't normally have to worry about applying diversity or any calcs because the emphasis on council jobs is speed so the brain work is generally done for you. You aren't trying to tell me thet you would be happy recommending 2.5mm to a customer with a cooker rated at 61A max?

 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Cooker Zs zero 0hms Mike P General Electrical Discussion 3 05-10-2008 06:40 AM
17th edition cooker regs bluecallum General Electrical Discussion 3 08-07-2008 03:41 PM
Wiring 13 amp single oven and ceramic hob to cooker radial adrianpaulwood General Electrical Discussion 11 02-06-2008 09:03 PM
diversity on a cooker ring kita Wiring, Theories and the Regulations 8 14-04-2008 09:47 PM
Taking Your feed to switches trickster77 General Electrical Discussion 9 20-01-2008 05:30 PM

Google Search
Google

All times are GMT +1. The time now is 07:02 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38