Earthing and Bonding Definitions

It is essential to understand the difference between earthing and bonding.
Earthing is defined in BS7671 as: “Connection of the exposed-conductive-parts of an installation to the main earthing terminal of an installation”.
Equipotential bonding is defined as: “Electrical connection maintaining various exposedconductive-parts and extraneous-conductiveparts at substantially the same potential”. (N.B. referred to as bonding throughout this document).

Both of these functions are carried out using protective conductors (as defined in the BS7671 Regulations). Protective conductors for Earthing are known as Circuit Protective Conductors (CPCs), protective conductors for Bonding are known as Bonding Conductors and may be either Main Protective or Supplementary.
The Earthing Conductor is defined as “A protective conductor connecting the Main Earthing Terminal of an installation to an earth electrode or to other means of earthing”.
For a TN systems the means of earthing is either a Protective Multiple Earthing (PME) terminal or a separate conductor which may be the cable sheath. In a TT system the means of earthing is the earth electrode which must comply with the requirements of sub-section 542.2.
The definition of an extraneous-conductive-part is “a conductive part liable to introduce a potential, generally earth potential, and not forming part of the electrical installation”. Isolated metal door handles, shelf brackets, metal windows etc, are unlikely to be extraneous-conductive-parts.
Author
Sintra
Downloads
76
Views
1,051
First release
Last update
Rating
0.00 star(s) 0 ratings

More resources from Sintra

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock