Discuss Intriguing problem. Shower and Cooker tripping CB not RCD in the UK Electrical Forum area at ElectriciansForums.net

Andy C

-
Reaction score
19
Opinions on this fault please, I have never come across this before.

Split RCD board with a shower (40 amp) and Cooker (32 amp) both on 6 mm T&E. Both are tripping the CB, apparently whilst switched off? RCD tested fine.

Shower is a 9.5kw, so feasibly the 40a might be a bit close to max, fed from a 45 amp pull switch.

Cooker is about 5.5kw so a 32a is fine, fed from a 45 amp double pole switch in a cupboard. The cooker is definitely tripping whilst switched off at the cooker? Not straight away but a few minutes later. No other load on circuit.

I haven't tested the appliances. Both are relatively new.

Both circuits have been tested from DB to isolating points at 45 amp switches and IR results were fine.

Thanks in advance for any suggestions.
 
Is it the RCD tripping? If so then the fact that the current rating us near its limit is not the problem. Don't forget it could be a neutral to earth fault.
And cumulative leakage could be a factor.
 
I'm confused, you say it's not tripping the RCD and yet you say RCD tested fine??
Why test the RCD if it's not that tripping? Also can you provide some clarification that the circuits are tripping their respective MCB's whilst the appliances are isolated?
 
I'm confused, you say it's not tripping the RCD and yet you say RCD tested fine??
Why test the RCD if it's not that tripping? Also can you provide some clarification that the circuits are tripping their respective MCB's whilst the appliances are isolated?
Thanks for the reply. To clarify. The RCD is not tripping when the MCBs formthe cooker and shower trip out. I have done IR test to isolators from DB, readings all good.

The cooker mcb is tripping whilst the appliance is switched off on the appliance front.
The shower tripping might just be a coincidence.

I will test from the isolators to the appliances to rule out any fault there.

What I can’t get my head around is the cooker tripping a 32a mcb whilst switched off unless the appliance is somehow faulty.
 
The cooker mcb is tripping whilst the appliance is switched off on the appliance front.

Not on the Isolator on the wall, or wherever?
So the there is still a supply into the cooker casing?
Are there any obvious issues within the cooker, assuming the above 2 statements are true?
 
Just to clarify does these MCB's trip with the cooker and shower switched off but isolators switched on?
What is the insulation resistance in this state (note the caution L-N)
What make is the consumer unit & MCBs? open mind on the tired MCB's theory never experienced it myself not saying its a possibility on cheaper brands.
 
I experienced the ‘tired’ MCB on a shower circuit.
You go there armed to the teeth with test gear and after testing and proving good, disconnected at the shower, you knock your ladder and the MCB trips! Reset, tap the CU and it trips - I made the most of the situation and sourced the correct make MCB for the CU replacement instead of the BG that was fitted.
Granted this is the only time it’s happened so far but some things do come under the acronym K.I.S.S
 

Reply to Intriguing problem. Shower and Cooker tripping CB not RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’m going to call an electrician out on Monday, but curious if anyone has any ideas about this fault: I have a new kitchen fitted and two...
Replies
10
Views
2K
A friend's partner has an interesting fault, if it is a fault. She sets the shut down timer on the cooker and when the timer goes off (which in...
Replies
9
Views
785
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
614
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
227
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock