My fluke T140 past away this week and now looking for a new tester.I was very satisfied with the T140, very practical and fast.
My dealer have only the new T150 at 190euros.On ebay is aprox 160.
Before ordering a new one was thinking to ask here and see what you are using ? If there is any other...
I'm doing an continuity test on a lighting circuit and I'm getting funny readings I'm putting on test lead on earth and one on switch live then I'm getting a reading of around 1.4 ohms but then when I'm checking the polarity it's shooting up to around 93 ohms but not breaking the circuit as you...
Hey,
I've just past my trade test and was placed on a new build to complete the 2nd fix
as the guy who roughed it has left.
Anyway, he's wired the lights using the loop method at the switches, I've never did this
previously as I would always do the joint at the ceiling rose, this has thrown me...
Hi guys, I have recently bought a Fluke 1652C and I am trying to work out how to carry out testing (course coming up soon) however I am a bit stuck with a continuity test I wanted to do on a ring circuit and would appreciate some help !
I was lucky enough to have an empty flat so carried out...
MikeWindsor
Thread
circuit
continuity
help
help please
please
testing
Iv just complete an eicr. I have a few queries.
1. Page 2.part k.I'm unable to get hold of the details for the Characterisitics of primary supply over current protection devices- can I put lim in these boxes.
2.page 2. Part L. Main protective bonding. There's no bonding as the mains water...
6mm singles from 100a TP 60947-2 in a main panel to an adcent enclosure to a 16a 60898-D Tp, then 6mm leaving this to air con units. Would you code 2 the 6mm singles from the 100a 60947-2? As exceeds current carrying capacity?. Or because the 6mm singles are less than 3 metres to the enclosure...
Hi
There seems to be some confusion at work about ring circuit continuity on an EICR. I was under the understanding that you took r1 & r2 added together and divided by 4, then during the live testing a Max Zs was measured using meter. The method two or 'figure of eight' is used only on Initial...
As you know it all happens at once, lost voltage tester, volt pen ain't working and all I've left is neon driver:hammer:
So question is any Of you seen any good deals recently. I was thinking fluke t5 or any you suggest
Does anyone else have problems with there continuity readings my readings never seem to be stable for example a newly installed ring end to end resistance on neutral and line ill get .46 and then a reading of .04 on line end to end the leads are always nulled and I even check readings on calcard...
Hi peeps
I have continuity measurements on a ring final circuit of: L/L 1.4, N/N 0.78, E/E 1.7
Loose connections somewhere?
There is a new CU with RCD.
Insulation resistance measurements are good.
There is a boiler added into the circuit as a spur.
Any suggestions or comments?
THANKS!!
:) :) :)
Hi
Running a quick test on a lighting circuit today, was doing R1 + R2 on downstair lights. Everything seemed OK, but upon trying to prove polarity by using switches obviously upon switching off the circuit goes open but when tried switching on again and testing again I got a wildly...
Hello all,
I have just done a pre-works visit for a CU change and found continuity between neutral and earth!!
This is a TT so I didn't think I needed to disconnect the main earth but after getting continuity between N-E I did, I also disconnected main bonding but still getting N-E continuity...
Hi all I keep having problems with my fluke the continuity readings are all over the shop never stable I always check my readings on a calcard before testing and when nulled I get correct reading i will test it on calcard 5 minutes later and it's half an ohm out so never know if I am getting an...
Can somebody help im going to take my 2394 in February and as far as filling out certificates and sequence of tests im not too bad, but as im still a student and still learning im just a little unsure on a few tests and why there within a certain sequence.
So why do you check continuity of...
Replacing cracked cover on ring circuit, the mcb was turned off , circuit dead
tested with volt meter and got beep continuity on L-N L-E N-E, .
Ring working before replaced the socket front .
Im thinking because appliances with neons pugged in on the ring
and it being TNC system that this...
Can anybody tell me the sequence of testing that's stated in BS7671? At college I've been taught CRIPES, which is:
Continuity
Ring final continuity
Insulation resistance
Polarity
Earth loop impedance
(functional) Switching
Why are these carried out in this specific order?
Haydenr25
Thread
before
being
bs7671
circuit
continuity
polarity
sequence
testing
Changing a CCU and reconnecting existing wiring (twin and earth) = did a N - CPC IR test for earth leaks prior to dismantling the old (BS3036) unit for obvious new RCD trips; all ok.
However, on ring circuit the continuity end-to-end readings of the R1 and Rn are 0.3 ohms different; 0.41 on...
Good Evening all,
Been at a property today starting intial tests for a board change tommorow. There are two ring circuits, on one of the ring circuits i had an open circuit on the cpc. Live and neutral where fine 0.4/0.4. I started to locate the break by splitting the legs and joining the live...