Problem appears to have been resolved. One of the homes NOT affected has admitted that he has had a problem over the past few days with a socket that has a short. He has repeatedly tried it and reset when tripped. The timings have been checked and match. It still shouldn't happen though, that is, other houses having their RCDs tripping. Very strange. Thanks to all for input.
 
Only guess really - but to trip the adjoining installation RCD implies the fault current is seen over there too, implies local earth not working?
 
how about this for a theory, not really 100% convincing, but ... the fault on another phase would pull that phase and the neutral closer together. Even with similar impedances i.e. no loose neutral, on N and that L (call it L1), the N would move away from L2 and L3. I.e. an overvoltage on those phases.
This overvoltage would last until the fault protection kicks in on the faulty circuit, which could be up to 0.4s for a socket circuit.
If that overvoltage causes extra leakage somehow, the RCDs would trip on the other phases.

If it's not TN-C-S then this could all apply to the installation earths instead.
 
Problem appears to have been resolved. One of the homes NOT affected has admitted that he has had a problem over the past few days with a socket that has a short. He has repeatedly tried it and reset when tripped. The timings have been checked and match. It still shouldn't happen though, that is, other houses having their RCDs tripping. Very strange. Thanks to all for input.
Thank you for letting us know, and have to say, I was kind of right.
 
Static vans do not usually have hook ups, they are hard wired into a supply from a meter in a building around 20-30 mtrs max from the static and the DB in the van is where the trips are, hook ups are for tourers not fixed statics, that said I do not doubt there are statics somewhere connected to a hook up, and as Tel said a lot of supplies to the meters and switches feeding the vans are PME, well around here anyhow.

Dont know how this comment should be aloud to stay on forum, have you ever worked on any static caravans cos ur talking complete bs!!
 

Reply to RCDs tripping at several properties in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
A few weeks ago I posted this in another thread...: The tripping kept occurring, so I went back and moved a likely candidate circuit to the...
Replies
2
Views
1K
Hi All, I have a 1950s rental house with a 100 amp main panel with a main shut off breaker. Breakers are Eaton/Cutler Hammer type, so the...
Replies
2
Views
952

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock