I might need to remove an old heater CU leaving some cable holes in the Henley block where its tails currently go. Anyone got a good suggestion for an insulating plug for those holes?
Hi there. I’m installing a secondary mini consumer box with a 40 amp RCBO.
The main tail that comes from the meter is 25mm2 and goes in to a Henley block and then another set of 25mm2 tails come out from this and go in to the main consumer unit of the house.
Mains service fuse is rated at...
Hi everyone,
I'm still training so some advice would be appreciated :)
We have a shed about 60m from the house where would like a supply. I've already ran some 2 core 4mm SWA and wired up a CU with a 30mA incomer, it will be protected upstream by a 16A MCB. I went for 2 core because I want the...
Hello peoples ?
I am installing an additional consumer unit to an installation. I’m going to stack them one above the other, normally I would use the henley blocks but I was wondering if there is an alternate solution to this? Is there any way Split the supply cables within the CU’s?
I know...
Hello.
Before I bother a professional with a call out, could I ask for some advice on here.
Our cat managed to dislodge the cut-off fuse on our board, shutting the power off. I pushed it back in and everything's back to normal. But in doing so, it made some rather nasty noises and it doesn't...
Hey Everyone,
I'm in the process of rebuilding a house in the highlands of Scotland that suffered a significant escape of water in the attic, place is trashed.
So my question on the mains in. The mains comes into a 100amp fuse then into the meter. Out of the meter is an armoured that runs...
Looked at a job today and found something which I believe to be odd.
TNCS system with tails out of the new smart meter into a small henley block. Then 1 set of tails only from the henley block into an old square d cu. The thing I found odd is that the henley block has what I assume is a DNO...
with bs7671 Amd 3 2015
is a henley block considered as switch gear and therefore enclosable in non ferous
I know it doesn't switch But an MCB wont cause an issue in the open position
i have never seen a melted Henly and its not the same plastic as the old CUs anyway
your thoughts ?
Help! got problem on site. I'm after several series 7 type fuses to satisfy BNO meter suppliers. The BG meter people want a series 7 fuse in front of each meter. Where can they be sourced from? Thanks
tried some wholesaler..no joy so far
Need help, I need to supply a 4th floor flat from a basement flat off the same meter, there is the main fuse then the meter.
I was going to put a henly block after the meter then straight up 4 floors to a fuse box, I think I need an RCD before it makes its journey up, don't know the cable I...
I have been asked to Supply & Fit a Pure Sine Wave Generator to a solicitors office for 1-2 days while the main gets switched off in the road for a building development alteration. They have been told by their IT guy it has to be a certain kind of generator due to the computers.
The Install is...
not working in the domestic sector i need help with 2 questions. firstly is it still allowed to cut into the tails between the meter and board and place a henley block in line so that i can feed a summer house as getting from the house is not an option due to doing to much damage to finished...
rover v8
Thread
blocks
henley
house
pulling
rcd
rcd's
still
summer
Right, I've been struggling with proper monitoring now for sometime, but seemed to have partly solved this now ...... however, it isnt exactly right on a conditional basis - can you experts point me in the right direction why this is happening;
OK, the tails are split straight after the DNO...
Hi,
I have quoted up a job and would like to know if anyone can see anything wrong with my design.
From the 100A main cut out the tails go to an 80A switch fuse and out of there to consumer unit.
I need to run a sub main to provide another consumer unit upstairs,whiere there is a possibility of...
nottz_spark
Thread
board
consumer
henley
main
seperate
sub main
switch