  1. J

    loop impedance on lighting circuit

    Hi everone,I am new to the forum and think its brilliant,I am currently studying for my 2394&2395 and am testing everything in sight with a fluke 1651 multi functional tester.When i try to do a loop test on a lighting circuit,I follow all the instuctions,but i keep getting >2000 ohms,i am...
  2. K

    Impedance?

    *Thread Title Correction* Impedance Hi, I'm going over some choice revision for my 2365 Lvl 3 course and have come across the question "What is the impedance of a 200V 50Hz circuit containing 8A?". Although I am presuming I need to use AC Theory, I have gone over all of my notes on impedance...
  3. B

    For Sale Megger LTW 425

    http://www.test-mete...dcXmBoChmzw_wcB Same as the above, it's a year old but has only been used 3-4 times tops. I don't think it's in calibration still, but I can arrange to have it calibrated for anyone interested. Key specs below: Will post some photos when I get home later. I think...
  4. M

    110v earth loop impedance

    My test meter only works on 230v.... So... Is there a way of working out the Earth fault loop impedance on a 110v supply that is supplied by a hardwired 110v Centre tapped to earth transformer? Anyone else come across this. I have some additional 110v sockets to fit in a workshop but need to...
  5. T

    Can you work out the value of the resistor?

    Hi guys, Just wondering if you can help me on this one, I have a RLC series circuit the values are as below; R = unknown L = 800mH C = 300uF from there I have calculated; the resonant frequency to be 10.3Hz the capacitive reactance 51.50 ohms The reason I need to know is I need to work...
  6. M

    Martindale EZ150 E-Ze check Xtra Non-Trip Earth Loop Impedance Socket Tester

    im bulding my first tool kit so i was browsing round for a socket tester and this came up. and it got me thinking how useful would the loop test even be. and wouldnt these need a calibration etc Martindale EZ150 E-Ze check Xtra Non-Trip Earth Loop Impedance Socket Tester | eBay
  7. P

    Earth Fault Loop Impedance

    Hi all, I am hoping someone can clarify if my understanding on earth fault loop impedance testing is correct. A low efli is needed so a protective decive can operate in the required time, the lower the z the quicker it will operate. ZE= External resistance from borad to supply, board...
  8. S

    trouble with 2394/2395 revision queston

    hey guys.... ive downloaded some revision questions for my 2394/95 course i have booked for august and ive come across a question im a little unsure about......even when i have used the regs and GN3 to help. a little help would be greatly appreciated as there is no answer sheet for the...
  9. J

    Earth loop impedance test on 24v dc supply

    Hi, Excuse my ignorance. I have a electrical panel with a 240v ac to 24 v dc rectifier. The outgoing circuit breaker is 63amp as the 24v d will be stepped up by a power supply unit in the next panel. Is an earth loop impedance test required for the 24 v dc supply? Thanks
  10. M

    Loop impedance test

    Hopefully someone can answer this query for me. I'm more used to domestic installations but have taken on a job in a workshop. The workshop is around 80m away from the intake which is a 3 phase TN-C-S supply. The workshop is new but I'm using an existing 16mm 4 core SWA cable. I'm using the...
  11. R

    Impedance Zs

    hi everyone I have a question: Water heater 3kw the length of the circuit is 28m , the line and cpc 2.5mm2 How determine the expected Zs? I'm looking for in On-Side Guide but I do not know..... any suggestions please Thanks
  12. spud1

    High Earth Fault Loop Impedance readings caused by RCDs

    Hi everybody, I have encountered a problem with EFL (Zs) testing a couple of times recently. I have had unusually high readings for the length of circuit and earthing system type and the increase in impedance seems to be coming from resistance across the line pole of the RCD in the consumer...
  13. S

    Ze external earth loop impedance

    Hi I've done a Ze test on a TNS system and it's come back as 0.14 ohms is this reading ok as the max is 0.8 is there not a min amount you can have thanks
  14. F

    Fault current

    Can someone explain why fault current is higher when your zs is lower trying to write down reason but struggling on what to put
  15. V

    240 but no earth loop impedance

    I'm testing a job at the minute and today I went to a double socket that has 240 at it but when I carried out a ELI test the result is a open circuit .the 240 I am getting is between L-E and the means of earthing is TT ,it's a radial circuit supplied bu a 20amp breaker totally confused??????
  16. H

    Suitable testing instruments

    Hey guys, I need help finding out which tester you'd need to test for: continuity of circuit protective conductors, earth fault loop impedance and prospective fault current. I'm pretty sure you'd use a low reading ohmmeter for continuity but I don't know the other two. Also, any requirements...
  17. M

    Earth Faulth Loop Impedance HELP!!!

    Hi can somebody shed some light upon correction factors for earth fault loop impedance. I know that the vales of zs in bs 7671 are if the conductors are running at max temp ie worst case scenario , am I right in believing that if you get a measured result you apply 0.8 to it?
  18. G

    External earth fault loop impedance Ze

    ​Can any one explains what are the three methods to find External earth fault loop impedance Ze please?
  19. S

    max measured earth loop impedance query

    Hi guys, Im just filling in my first ever solo EIC when I check the onsite guide and gn3 for max permitted zs (tabulated) for bs60898 type b 32A the table shows 1.16ohms but to me it didnt ring a bell, checking bs7671 table 41.3 shows max zs to be 1.44. Can anyone shed some light on why and...
  20. sparkdog

    Megger earth & loop impedance testing event.

    Got a letter about this free event.Anyone think its worth going to?

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock