fuses

  1. G

    Eicr remedials

    Main switch 160a bs88fuses, 35mm tails feeding busbar chamber with switch fuses ontop feeding distribution boards. A c2 has been given to undersized main tails. I thought that because the tails are only about 400mm long from switch into busbar that it was ok? Thoughts?
  2. S

    rewireable fuses

    Can I get a 5 amp rewireable fuse from any wholesalers ? Need one ASAP !!!
  3. Q

    BS1361 fuses

    I'm doing some past papers for my 17th exam this week and have found 2 questions about bs1361 fuses - their operating times and max zs. I can't find any data in the regs about them. Am I being blind or are these questions pertaining to old regs that have been removed from the current edition...
  4. R

    750kva on 200A primary fuses

    11kv/440-750kva 3 phase tx on 200A primary fuses, spotted this at work, whats the max current per phase you can draw on the secondary without rupturing the fuses.
  5. R

    Amtech 3 phase tx load

    Just trying to work out a cable and fuse size for a 3kva 415/240v transformer with a 2kW load on it, using Amtech single cable, there are no settings for showing a transformer on the load side, is it possible to calc a transformer load on Amtech. If I use a motor as the load it chooses fuses...
  6. A

    Major or Minor Works?

    Hi, I have had 3 phase cut-out and meters for 3 flats moved from my cellar to outside meter cabinet. Sparky has installed switch fuses and around 15 metres of SWA for each flat to relink to old supply point. Work looks decent so I am not disparaging said sparks work. I have a query though. He...
  7. MerlinGremlin

    pulling the main fuse

    Evening Gents and Ladies hope all are well, just wondering if anyone can give me advice on where I could attend a training course to be qualified and authorised to remove cut out fuses. I did one many moons ago as an apprentice with the local council when I worked there, we went to Hoy Lake the...
  8. B

    What is a KMF please?...Was reading about switch fuses when extending tails. Thanks

    W n d e r e d w ha I s ta n d s f o r
  9. S

    Fuse characteristic

    Hi, I'm currently studying for both my 2394 and 2395 exams and I've been thinking of scenarios to test myself of certain theories, I thought of one where a garage board would be fed with a 13a fuse spur with only a 1.5mm armoured buried under ground. So I started thinking about fuses etc and I...
  10. N

    DNO Fuses In Flats Replaced By Dummy

    Now obviously I have not seen this with my own eyes as it would involve pulling possible DNO fuses which I would never do...but I have it on good authority that there is a certain small block of flats where each flat has, in a meter box outside the front door, its own meter and what appears to...
  11. P

    flat submains and landlords suuply

    hi ya'll got a query, just questioning my judgemet been o look at a job were a spark has done a disappearing act and work needs finishing the scenario- total rewire, new3 phase mains incoming and gas etc 5 storey building x4 new flats all new installs by the entrance ground floor x4...
  12. N

    Customer tonight wants me to replace rewire able fuses with plug in MCBS.

    Been to a job where a young couple want to replace their white sockets and light switches with chrome finished. I took a look at their CU and it is a wylex re-wireable fused board with separate RCD covering all circuits. It then became clear they had no idea what a rewardable fuse actually...
  13. Davehaywire

    Asbestos behind 3036 fuses solution needed?

    What coding would you be giving for old DBS with asbestos behind fuses? As its not affecting electrical safety? is there something you can put in place of the asbestos when removed, as its to hold in arcing or flashing when the fuse wire blows right? if you remove the asbestos does this then...
  14. J

    Separate fuses for 3phase supply

    Hi All, Just trying to double check if there's a reg suggesting a 3phase circuit should have over-current device that disconnects all line conductors at once? Got an old rewireable board supplying 3phase motors with 3 individual fuses. I'm looking at 530.3.1 ................... Can anyone...
  15. t01474

    45/50A SD5 HRC fuse needed

    Hi everyone. I'm doing some work on a farm and came across a problem. The DNO head has 60A fuses in but down stream of that is a 3 phase MEM Glasgow switch fuse with 100A fuses fitted. Obviously there is no discrimination whatsoever there so I explained that the fuses need to be downrated to 50A...
  16. S

    Memera 2000 fuse box

    Hi my house has a memera 2000 fuse box. The kind which still requires fuses to be placed in it. Recently it has been tripping on a regular basis every couple of weeks or so. I have managed to isolate the problem by pulling out one of the 30 amp fuses. This allows all other electric to be on...
  17. G

    Eicr 1361 fuses 3phase circuits from db

    Come across a DB in a workshop single 1361 fuse carriers three phase circuit. Does this go down as a c3 or c2? Potential if a fuse goes unit would stop but you would still have 2 phases at it??
  18. N

    Periodic Inspection Advice Please

    Hi Guys I have just carried out a Periodic Inspection on an installation that must be at least 30 years old I observed the following and any comments would be greatfuly received There is an old 6 way rewire able CU when the cover is removed the supply conductors are exposed even with the switch...
  19. A

    Question about fuses and power cords

    hi guys, I am in no way an electrician so apologies in advance But wondering if you could help me out. I've got a little home recording studio and have just copped a new piece of kit (a compressor) for my setup. Unfortunately it didn't come with the power cord. Power cord is just the standard...
  20. D

    DNO Supply Question

    Hi there, I was wondering if I might be able to call on the knowledge of someone with experience of three phase mains supplies from our energy provider. We are a sports club looking into the possibility of installing some new floodlighting around our pitch and are currently in the very early...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock