Old 13-03-2008   #1 (permalink)
Pat Tester
Junior Member
 
Join Date: Aug 2007
Posts: 14
View Pat Tester's Photo Album
Default 32A ring

Can someone confirm longest legth for a ring main using 4mm singles P,N & E that can be run without exceeding max voltage drop or Ze ?

I have a length in mind, but don't wish to appear a twat, so will await some answers and then nod my head in agreement

Thanks in advance

Pat Tester is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 13-03-2008   #2 (permalink)
Grae79
Senior Member
 
Grae79's Avatar
 
Join Date: Jan 2008
Posts: 245
View Grae79's Photo Album
Default Re: 32A ring

i've got about 105m for max voltage drop of 9.2V; using 32A for Ib and clipped direct.

take it you mean Zs not Ze?
Grae79 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 13-03-2008   #3 (permalink)
Pat Tester
Junior Member
 
Join Date: Aug 2007
Posts: 14
View Pat Tester's Photo Album
Default Re: 32A ring

Yes Zs, I must try harder, another self inflicted wound coming up as punishment
Pat Tester is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 13-03-2008   #4 (permalink)
Grae79
Senior Member
 
Grae79's Avatar
 
Join Date: Jan 2008
Posts: 245
View Grae79's Photo Album
Default Re: 32A ring

for 105m i get 1.36Ω for Zs...which is OVER the max. of 1.2Ω (1.15Ω for 17th). using a TN-C-S supply and a 32A type B 60898.

therefore the length of the circuit would need to be reduced to bring it into compliance with the max Zs. (would do the math but have had one of those days )


Max circuit length to comply with both voltage drop and Zs is: 88.6m (83.4m for 17th)

Last edited by Grae79; 15-03-2008 at 10:04 AM.
Grae79 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 13-03-2008   #5 (permalink)
MacSparky
Senior Member
 
MacSparky's Avatar
 
Join Date: Feb 2008
Posts: 114
View MacSparky's Photo Album
Default Re: 32A ring

Quote:
Originally Posted by Grae79 View Post
i've got about 105m for max voltage drop of 9.2V; using 32A for Ib and clipped direct.
Would you mind explaining your method for this Grae! only i am doing this at college at the moment and got a completely different figure.....

Get off my planet...
http://www.mysportydate.com/
MacSparky is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 13-03-2008   #6 (permalink)
Grae79
Senior Member
 
Grae79's Avatar
 
Join Date: Jan 2008
Posts: 245
View Grae79's Photo Album
Default Re: 32A ring

what'd u get? 26.1m? 52.3m? none of the above?
Grae79 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 13-03-2008   #7 (permalink)
MacSparky
Senior Member
 
MacSparky's Avatar
 
Join Date: Feb 2008
Posts: 114
View MacSparky's Photo Album
Default Re: 32A ring

16.1 m based on table 6D2 osg methods 3&4 .....pat tester mentioned the 4mm in singles!

Get off my planet...
http://www.mysportydate.com/
MacSparky is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 13-03-2008   #8 (permalink)
Grae79
Senior Member
 
Grae79's Avatar
 
Join Date: Jan 2008
Posts: 245
View Grae79's Photo Album
Default Re: 32A ring

hope that helps.
Attached Files
File Type: doc Doc1.doc (17.0 KB, 31 views)
Grae79 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 13-03-2008   #9 (permalink)
Shakey
Guest
 
Posts: n/a
View Shakey's Photo Album
Default Re: 32A ring

Quote:
Originally Posted by Grae79 View Post
for 105m i get 1.36Ω for Zs...which is under the max. of 1.5Ω. using a TN-C-S supply and a 32A type B 60898.
yep 1.36 for Zs. Tabulated value of 1.5 (1.44 in 17th edition)

so max value that you be allowed to read on the circuit is 1.12 ohms, and so the 1.36 would not comply. thats why we dont design to the maximum!
 
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 14-03-2008   #10 (permalink)
MacSparky
Senior Member
 
MacSparky's Avatar
 
Join Date: Feb 2008
Posts: 114
View MacSparky's Photo Album
Default Re: 32A ring

Thanks Grae.... very helpfull cheers


Get off my planet...
http://www.mysportydate.com/
MacSparky is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Max floor area for ring question cornburn Wiring, Theories and the Regulations 6 22-09-2008 09:23 PM
Visualising Cont. of Ring Final Conductors test Carter Electrical NVQ's & Courses 3 27-08-2008 10:19 AM
Lighting spur off ring main Earthy General Electrical Discussion 4 11-08-2008 06:54 PM
Help New Kitchen Ring on 17th linzilou72 Wiring, Theories and the Regulations 12 11-08-2008 05:26 PM
diversity on a cooker ring kita Wiring, Theories and the Regulations 8 14-04-2008 09:47 PM

Google Search
Google

All times are GMT +1. The time now is 09:41 PM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.0.0
(c) 2008 Electricians Forum | Electrical Forum | A forum for electricians in the UK

COMMUNITY SPONSORS

 Electrical Courses

Electrical Courses by Able Skills

Electrical Courses by Construction Skills College Limited

Electrical Courses by TradeSkills4U

Trusted, Rated, Approved Tradesmen!

Find Trusted Tradesmen

SPONSORS WANTED

Sponsors ABOVE keep the forum free to use. Some offer special rates to forum members too.

OTHER LINKS

Find an Electrican
Electrician's Register Here FREE
Trusted Tradesmen
Electrical Reference



Electricians Forum is the UK's bussiest and friendliest electrical forum. Electricians forums is growing by the day and is a trusted website when it comes to providing Electrical Advice. Our most popular forums are the Electrical Discussion Forums, Electrical Training Forums, Electrical Wiring Forums and the Electrical Installations Forums. Please bookmark the Electricians Forums - Electrical Forums - Electricians Forum. Checkout our Electrical Reference website, and feel free to register on Find Trusted Tradesmen .co.uk under the Rated Electricians section.


1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38