I was carrying out an r1+r2 today and when disconnecting the cpc out of the earth bar to link worth the line it sparked on removal from the earth bar....
I tested between the cpc and the earth bar and got 120v
Tncs earthing arrangement
I've carried out insulation resistance test and that was...
hi avery1 need your help i done new rewire and theres proplem with lighting circuit,iinsulation resistance between LN-earth IS 120 useing megger mft1533,and same problem with same circuit getting 48volts between switch wire and earth with switches off...please p;ease help me :crazy:
Went to a job yesterday where a previous spark had upraded db to dual rcd fair enough job look to standards but customer told me spark had done no eicr? Is this acceptable? Is there a loophole in system?
Hi All, a customer asked me to look at his supply to the garage which had been installed by previous owners. The garage is approximately 2 maybe 3 metres from the house and as far as I can tell is fed from 2.5mm T&E spurred off the ring. The cable exits the house through the wall about 2 .5...
I want to add a second fluorescent fitting in my garage. The wiring I require is not an issue but the routing between the two fittings is. The reason is that the integral garage has a plastered ceiling as there is a bedroom above. Although the fittings will be only about 1.5m apart, there are...
My solar-inverter has an in-built AC battery charger ( 220V, 50Hz) as well. Specs of Inverter are 2000 Watts, 48vDC.
I have installed Panels of 1200Watts @ 48VDC
During day-time, some days are such that my power consumption compared to Solar Energy being made is low, and my batteries are...
digimart
Thread
automatic
between
incoming
mains
power
solar
switch
switching
Evening all,
I'm about to start a couple of biggish jobs and need to think about getting customer to sign order for works agreement.
How should it be laid out? Does anyone have a template they use that I could have?
Thanks
egginyourface
Thread
between
customer
electric
electrical
electrician
signed
Good morning all,
Apologies if you have gone over this a number of times before (I have tried searching for a thread, and have found some that have touched on what I'm after but not quite explicitly enough).
If the measured PFC is greater than 6ka (for example) with circuit-breakers' breaking...
kitleach
Thread
between
breaking
capacity
circuit
fuse
mcb
pscc
service
short
Hi
If anyone can help,I am carrying out an EICR on part of large hospital and have found voltage that varies between 100 and 200v between live and neutral on one single phase submain cu. It is present when main switch is off so is on load side. Apparently they get voltage around 0v to 60v...
I just had a 4kW system installed.
It uses the Samil Solarriver 4000TL-D inverter which has 2 DC inputs. There are 2 strings of 8 panels, each going to one input of the inverter.
All the panels have the same aspect and zero shading in the afternoon so I'd expect them to supply the same power at...
Hi Guys
I've just completed my first 3 phase installation. A 3 phase CU (Proteus) in a church extension. There are 12 x 230V circuits feeding sockets , lights, heaters, etc.
1. Do you record all circuit test results on the same page or use one page for each phase?
2. Do you record Zs at DB...
I have spent quite a bit of time today trying to understand why I am only getting 0.654Mohms on the upstairs lighting between Live and neutral (at 250V)!!!
L-N 0.654 Mohms
N-E 25.11 Mohms
L-E 24.7 Mohms
I get almost the same when measured at 500V (cant remember exactly but about 0.6Mohms)
I...
Hi guys, looking for abit of help.
Carried out a consumer unit change today, carried out all dead testing etc, all came back ok.
New board is a twin 63a RCD.
With the following configuration both RCDS tripped straight back out.
RCD 1 *upstairs lights
*Downstairs sockets...
Hi all, l recently did a eicr on a fish and chip shop.
3 phases (only one phase in use by chip shop). Earth conductor is welded together to each phase by TN-S earthing system means.
When it came to the IR test, l tested the norm tests, L-E, L-N & N-E.
Bearing in mind that we are now supposed...
Jabbajaws
Thread
between
board
circuit
conductors
ir test
test
tests
wylex
Hi, iv changed an outside light for a customer and completed all the necessary tests. After powering up I got 230v between L and N but strangely 120v between L and E. The tests were done at the jb prior to the light fitting. Any ideas what could be causing this?
Thanks in advance!
Hi. I've tried to fit an Optima Compact alarm panel with built in key pad. Upon energising there is a tamper fault. I've removed all zones & linked them out but still no joy. This is the reason I hate doing alarms & will avoid in the future! Any ideas please??:devil:
simbin
Thread
between
compact
engineers
fault
optima
panel
return
tamper
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.