disconnection

  1. S

    RCD disconnection times on 2018 forms

    Evening all, happy Friday! On the new forms there is only one column for RCD disconnection times. I understood you would just record the highest of the 5x readings but on looking around to confirm I found this article on Professional-Electrician: "The model forms in Appendix 6 have been...
  2. J

    Changes to the requirements on recording RCD disconnection times

    Hi everyone, long term visitor to the forum but first time posting a question... be gentle This question is with regards to the changes to the 18th edition certificates, which only require one disconnection time recorded. When recording the highest value taken when carry out RCD tests, Reg...
  3. spud1

    Disconnection time of a 32Amp Cooker circuit with a panel socket?

    Hi, What would be the Maximum disconnection time for a 40Amp domestic Cooker circuit in a TNCS system be, where it has a 13A socket outlet on the panel/isolator faceplate? Obviously a final circuit >32A would be 5 secs but I was just interested as to whether the presence of a 13A socket outlet...
  4. sham

    looking through previous certificate and have a question about disconnection time.

    On a domestic inspection and testing certificate or conditional reports, I always put maximum disconnection time permitted by BS7671 as 0.4 sec. I've been given a testing job for an HMO property and on the previous conditional report, the maximum disconnection time of 0.4 sec is only given for...
  5. R

    Automatic disconnection of supply

    Can the above method alone be classed as basic protection according to 131.2.1 it can. Based on that regulation you can leave live terminals exposed if supplied by a 30mA RCD
  6. R

    Disconnection times for finals

    Just received a completed test sheet from an installer on a TN system with the max permitted disconnection time column filled in for the lighting circuit and 20A heater circuit as 5secs, surely 0.4
  7. P

    Disconnection times help

    Hi all just a little bit of advice at the company i work has just had a condition report done and they have marked down excessive zs for a 63a type d breaker but they have put it at 0.4 disconnection time it is a permanent fixed compressor I thought this would have been 5 sec it also has a b.s...
  8. John Lundrigan

    I'm confused about Type C Breaker Disconnection Times

    Hi All, When I consult Table 41.3 for a Type C Breaker rated 16A I see s max Zs of 1.37 Ohms. However this value is defined for both a 0.4s AND 5s disconnection time. This is obviously correct so I am missing something. Fig 3A5 also shows the table 0.1s to 5s. Can anyone explain please...
  9. S

    Deadly Disconnection here in Minorca!

    Presently on holiday in Cala Blanca, Minorca and came across this situation. The meter box is built into a wall outside a now disused restaurant along the pavement, the door is completely missing and the clear plastic cover over the 4 wire cut out has been broken and removed. It would appear...
  10. Bob Geldoff1234

    NIC QS Assessment charge

    Not long had my Approved NIC/EIC assessment and had to be QS assessed.This took an extra half a day(on top of the other half a day for the yearly assessment).Just got the bill for the half day charge.......£366!:eek::mad::( Feel ripped off or what. Have any of you guys had to pay this fee?
  11. Edtwozeronine

    Homework help

    I'm looking for the section in my on-site guide that covers disconnect times for circuits over 32a. In my regs class my homework features a circuit with a type B 45a RCD. EDIT: oops never mind I now see it says anything exceeding 32a must not be more than 1 second. I thought there was a more...
  12. B

    Maximum disconnection times

    Hi does anyone know max disconnection times on tn-s system for: 16A radial 6A lights 32A distribution Cheers
  13. M

    Would you replace this RCD?

    This is a new RCD, came in the CU. The max disconnection time I need to comply with is 400ms (Table 41.1 TN ac 230V). From a new RCD I'd expect something roughly in the region of 30ms (for a 30mA fault test). What I'm getting is 234ms (x0.5 there's no disconnection and x5 it's a 13ms...
  14. Z

    Verifying SWA CPC suitability disconnection times / adiabatic equation

    As you may know looking at some of my posts I've been thrown back in the deep end recently – and don’t have much experience with complicated calculations. As this is the first time I've used SWA to go from the main supply to the primary CCU, and as I'm using the steel armour as my CPC, rather...
  15. 1capybara

    Table 41.3 Max earth fault loop impedence (Zs)

    The heading of table 41.3 says it shows " max earth fault loop impedance Zs for Circuits Breakers..... giving compliance with 0.4s disconnnect time of 411.3.2.2 and 5s disconnnect time of 411.3.2.3." 411.3.2.2 is for final circuits not exceeding 32A. 411.3.2.3 is for distribution circuits and...
  16. H

    disconnection times for 100mA BS61008 on a tt system

    Gents, tested a pub split load db today in the sticks. before i commence any work, am i right in stating anything over 0.1 on the 100mA side is a fail? did a test on the man 100mA and its disconnecting in 0.25 I've tested the sockets on the 30mA side and they are disconnecting correctly. Pubs...
  17. M

    Disconnection times with off grid application.

    Hi All New to this forum and fairly new to the business too. I have a project I'm putting together which is an off grid house. There are two 5000VA inverters with sufficient battery size and a sizeable generator to switch in once loads exceed about 7kW, which will ADD a further 100A. Here's...
  18. M

    NICEIC Certification Scheme help filling in niceic test certs please

    The test cert is for a transportable building I have fill in a test not done it since college, i dont know what to put in the max disconnection time for Bs60898 MCBs protected by a 63A 30ma RCD main switch, no circuit exceeds 32A is it 0.4s for a TN system is it 0.2s for a TT system or 300ms...
  19. S

    RCD test

    hello every one can some body help me please in this particular question?When tested at Idn time 5 , a 30nmA RCD protecting a 230 V a cooker circuit incorporating a socket outlet in its control unit must trip within : time please
  20. D

    DISONECTION TIMES- Circuit Ratings

    Stupid question that i need answering. How do what your circuit is rated at? I know that if its above or below 32A there are different disconnection times depending on the type of earthing system

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock