Discuss Isolated Board but still live in the The Welcome Forum area at ElectriciansForums.net

Brendo

-
Reaction score
2
Any advice would be greatly appreciated on this.

Visited a job the other day where the light circuit had blown at the board. We Isolated the mains and tested but neutral bar remained live. Found that a rogue twin and earth with its neutral was on the bar and was live however the line conductor had been disconnected previously.
Could anyone's experience shed some light on what might be going on that although the mains was isolated this had happened.
 
What are you measuring the voltage with. The rogue neutral may still serve a purpose for a circuit from another source so you will get potential from neutral to earth with your board isolated.
 
It's a Duspol Voltage tester which I use to make sure the mains was isolated before getting my fingers stuck in. I did think the rogue TandE might be from the communal stairwell lighting
 
Are there any UPs on the insatllation, safe isolation, also includes backefeeds from other sources, could be worth checkng.
 
No UPs on site at all. I've disconnected it now and all communal lights remain functional. Begs the question why it's there to begin with
Need to find out where it goes/comes from, or find out what doesn't work when it's disconnected.
 

Reply to Isolated Board but still live in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi there, Any advice on this would be greatly appreciated! (Note, this is not a DIY, I'm using a fully qualified electrician, just posting here...
Replies
8
Views
591
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
Hi all.. Bit of a nightmare afternoon,, testing a caravan park TP&N panel board IR testing while board isolated before returning power (merlin...
Replies
5
Views
911
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
735

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock