Completely electrically illiterate :gorgeous:: all power was switched off apart from the fridge/freezer and wine cooler when we went on holiday for a week came back Saturday turned on the power all went on except the 1 x MCB for the downstairs ring, which runs the front room and dining room...
Looe21
Thread
boiler
circuit
downstairs
mcb
power
removed
ring
ring circuit
socket
still
tripped
so end to end L-L 0.4 N-N 0.4 E-E 1.1 very reasonable ,
but when the l-n are crossed over at the consumer unit . ok down stairs but the reading goes up to 16 ohms upstairs
but when l-e are crossed over at the consumer unit the last four sockets upstairs give no reading. at this point i am...
Hey guys,
What are peoples thought on a single socket for a free standing electric radiator in a downstairs cloakroom. It is a normal size downstair cloakroom with a toilet and small hand basin and nothing else in it.
Would I be right in thinking the regulation would not oppose a socket in...
Hi All
New to this forum.
Im currently doing a Electrical condition report on a domestic house that I have just fitted a dual RCD board and Equipotential bonding in
The Neutral on the landing light is taken from the downstairs circuit so is a C2 on the report
Its not practical to rewire this...
To make things worse the voltage is entering a shared Main Earthing Terminal from a separate premises with occupiers that don't seem to be that bothered about the situation. Things don't get better. In the section of the building which doesn't contribute to the voltage to the MET they've...
Evening Chaps
I've got a switching conundrum that I was hoping one of you guys could help me with!
I've been working on a heating system and the previous spark managed to run 2 pumps either together or independently with one boiler and a 2 channel programmer!
I however cannot get pump 1 to...
Hi all,
I just plugged in a (apparantly faulty) steamer, and all my plugs went off, but when I went to check out the consumer unit, everything was switched to "on" including both that are labelled "plugs down" and "plugs up"...... except this dial on the left which says "RCD connected circuits"...
Hi Chaps
Thanx to everyone who sorted me out with the last query . on to the next.
I have been asked to install a second two way switch in friends hall way. The existing switch is just inside the front door and controls the hall and landing lights as normal , what she would like is a secondary...
Young Dave
Thread
downstairs
extra
landing
light
lights
switch
two way
upstairs
I have just changed a DB and checked for the obiuos shared nutural.. Just to realise that the landing light is wired into the downstairs circuit
Is this ok or do the regs prohibit this ?
Hi all. Having moved into my house i wanted to put a nice hanging light fitting above the hall stairs. i removed the pendant thats there and tested the circuit L/N N/E L/E im not getting 240 across Live and Earth. getting 240 between L/N no probs.
Basicly i have a switch upstairs which is a...
robert0881
Thread
circuit
downstairs
earth
light
lighting
no earth
please
stair
switch
Hi, I need a bit of direction and help never really touched a heating system before and just have a few grey areas that I need clearing up.
The work I have done in the forces for 12 years has never took me down the path of heating systems now I am fine with connecting up combi's simply fcu with...
hutch6447
Thread
airing
boiler
downstairs
going
heating
plumber
system
wiring
Hello guys had a lady on the phone who said she has upstairs and downstairs ring mains, she can plug the 1400 watt vac in upstairs and its fine but she cant plug it in downstairs as it trips the RCD protecting it I am not sure never come across this?
hutch6447
Thread
downstairs
leakage
other
probably
rcd
rcd tripping
tripping
upstairs
The house I recently purchased has got the downstairs s/o on one circuit. There are 4 in the kitchen and 4 in the lounge. Does the kitchen need to be a seperate circuit? To me it seems daft just having 4 s/o on one circuit.:rolleyes2:
Hi guys
Hope you's may be able to be help me here as i am puzzled.
I have 2 sockets downstairs and two upstairs not working now, they used to work perfectly and suddenly there seems to be no power going to them. I also think one of the sockets upstairs has borrowed a neutral from the one...
Stevo90
Thread
borrowed
circuit
downstairs
neutral
problem
socket
upstairs
Evening lads.
Most of my work in new build installation but i have been asked to price for the above job. Its a large 3 bed detatched house. its going to have an up and down stairs ring circuit (3/4 sockets in each bed, 1 socket in hall and another on landing, 6 twins in lounge). it will also...
Ive been asked to do some jobs next week, they want the inverters placed adjacent the cu, is this quite common practice? i thought they would go in the loft space?
I assume to reduce the volt drop.
Am i ok to pass the dc down through ceiling in pvc conduit?
also one job is 16 panels 1 string...
Hi, I'm new the forum seeking some advice :)
My parents have just had their rewireable fuse board updated and some spotlights installed on the landing.
The problem is the RCD keeps tripping out (only sometimes) when the landing lights are switched on. Now I know you will be thinking borrowed...
Hello All,
New the game and this forum so please bear with me.
I have just changed a customers old consumer units for one compliant with 17th edition. The circuits were all muddled up and it took a while to figure out all 18 wires and what they did. However the last "circuit" which due to the...
Fitted 2 new rings and a new CCU. Got readings on r1 r2 rn end to end on both and also R1 R2 R1 RN on both but no rn on downstairs ring, it just shows open circuit. Checked all sockets for loose wiring but all ok. Any suggestions? Thanks