Default Replacing a consumer unit.

Hello all,

A bit or a lot of advice would not go a miss on this little nugget.

I have recently become self employed as an electrician. The NICEIC application is winging it's way to me right now (obviously not before the bunsen has been charged). I have the assessment to contend with. I am totally green as far as this is concerned. There are 2 of us involved and decided to go down the NICEIC route.

During telephone conversation with sales person, I elected for the consumer unit assessment, and then a socket at fellow self employed persons abode. I have no problem changing the consumer unit from a practical sense, but as far as the NIC is concerned could you please give me all the advice you find applicable to my situation.

While I can hear people having a bout of Tourrettes at seeing the NICEIC acronym in front of them, a little piece of enlightenment wouldn't go a miss on what I should expect from said organization.

Regards

JOC

Johnocd is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 05-03-2008   #2 (permalink)
EasyFox
Respected Member
 
Join Date: Sep 2007
Posts: 443
View EasyFox's Photo Album
Default Re: Replacing a consumer unit.

Well firstly make sure the cu meets IP4x sure as eggs is eggs he/she will check it (did on my last 2 assessments)
If TT arrangement on the incommer cu setup as 100mA s type rcd up front & 30mA rcd for sso's.
Make sure the conductors are in number order on earth / neutral terminals in relation to ocpd (should be anyway but they do check, did on my assessment last year).
Ensure labels are present & correct & not forgetting circuit schedule, You can buy self adhesive ones of NICEIC, but I just do an excel doc then laminate it & stick some double sided tape on the back & fix near cu.
You'll most likely be asked to test PSCC/PFC & Ze (they've never failed to ask for that yet).

Got to go out for half hour so if you want more say & i'll post later
EasyFox is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 06-03-2008   #3 (permalink)
Johnocd
Junior Member
 
Join Date: Mar 2008
Posts: 3
View Johnocd's Photo Album
Default Re: Replacing a consumer unit.

Cheers for that easyfox.

I know that they are not there to hinder (apparently) but don't want to look like a numpty!

So am I correct in saying that I can crack on and install a board and get this socket at other address done before they attend? Any info you can think off will be useful.

JOC
Johnocd is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 06-03-2008   #4 (permalink)
EasyFox
Respected Member
 
Join Date: Sep 2007
Posts: 443
View EasyFox's Photo Album
Default Re: Replacing a consumer unit.

Quote:
So am I correct in saying that I can crack on and install a board and get this socket at other address done before they attend?
You'll have to, they only want to see completed work. Dont forget it's notifiable work (CU change), so you will need to inform LABC & pay their fee.

Quote:
don't want to look like a numpty!
If you take it steady ask questions of the assessor, know what you are doing when testing & know what the results mean & have completed the work to comply with BS7671 then you'll have nothing to worry about.
Remember you wont be asked anything that isnt in the regs in one form or another.

Things you'll need for the assessment:
(1) Documents; part P doc / BS7671 / EAWR / osg
(2)Test equipment / calbration certs / your own system for checking accuracy of test equipment
(3) Install certs, those that you have issued & unused certs.
(4) proof of public liability insurance to the value of £2 million
(5) list of electrical work completed & certs issued.
(6) complaints log, even if you havent had any complaints
(7) Health & safety policy
(8) cup of tea.

Possible questions:
You'll be asked about the earthing arrangements of both properties.
For the socket:
You'll be asked about max dissconection time allowed. Be asked to test or explain the test for R1+R2. Asked to test Zs & rcd.

For the cu:
Main thing is you'll be checked for safe isolation, do it wrong & he'll fail you there & then.
Remember, check on known live source, isolate & check dead, check on known live source again (use the meter side of cu main switch for known live source if you dont have a prooving unit).
Be slow & methodical about the testing & I find it better to give a running comentry on what I'm doing (keeps him informed & reminds me whats next)
Like I said dont be afraid to ask questions or his preffered method of doing things..IR test would they be ok with P/N - E or do they want it done P-E , N-E , P-N ( we all know that it should be the former but it show you know either can be done under some instances)

Sorry if some of the above is like sucking eggs for you but I thought others may get some benefit if I posted all I could remember.

Anyway must go & swot up on the regs 2382-20 comming up soon + assessment with Mr NIC next month. Boy did that ever come round quick again

Quote:
IR test would they be ok with P/N - E or do they want it done P-E , N-E , P-N ( we all know that it should be the former but it show you know either can be done under some instances)
And the mistake is?????????????????

Last edited by EasyFox; 06-03-2008 at 11:46 PM. Reason: Automerged Doublepost
EasyFox is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 07-03-2008   #5 (permalink)
Bane
Respected Member
 
Join Date: Jan 2008
Posts: 908
View Bane's Photo Album
Default Re: Replacing a consumer unit.

EasyFox is cooooooooooooooooooooooooooooooooool.

Bane is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
consumer unit upgrade CUDABOY General Electrical Discussion 11 17-09-2008 01:32 PM
Consumer Unit Change. spud4dd Inspection, Testing and Certification of Electrical Installations 3 27-08-2008 03:39 PM
consumer unit change/move montybaber Wiring, Theories and the Regulations 11 10-08-2008 04:28 PM
Electric Shower & Consumer Unit within my flat Southsider General Electrical Discussion 11 04-08-2008 10:46 PM
Consumer Unit (RCD Triping) londonelec General Electrical Discussion 20 28-07-2008 10:52 PM

Google Search
Google

All times are GMT +1. The time now is 06:31 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38