Old 01-03-2008   #21 (permalink)
markthespark
Member
 
Join Date: Jan 2008
Posts: 42
View markthespark's Photo Album
Default Re: What size cooker feed?

id stick a 10mm in and bang it on a 40amp breaker shud do the trick
markthespark is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 01-03-2008   #22 (permalink)
Cirrus
Guest
 
Posts: n/a
View Cirrus's Photo Album
Default Re: What size cooker feed?

Yeah, I have pulled in 10mm and ordered a 45A RCBO
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 01-03-2008   #23 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: What size cooker feed?

Quote:
Originally Posted by cirrus View Post
Well, the standard is to use 6mm in domestic situations and this is why the council spec 6mm with 10mm for larger cookers. We have to use 10mm as a matter of course on our showers too. We don't normally have to worry about applying diversity or any calcs because the emphasis on council jobs is speed so the brain work is generally done for you. You aren't trying to tell me thet you would be happy recommending 2.5mm to a customer with a cooker rated at 61A max?

Cirrus and Grae

think you may be missing the point gents.

Firstly why would cooking the sunday dinner make any difference.? So even if its an electric hob, main oven goes on, gets up to temp, cycles on and off, some time later rings go on the boil the spuds THIS IS CALLED DIVERSITY. 61A max would be oven, grill, fan everthing, and most ovens wont let you!!! (they have this thing called a sector switch on the front!)

And Cirrus, I assume you are familiar with ring mains. So lets say you've got a small ring with 10 doubles on it. That's 26A per outlet, so that's 260A max for the ring - but you are happy to reccomend that to a customer on 2.5 mm cable???? even connected as ring thats only 54A!!! But we dont pull 260A do we? and why not? DIVERSITY

sort of knocks your 61A max into a cocked hat, dont it!!!!

Note to forum members: look up diversity in the dictionary!!! Or even BS7671!!!!

And no, i generally wouldnt use 2.5 for a cooker, because it doesnt allow for changing the appliance to a larger one later, and is cutting it 'to the wire', but it doesnt mean i would blindly throw in 6 or 10mm either

And yes you CAN get 25A Type B 60898's. Trouble is, not many people use them (or know the exist!)

And this whole thread has proved my point. Gentleman, if we also blindly throw 6mm into a cooker, 10mm into a shower and only ever use 6, 20, 32 or 40 A MCB's we get to the point where we lose the skill to actually work these things out when we need to - as proved here.

Now and again just sit down and do a calc on that circuit, before you just become, effectively, electrical labourers

i get annoyed when i see this trade dummed down to the point where anyone could size up a circuit just by reading a leaflet from B&Q or Wickes

Rant over with

And well done to Easyfox for stating a simple diversity equation that should be common knowledge

Last edited by Shakey; 01-03-2008 at 02:50 PM.
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 01-03-2008   #24 (permalink)
Grae79
Senior Member
 
Grae79's Avatar
 
Join Date: Jan 2008
Posts: 245
View Grae79's Photo Album
Default Re: What size cooker feed?

are you working to the 17th edition then cirrus?

and as for that Shakey...possibly the most patronising reply i've read yet....well done u!

Last edited by Grae79; 01-03-2008 at 02:52 PM. Reason: Automerged Doublepost
Grae79 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 01-03-2008   #25 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: What size cooker feed?

Quote:
Originally Posted by Grae79 View Post
are you working to the 17th edition then cirrus?

and as for that Shakey...possibly the most patronising reply i've read yet....well done u!
Sorry Grae

didnt mean to patronise, i'm in crap mood because her car just failed the mot. need new discs and pads. Threw the money to the guy to get it done 'cause i just dont have the time. Then sat there for an hour and a half waiting to get it done. Then realised i could have done it myself in that time anyway, and saved myself a wodge.

And now she's onto me to clean the cooker......which is probably on 2.5mm cable
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 01-03-2008   #26 (permalink)
Cirrus
Guest
 
Posts: n/a
View Cirrus's Photo Album
Default Re: What size cooker feed?

Well that told me! I agreew ith you on one point Shakey - it is too easy to simply get sucked in as an electrical labourer on these council rewires as all the thinking has been done for you. That is why I liked commercial and Ind work so much as it made me think. Still, rewires pay well.

Grae - I am working to 16th until June when 17th officially comes in I guess. Why?
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 01-03-2008   #27 (permalink)
EasyFox
Respected Member
 
Join Date: Sep 2007
Posts: 443
View EasyFox's Photo Album
Default Re: What size cooker feed?

Quote:
And well done to Easyfox for stating a simple diversity equation that should be common knowledge
Why thank you
I did have to re-read the first posts, thought it was a wind up .....or am I just sad being able to remember the diversity calc/equation

Have just read the other posts & feel a bit of a numpty because I also did the cable calcs but not knowing what the ocpd was didnt post the calcs.
Anyway I binned the idea of using 2.5mm purely on the grounds of...well I dont know why.. so a lesson learnt there, nice one shakey just goes to proove dont just do it because thats the way its always been done

So I was left with 6mm or 4mm (didnt bother with 10mm why waste money) & because I'm in business to make a profit I went for 4mm .

Well that was all hypathetical but enjoy working such things out...keeps the old grey matter ticking over, as Shakey said we can all just put 10mm or 6mm in as thats how its been done & just passed down to the next generation of sparks, & the art of working such things out is slowly being lost to your average house basher.

Thinking back to an old college lecturer he always said
"Using diversity sometimes means smaller conductors, smaller protective devices, smaller switch gear but always a bigger proffit"
EasyFox is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 01-03-2008   #28 (permalink)
Cirrus
Guest
 
Posts: n/a
View Cirrus's Photo Album
Default Re: What size cooker feed?

Seems the trade is changing and not necessarily for the best
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 01-03-2008   #29 (permalink)
Grae79
Senior Member
 
Grae79's Avatar
 
Join Date: Jan 2008
Posts: 245
View Grae79's Photo Album
Default Re: What size cooker feed?

Quote:
Grae - I am working to 16th until June when 17th officially comes in I guess. Why?
just curious...cos you said were putting it on RCBO.
Grae79 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 01-03-2008   #30 (permalink)
Cirrus
Guest
 
Posts: n/a
View Cirrus's Photo Album
Default Re: What size cooker feed?

The council have insisted in this case because there are no spare ways in the new board on the rcd side so they want it on non-rcd but with an rcbo in place.

 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Cooker Zs zero 0hms Mike P General Electrical Discussion 3 05-10-2008 06:40 AM
17th edition cooker regs bluecallum General Electrical Discussion 3 08-07-2008 03:41 PM
Wiring 13 amp single oven and ceramic hob to cooker radial adrianpaulwood General Electrical Discussion 11 02-06-2008 09:03 PM
diversity on a cooker ring kita Wiring, Theories and the Regulations 8 14-04-2008 09:47 PM
Taking Your feed to switches trickster77 General Electrical Discussion 9 20-01-2008 05:30 PM

Google Search
Google

All times are GMT +1. The time now is 10:23 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38