U.S. Highway 16A (US 16A) is a 36.971-mile-long (59.499 km) scenic United States Numbered Highway. It is an alternate route for US 16. It splits from US 16 in the Black Hills of the southwestern part of the U.S. state of South Dakota. The highway's western terminus is an intersection with US 16, US 385, and South Dakota Highway 89 (SD 89) in Custer. The eastern terminus is at an interchange with US 16 called Keystone Wye south of Rapid City. Portions of US 16A are known as the Iron Mountain Road, named after the peak it summits.

View More On Wikipedia.org
  1. gobananas

    aircon cable size

    hi....im running cable for a split type 1.5 hp aircon....i have a roll of english 2.5 twin & earth, is this ok for the job? im running it to the fusebox into 16A breaker.....the run is about 5 meters.....
  2. P

    Fitting 16A hardwired oven to 32A cooker circuit

    Hi all, I'm new on here.... I have an existing 32A cooker circuit with a wall switch with 13A plug hole.The manufacturer says the new oven is hardwired and is 16A. Can I just replace the breaker in the consumer unit with a 16A one and use the existing wiring? Current breaker is a Proteus...
  3. gm1984

    UK 16a oven on 20a fused spur from Kitchen ring main

    Hi, I've just bought a new built-in 3.4kw oven = 14.8A @ 230v. I'm getting 245v so actually 13.8A. Existing oven plugs into single socket fed from 20A DP switched fused spur. Ring is small (3 double sockets) with 4 x 20A DP switched fused spur single sockets (oven, washer/dryer, dishwasher...
  4. C

    16A device on a 15A breaker, do I need to replace the breaker?

    I'm going to have to replace my faulty EVSE car charger with a new one. The Clipper Creek one is pretty pricey, so I'm looking at a much less expensive Zencar. The concern is that it says it requires 16A. My garage has a single 15A breaker for it that's in the house, but I don't know the size...
  5. Sparked Out

    Spur off a spur.... make safe with 16A MCB from ring?

    Just recently has some work done on a conservatory, and in the process discovered that the 2 double sockets are not part of a ring main... looks like one is a spur off the back of a ring socket in the main house, and the second is a spur off of that :eek: So, question is, if I replace the ring...
  6. F

    16A oven ok on existing set up?

    Hi all, I appreciate that this is a question that has been answered a lot but each response I could find was for slightly different set up to mine, so hoping you guys might be able to advise. If any work is needed I will get an electrician out, but don't really want to take time off work and...
  7. H

    Replacing 13A flex outlet with 16A

    Hi, I'm replacing a microwave oven rated at 13A with one rated at 16A. This plus a conventional oven are fed from a 32A MCB in a consumer unit, via a single 6mm2 T&E cable to two 13A fused flex outlet switches. The original installation was professionally done seven years ago. Can I replace...
  8. J

    Replacing single 13a plug in oven with 16a fixed wire on 32a dedicated circuit

    Hi all, Thank you in advance for your help. This is my current setup: 32a MCB to 45a CCU with 6mm^2 wiring (no additional socket at CCU) 6mm^2 wiring to two separate sockets behind kitchen units (one for gas hob ignition one for 13a plug in oven, nothing else on circuit) My new oven is 3640W...
  9. D

    Armour cable ran to garage on 16a breaker

    Hi Everyone, I have armour cable running from my house to my garage in a new build, it is connected to 2.5 that connects to my consumer unit, can i put a socket before armour cable for my wifes new battery hoover without any adverse effects? its protected by a 16a breaker then runs to garage...
  10. P

    Lights wired into 16A radial circuit

    I've discovered that one of the bedroom lights in our 1930's 3 bed semi have been wired (I guess as a spur) into the upstairs 16A radial circuit. Similarly the light in the porch extension at the front of the house are on the 16A radial too. I know the best solution would be to wire correctly...
  11. Richard Burns

    16A ring oh no its a radial

    Sorry to put this up as I do not have enough information, just after some thoughts really. Have a house where they want some additional sockets and looking at the CU (16th edition) there are two 16A circuits with two cables (2.5mm2) coming out from each, OK I thought two 16A RFCs, bit odd. In...
  12. S

    16a MCB/Water Heater

    Right theres a good chance I could be picking this up wrong, but I'm sure this was what was said. Boy in my college class said he spurred off a water heater circuit (3kw) for a socket for a 2kw fire. Surely this can't be right?
  13. P

    Looking for MEM QEB/QB 16A MCB?

    Can anyone help? got old MEM Memera 21 board , a 16a mcb broken (type 1) . Wholesalers can't supply under £40.00 as now (type 3). Halfway through Level 3 CG2330 (Confident to change/upgrade board). At this stage would rather replace Mcb? ,any advice very grateful.
  14. M

    Size of Flex for 32A CEE / Comando Plug to 2 x 16A CEE / Comando Trailing Sockets

    Hi Guys, Firslty i'm new to the forums so hello and hope you're all doing well. A quick question on the size of the HO7 flex I need to use for a splitter that will have a 32A Comando Plug on one end and two 16A Sockets on the other. Would I be right in saying that each split will need 2.5mm...
  15. C

    Garage Radial on 16a MCB

    Am i allowed to install a radial circuit that supplies 1 single and 1 double socket in a garage with 1.5mm cable? It is unsheathed cable in plastic conduit (ref method B). From the BRB this has a Current Carrying Capacity of 17A. It is on a 16A MCB and the load it supplies will be a freezer...
  16. B

    16A 4 pin wall socket

    This is my first post so Hi to all I have to wire in a couple of 16 amp 3 phase wall sockets in a work shop. The ones I have been given are 4 pin. If I run Line 1, Line 2, and Line 3 standard brown Black Grey I am guessing the 4th pin is for earth and power is between each phase? Just...
  17. A

    Abb mcb 16a

    Does anyone have an ABB MCB 16a i could buy off them? I have been to my suppliers and they want £75 for one as ABB have a minium order of £50 plus p&p or does anyone know if any other makes fit?

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock