This is beginning to do my head in.
Power-One state that an AC type 300ma RCD should be fitted on the AC circuit when using an Aurora transformerless Inverter. This we did on an install that was assessed for our MCS accreditation. However we were pulled on the fact that the AC cable ran behind plasterboard for 2 metres and may not be more than 50mm from the surface. We were told that we should fit armoured cable as there was no 30ma RCD on this circuit and this would then meet the requirements of BS7671 17th Edition.
Correct me if I am wrong, but I think every new circuit has to be protected by a 30ma RCD under 17th Edition. This then conflicts with the recommendations from Power-One who state that the reason for fitting the 300ma RCD is "This will aim to avoid wrong protection trips, due to the capacitive leakage current related to the PV modules and that will be present because of the transformer less inverter’s topology."
Fitting a 30ma RCD in the circuit would negate the usefulness of the 300ma unit and lead to nuisance tripping which has been raised in another thread.
To meet the Assessor's requirements we will simply fit armoured cable for that part of the AC cable which is behind the plaster board.
Can someone put me right or suggest how we can connect in the AC circuit and meet both the requirement for the 300ma RCD and the requirements of 17th Edition.
Power-One state that an AC type 300ma RCD should be fitted on the AC circuit when using an Aurora transformerless Inverter. This we did on an install that was assessed for our MCS accreditation. However we were pulled on the fact that the AC cable ran behind plasterboard for 2 metres and may not be more than 50mm from the surface. We were told that we should fit armoured cable as there was no 30ma RCD on this circuit and this would then meet the requirements of BS7671 17th Edition.
Correct me if I am wrong, but I think every new circuit has to be protected by a 30ma RCD under 17th Edition. This then conflicts with the recommendations from Power-One who state that the reason for fitting the 300ma RCD is "This will aim to avoid wrong protection trips, due to the capacitive leakage current related to the PV modules and that will be present because of the transformer less inverter’s topology."
Fitting a 30ma RCD in the circuit would negate the usefulness of the 300ma unit and lead to nuisance tripping which has been raised in another thread.
To meet the Assessor's requirements we will simply fit armoured cable for that part of the AC cable which is behind the plaster board.
Can someone put me right or suggest how we can connect in the AC circuit and meet both the requirement for the 300ma RCD and the requirements of 17th Edition.