I am currently painting my sister's kitchen. She used to have a visor-style cooker hood which was so old and grubby that she had it taken away a few months ago (by a joiner...). To my surprise, when I opened one of the cupboards during painting, I noticed that what he has done is unscrew the the...
Hello everyone, I am no domestic electrician but I do work as a designer in the railway, low voltage signalling circuits etc. My question concerns my oven. I have just bought a second hand double oven of the internet and went to fit it in my rented house. The existing oven is connected using a...
I recently had a large renovation project carried out and electrical work by the builders own electrical contractor. I have a problem with my chimney extractor over gas hob...it's not extracting sufficiently and smoke is filling the room. There are no blockages and we now think it is because the...
Hi, quick posting - welcome any advice as new to this stuff...
Have a Howden HJA 0150 gas grill/oven with a broken thermostat that and can't get a replacement (grill igniting but no gas coming out of oven burners when on).
The Howden grill/oven is on a ring in the kitchen which has following...
Hi all,
Looking for some advice if possible please!
Got one if then jobs that you get roped in to and that’s turned from a quick simple tasks to maybe a small can of worms.
The customer wanted her oven connecting as curry’s have installed the hob but not the oven.
Cooker circuit -...
Hi
Hope someone could help, I have a Smeg induction range cooker that randomly trips the switch to all the plug sockets in the house but never trips the switch the cooker is on, we have had an electrician check the wire from the cooker to the mains and all came back OK and a specialist smeg...
hi all,
i recently bought a flat and got a years old cooker hood in it.. which i am trying to replace..
all done but the connection inside it does not have power... tried all the switches on and stuff but still no joy..
any place where is should check .. or how to find the fault or where the...
Just been asked to reinstate a cooker point.
Existing feed is checking out perfectly.
However, the existing back box has top and bottom lugs ~135mm apart.
I'm assuming that this is an old imperial box.
Can anyone suggest what faceplate is appropriate?
Yes, yes, next time I take a photo...
When selected on, thermostat light not coming on also fan not turning Oven is cold and fan can be hand turned any ideas of fault. your help would be appreciated. Con checked the thermostat switch (all fine). other ovens and grill are operating fine. wire diagram is a bit complicated.
Hello,
DIY enthusiast, but no real skills! Our fan oven stopped heating so I thought I would replace the heater element. When I have taken it apart, it looks as if part of the wiring may have come off. There is a clip on the right hand side with no wire coming from it. Will this be the issue...
Disconnected a cooker ready for a kitchen to be removed, and found this.
Freestanding cooker with 4 rings, oven and grill.. rated 11.3kW, supplied by what looks like 1.5mm flex.
I know take diversity for cooking appliances, but 1.5 is pushing it a bit.
Just wondered if this was original to the...
I've been trying to locate anything in the regs that say this can't be done, but can't see anything.
Basically I have a 3kw oven on a 4mm T&E cable going to a 32A MCB (Cable is clipped direct in loft to consumer board, and not covered by anything en-route - property is a bungalow). The isolator...
Hello lads .
Not seen the job but my old buddy the plumber has informed me today he has replaced an old cylinder with an unvented .
Alarm bells are ringing im going to ring the cylinder manufacturer on monday to clarify a few things but im concerned about achieving positive shut off .
I...
Hi,
We have an old cooker on the mains with a cooker mains red switch with a normal plug next to it.
The red switch is in the off position as is the plug switch.
Whenever I reset the RCD for the cooker ring in the fuse box, the entire RCD trips again - even if the cooker's red switch on the...
Hi There,
I've just discovered that my rangemaster dual fuel cooker is plugged into a socket under my kitchen unit with a 13amp plug.
I've not had a problem with it until today. The cooker was installed when I purchased the house back in 2014.
Today I was using both the grill and cooker as I...
The customer has asked for a cooker hood with some kind of heat exchange. I'm not entirely sure what he wants, but I'm guessing it's a cooker hood which reuses the hot air, i.e an MVHR. This is the only one I can find though and it's ridiculously expensive Lo-Carbon Sentinel Kinetic Cooker Hood...
Hi
we are about to re do our kitchen and am looking for information on the hard wireing for the built in cooker as we want to move it! Can I buy new cable and lengthen the cable from the cooker to the wireing point and have the cable running around behind the cabinets? If not how much would it...
Hi All
I had some new wiring put in professionally and I asked to wire ready for a cooker. He has left me a cable from the floor where I said it was going but no switch. When I went to buy a cooker with install included it said on the website they would only install it if there was a cooker...
Hi there.
I’m looking for some professional advice.
I recently bought Beko Cooker model KDC653S, it doesn’t come with the electricity cable and according to the manual it require H05W-FG 3X4mm or equivalent with total power consumption of 10KW.
I called all local shops including electricity...