Hi All,
Have been reading forums for years now,time came to ask for advice.
Have a job to fit main 3 phase isolator for a shop with flats above.About to 2 nd fix the flats now,when the supply is sorted.There was a single phase to the flats,done some years ago,without any isolators.Now the...
Hello
My first post on my first job...
I have just installed an extractor fan. It was going to have a timer but the house wiring is confused: the switch and light are not connected directly, instead the cables go off under the floor boards and yet the switch is 50cm from the switch??
So the...
I get regular work from a student landlord. In one of his properties the shower isolator switch has burnt out on the feed side several times. I've replaced the switch twice (last time with an MK) and the shower's also been replaced. Insulation resistance on the circuit is >500 and the MCB...
Hi guys. I've had my kitchen 're fitted and in doing so 're wired. The hob and cooker both off of 32 ampseperate breakers in 6mm cable.
The rest is on a socket loop 2.5 mm cable in to a 32 amp breaker. But linked into the loop is a 3 gang isolator grid for cooker hood fridge and washing...
Hi All
I'm trying to find an isolator that will take a class 4 security padlock for a factories roller shutter door, this is to comply with their latest insurance assessment.
Can anyone point me in the right direction please? The usual 16/32A rotary isolators do not have a big enough hole for...
Currently have feed to 16A rotary isolator, I’m gonna come of this with 2.5mm to a socket then to a fused connection unit to feed 2 lights if lid this ok
In the future I would like the upgrade the consumer unit within my flat as to be able to add additional circuits (as the current one is plastic and is tiny).
However there is no means of isolation from the incoming supply, there is also no earth from the incoming supply either which is another...
Hi Guys just replaced a 200 amp main isolator in a factory along with a replacement 3 phase board should you do an installation cert or a minor works as it's like for like
Whilst checking for a tripping RCD I found that a 13A Switch Fused Isolator, for a double socket behind a washing machine and a dryer, was giving various voltage readings when in off position, 240v when on and stayed at 240v when switched off. This video shows the problem...
Found this in the cellar of an old house in Durham...
The neutral is fused so I’m guessing it’s “really old”
Any body know roughly the era it would be?
Hey peeps,
I have a movement sensor in my en suite which turns on the extract fan. Trouble is, it's been installed so that it only triggers the fan when the light switch is on.
I want to rewire it so that the fan comes on irrespective of whether the light is on or off (but obviously still...
A question regarding the use of a mccb as a 3 phase main isolation switch to a DB.
Is it a necessity?
Current set up is I have a 3 phase 70mm supply feeding a DB.
The origin of this supply is unknown, hence I’m getting northern power out to investigate as the main cut out earthing arrangement...
Afternoon All,
Maybe an odd question. For the last 8 years I've been in this industry I have always fitted single and 3 phase disboard/CU's with locks and no remote isolator other than on a locked main panel.
I'm on a new job where we are using a mix of Siemens 3 phase boards and Crabtree...
Just joined for help - hello all :)
I am NOT an electrician, but I am able to switch off the supply to change light switches and plug whatever was in L1, L2 or Common into the new switch.
I bought a new chrome fan isolator switch today to replace a nasty plastic one however, and the markings...
Hi,
Got sent to a job today at student halls of residence. They have had 3 45 amp isolator switches blow in the last month for the zip inline water heater.
As shown in pictures, the water heater is being fed by a B40MCB and then in to a 45 amp isolation point above the door, then to the heater...
A fellow electrician wants to install a 100A isolator switch between the meter and cu. Is it correct that this also has to be metal as per 3rd ammendment. The wylex rec2 is plastic so does it need to be changed.
Of you could share your expertise please.
Just been quoted £167 + VAT for installation of a DP Isolator (by Western Power Distribution) on a domestic property I've been asked to work on!
I generally like to do things "by the book", i.e. I'm not a fuse puller....but at this price I might just change my mind.
I assume the lady I spoke...