Today I have three 13A 30mA RCD plugtop adaptors to test - two around 5-7 years old and one brand new. When testing these I insert a Seaward NTB1 isolation transformer to prevent tripping any upstream CPDs.

The two old adaptors would not energise when connected to the isolation transformer, however they would energise when connected direct to the mains (they were both immediately tripping, indicated be the repeated 'clicking' sound when connected to the isolation transformer.) However the new adaptor energised as normal when connected to the isolation transformer.

I then took the questionable two adaptors and tested them connected direct to the mains and they both gave good readings, tripping within acceptable times for I and 5I at 0° and 180° (also - as expected - tripping an upstream RCD).

Tests carried out with two separate instruments, a Megger MFT1741 and a Kewtech KTD50, gave the same results.

This has left me confused...
- if the isolation transformer was at fault, why would the third (new) adaptor energise?
- if there is another problem with the two old adaptors, then what could that problem be, since they give credible results when tested without the isolation transformer?

Any help & suggestions welcomed.
 
Last edited by a moderator:
Two RCD's in 'series' as it were will always give problems.
Is the upstream rated at 30mA as well?
Manufacturing differences, ambient temperature, other external influences can affect the operation. One might trip at 29mA, the other at 31.
Can the upstream RCD be removed? If not, why use plug in adaptors, the protection is there.

I cant answer what might be wrong with the transformer, but you test RCD's so that they function properly in everyday use, and in everyday use they will be plugged into the mains, not through a transformer.
 
Two RCD's in 'series' as it were will always give problems.
Agreed - this is why I have the NTB1 isolation transformer. I test several hundred of these RCD plugtop adaptors using it every year without problems.

Can the upstream RCD be removed?
No, that is on the main board for the office & workshop

If not, why use plug in adaptors, the protection is there.
We don't use the adaptors, they belong to the customer that has brought them to us for ISITEE, along with other leads and equipment.

I cant answer what might be wrong with the transformer, but you test RCD's so that they function properly in everyday use, and in everyday use they will be plugged into the mains, not through a transformer.
As above, the transformer is only used whilst testing, to prevent the board to the office & workshop repeatedly tripping.
 
Yeh. I thought about it after I posted. Testing RCD adaptors from another location.
So you've done hundreds of these tests with the transformer and these are the only problem ones?

Install a test socket without RCD protection. Label it accordingly.
Or just say the adaptors failed and tell client to get new ones.
 
I am going to 'Pass' them on the basis they gave good readings to all 6 tests (½I, I and 5I) when connected to the mains, which as you rightly state, is how the customer will be using them for everyday use.

For my own sanity, I'm trying to fathom why they won't energise when connected to the isolation transformer, when the new one, incidentally by the same manufacturer (SMJ) will energise.
We stock them for resale and I have opened another two new ones and they energise on the isolation transformer, as expected. Just these rogue two that don't!
 
The older adaptors may have neutral / earth voltage detection that is preventing them operating if the output from the NTB has any deliberate series impedance between the secondary neutral and earth. I've no idea what is in those little boxes, never felt the need to use them because I always test RCDs load-line-to-supply-neutral which does not risk tripping any upstream protection.
 

Reply to Plugtop RCD Adaptor test problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All, Weird matter happening here and I hope you can help! My 3 Pahse EC Fan is connected to a sensor and a controller for the temperature...
Replies
2
Views
861
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock