Default What size cooker feed?

Was wiring a kitchen yesterday and the guy is having an electric range cooker installed and I needed to get a feed to it. The councils ask us to put in 6mm t&e as standard but will sometimes agree to 10mm. However, this cooker is rated at 14.1kW!!!! I calculated that at about 61A. Now surely I can't be expected to try and install 16mm t&e and worse still - terminate it in the cooker? I appreciate I have to factor in diversity but -
What is worse, his main cut out is only 60A and he also has a 10kW shower, 4 ring mains as well as the usual lighting circuits, water heater etc..
The council will not pay for 16mm so instructed me to pull in 10mm and leave it at that. Your thoughts chaps?

 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-02-2008   #2 (permalink)
rumrunner
Guest
 
Posts: n/a
View rumrunner's Photo Album
Default Re: What size cooker feed?

Good question ,how does it work out if you wire it in micc,maybee you can satify everyone that way
i dont do this type of work and didnt bother finishing the 16 edition course ,due to head blow off ,so please treat it as a sugestion rather tham a solution
atvbitwww
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-02-2008   #3 (permalink)
Cirrus
Guest
 
Posts: n/a
View Cirrus's Photo Album
Default Re: What size cooker feed?

Nah, they wouldn't entertain pyro as it's domestic.
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-02-2008   #4 (permalink)
Grae79
Senior Member
 
Grae79's Avatar
 
Join Date: Jan 2008
Posts: 245
View Grae79's Photo Album
Default Re: What size cooker feed?

what's the diversity calc for cookers? don't have osg to hand.
Grae79 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-02-2008   #5 (permalink)
Cirrus
Guest
 
Posts: n/a
View Cirrus's Photo Album
Default Re: What size cooker feed?

Nah, neither do I and yesterday it was a case of too many differing opinions. AGA reckon 10mm is fine and even 6mm would just about be ok too!
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-02-2008   #6 (permalink)
Grae79
Senior Member
 
Grae79's Avatar
 
Join Date: Jan 2008
Posts: 245
View Grae79's Photo Album
Default Re: What size cooker feed?

was just looking at some ranges on t'interweb....similar sort of spec...they recommend connection through 45A conn/switch.

how long's the run?
Grae79 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-02-2008   #7 (permalink)
Cirrus
Guest
 
Posts: n/a
View Cirrus's Photo Album
Default Re: What size cooker feed?

Run is only 4 metres max
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-02-2008   #8 (permalink)
Grae79
Senior Member
 
Grae79's Avatar
 
Join Date: Jan 2008
Posts: 245
View Grae79's Photo Album
Default Re: What size cooker feed?

not too bad really...i mean 10mm's rated at 63A using ref method 1. so with diversity in effect would've thunk would be ok, but don't quote me on that. better off doing sums and what-not, obviously.
Grae79 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-02-2008   #9 (permalink)
EasyFox
Respected Member
 
Join Date: Sep 2007
Posts: 443
View EasyFox's Photo Album
Default Re: What size cooker feed?

Quote:
Originally Posted by Grae79 View Post
what's the diversity calc for cookers? don't have osg to hand.
First 10amp of rated current then 30% of the remainder
Dont forget to add 5amp if sso on ccu.

25amp with diversity
30amp if socket on ccu
EasyFox is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 29-02-2008   #10 (permalink)
Grae79
Senior Member
 
Grae79's Avatar
 
Join Date: Jan 2008
Posts: 245
View Grae79's Photo Album
Default Re: What size cooker feed?

did u pluck that off the top of ur head Easy?

Grae79 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Cooker Zs zero 0hms Mike P General Electrical Discussion 3 05-10-2008 06:40 AM
17th edition cooker regs bluecallum General Electrical Discussion 3 08-07-2008 03:41 PM
Wiring 13 amp single oven and ceramic hob to cooker radial adrianpaulwood General Electrical Discussion 11 02-06-2008 09:03 PM
diversity on a cooker ring kita Wiring, Theories and the Regulations 8 14-04-2008 09:47 PM
Taking Your feed to switches trickster77 General Electrical Discussion 9 20-01-2008 05:30 PM

Google Search
Google

All times are GMT +1. The time now is 08:08 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38