a client needs a 32a single phase commando installed so they can charge the forklift via a 7.2kw charger.

There is currently a redundant ring circuit adjacent, tested ring continuity and a is ok on the 32a RCBO.

Apart from sounding a bit piky can anyone see anything unsafe with the temporary arrangement?
 
a client needs a 32a single phase commando installed so they can charge the forklift via a 7.2kw charger.

There is currently a redundant ring circuit adjacent, tested ring continuity and a is ok on the 32a RCBO.

Apart from sounding a bit piky can anyone see anything unsafe with the temporary arrangement?
 
You will have a fully loaded circuit for the charger on its own and presumably long periods, the legs of this redundant ring,they may have difference in the shared load
Maybe split the ring at that point and check the difference in the resistance of each leg,see if its going to stress any one side,
then consider blanking off any other outlets
 
433.1.204 states accessories to BS1363 may be supplied through a Ring Final Circuit. A "commando" or "ceeform" IEC60309 socket is designed to BS4343, not BS1363 - therefore should be on a radial circuit.
 
That is Mable.
you remembered her name! That means a lot that does westie.
Has she settled in now.
No man. It's a long and very sad story, but I had to let her go to another owner, due to family pressures and my own impetuous actions when I got her as too-soon replacement for my previous dog. Shes doing just fine though, and probably forgot about me now. Thanks for asking anyway matey.
 

Reply to Commando socket question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
1K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
504
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
1K
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
596

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock