Discuss Main 185mm earthing query in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
22
Hi guys bit of knowledge needed..
Have a 2x185mm 3phase supply going to a panel board with 800amp main switch from a UK Power networks transformer about 15m away, also run with them a 185mm earth which goes to a earth bar next to the panel board where all the outgoing swa earth overlays are connected also. What size earth should go to the panel board a 185mm as that's the size of the incoming earth and theain switch is 800amps or can it be smaller like a 70mm as the outgoing earth's are all connected to the earth bar..
Some thoughts on this would be great.. Thanks
 
The adiabatic equation is not needed for line conductors over 35mm so as long as the earth cable is the same material as the line conductor the earth will need to be at least half the size of the line conductor feeding the panel.
 

Reply to Main 185mm earthing query in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hi, This post is about my concerns with medical IT socket outlets and want to alert you all if you are fitting them in a hospital. The current...
Replies
20
Views
2K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock