100ma

  1. 1

    100mA Main RCD Cut Out before 17th Edition Consumer Unit?

    Just a quickie please:thumbsup If a seventeenth edition consumer unit (with 30ma RCD's) is fitted after an already installed 100mA RCD will there be any discrimination issues? The reason I ask is because I'm sure I remember a while back when I was doing a job with somebody else that the MAIN...
  2. G

    100mA Type S RCD as Main Switch on TT Zs of 188 Ohms wouldn't trip.

    I was testing the above RCD yesterday on my Megger MFT1553 using the Autotest function set to the correct trip range of 100mA but I couldn't get a response from the RCD even at x1. At this point, the meter would simply flash <50V. I then retried the test using the manual functions but still got...
  3. L

    Using 2 100mA RCD's for essential and non-essential circuits and nuisense tripping

    Hi All. I'm working on a project in Northern Ireland. The supply is protected by a 100mA RCD which is regularly triping due to many items of our plant have high earth leakages. We have a large IT area, which, as many of you will be aware of, has a high earth leakage. We also have a good few...
  4. M

    100ma rcd tripping times please???

    Does anybody know the tripping times for a 100ma 100a rcd, x1 and x5 many thanks for your previous help earliar.......................;)
  5. M

    100ma or 30ma??????????

    Hi Everyone, a quick question for you all, if on discovering a property had no main incoming earth, there were no earth block (tnc-s) to connect off either, you installed an earth rod and the reading was acceptable below 200 ohms, i think, what would you use on your fuseboard for your main...
  6. M

    100mA / minor works

    A domestic TNS installation has a 100mA RCD main switch and 'Type 2' MCBs. I Need to move a kitchen socket away from a hob, install an additional one, install a fused spur unit for an extractor hood, and move two light switches to the other side of a room. The customer is a right pain and it...
  7. D

    100ma rcd tt

    Just checking, Did a PIR earlier for a mate and his rental property is TT cpvered by 100ma RCD wired in accordance with what ever reg was out at the time..! ZS @ 100ma = 500 ohms...?? am i correct !!??? cant remember top of head..!
  8. I

    TT 100ma Rcd + earth electrode??

    Hi al,l I am working on a tt system at present. I am going to be a adding a new d/b which will be ran from an existing board which has a 30ma main switch, controlling 1 other circuit i need to change the main switch to 100ma and the 1 circuit its controlling will need changing to a 30ma rcbo as...
  9. B

    TT 100mA question

    Hi fellas quick enquiry regarding the above. Went to an installation yesterday with this layout: cut out - 60A metal switched fuse - plastic consumer unit. All equipment fitted at a height of 2.8 meters, all conductors and main tails in trunking. Does a 100mA RCD need to be installed to...
  10. K

    100ma RCD

    If a building has a 100ma RCD unit as a main switch would you insist on a 30ma one also to protect socket outlets on a PIR main switch as an rcd doesnt comply anyway. im thinking code 3 Also a spur taken of a spur ive coded as 1 as its a fire risk imo, would you agree?? no main water bond...
  11. D

    100mA rcd

    Can a 63/100mA S type rcd be used for ring circuits (16th edition install 3 rings rcd protected) failed on the TD setting passed on non time delay?? MAC
  12. S

    WYLEX 100mA 80A RCD

    Hi all, Does any one know if a WYLEX 100mA 80A RCD WEM 80/2 is time delayed. It currenty protects a TT system and I will be upgrading the consumer unit to an 17th edition unit with 2X30mA RCD's. I worried about discrimination, and dont want it tripping before the 30mA RCDS's I know removing it...
  13. S

    replace 100mA RCD

    Hi, I have a job lined up to update a consumer unit, It is a TT system, there is a 100A 100ma RCD unit between Meter and the consumer unit, the customer wants this removed. If I fit a Slip board consumer unit, 100A mains switch and 2 X 80A 3oma RCD so all circuits are coved by 30ma RCD, is...
  14. L

    CU split board - 30ma / 100ma , problem or not a problem?

    been looking at a cu today, sum of us had a discussion about rcbo's n rcd's. Righty, what we have is a split board, 30ma rcd on one side, and 100ma s type main switch on the other. Got Cb's on the 30ma side which is fine, but on the 100ma side theres 2 x 30ma rcbo's. Now does this contravy...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock