Hi All
I have a prob i hope someone has come across
clients RCD is tripping at odd times. Doest seem to be any pattern or any specific piece of equipment causing it. Not one particular circuit either...trips on downstairs ring, upstairs ring, lightings ...you name it.
Wont reset until all mcbs...
Evening everyone,
In process for tendering for a job, 3 floors and cellar, presently 14 rooms, going to be extended to have another annex, conservatory and another extension for kitchen.
Im thinking the way to go on this one is RCBO's, splitting it so each floor has a socket circuit and a...
After some advice really..
I have the following circuits on the first RCD:
1)Upstairs Lights
2)Downstairs Ring
3)Kitchen Ring
4)Intruder Alarm
And on the second RCD:
1)Downstairs Lights
2)Upstairs Ring
3)Garage
4)Cooker
Would you have done anything differently and if so, why?
I need to provide a generator to site.
Do I check the current rating of all the
equipment to be used at this site (It
isn't a large site), total them up and
look for a generator with that load
capacity? Is it that simple or am I
missing something?
I have FOR SALE A megger 420 pat Tester 11 months old only used on my own household appliances has loads of extras printer,barcode scanner, microwave leakege tester, see the whole lot on ebay item N/o:321016668405
Can be bought for £950 the whole lot
Hi All
I would appreciate your help with the following.
I am familiar with standard calculations such as calculating the current draw on a three phase heater battery when the loads are balanced across the three phases. I have recently come across some equipment where it appears the heater...
Hi have a problem which I hope that somebody can shed some light on.
New install on existing TT supply, with two DBs fed from an SWA sub main with 100mA S type RCD and 100A switchfuse at the origin (no other loads on supply).
DB 1 is for a new install and all circuits are protected with 30mA...
Hi All
Changed a C.U today, Volex (not my choice but customer supplied it) Dual RCD, one 80A & one 63a. All test results good except on RCD test at socket outlets. on half test all OK, on 5 x test all OK but on 1 X test @ 180 no trip but fine @ 0. Ramp test ok. When tested at RCD with mcb's...
Hi,
I am dealing with alot of applications to UKPN. What would be the best way of estimating loads for this application. Am i right in thinking that for an office environment, going by the BISRA rules of thumb:
Lighting 12w/m
Power 15w/m
Heating 70w/m
Cooling 125w/m
multiplied by the floor...
sparkystu27
Thread
application
electric
electrical
estimate
loads
ukpn
Hi guys having a brain fade moment.
Any reason why I can't use C type RCBO's instaed of B?
Doing a CU change at a Nursing home and been quoted for C type, currently they're B type.
Board is 3 phase but all breakers are single phase.
Thanks in advance.
Steve.
Hi All
Got a 3 phase 20A per phase supply coming in, feeding 2 gites. The owner needs the 3 phase supply to also feed a new house 66 meters away. The house will only single phase loads and probably be unbalanced most of the time
Now the tables I have, show that for a single phase - the wire...
fjr1300
Thread
3 phase
cable
cable size
loads
phase
roman
single
single phase
size
supply
times
Just wondering after doing a job today, what is samllest fuse size you would use for sockets in a kitchen if there wasnt a washer or dryer in there ?
I put a 32a mcb with 4 double sockets and a single and when all finshed i did think with the loads present surely a 25 or 20 mcb be ok. I always...
Hi, i have a problem with an RCD in a Garage unit - 1/2 30mA no trip, 1 x 30mA >300, 5 x 30mA 17ms. Any ideas what could be happening for the 1 x 30mA test.
Cheers
I am currently training as an electrician and have been set a question and was hoping someone please explain to me how to calculate the connected load if I have a mixture of single phase and three phase loads, and I have a three phase service connection from the utility.
For instance, is the...
Hi am new to the forum, have recently become a MCS installer via NICEIC am struggling a bit to make my mind up about the design side of the job to either go for PVSOL or equivalent as i have had contact via a couple of companies that will do all the design etc and sell the kit but obviously...
Hi. I'm having a bit of trouble trying to do the calculation in BRE 489 for solar pv wind loads. I understand the equation;
F = qs x Cp, net x Ca x Aref
But what i don't understand, is what to do with the number at the end.
Do i look in say a schuco mounting rail...
Hi guys,
Customer woke up this morning with the Main switch/RCD tripped. He narrowed the problem down to the kitcken ring so He unplugged all the counter top appliances and switched all the big under counter appliances off at the switches.
I got there and turned the mcb on then plugged the...
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.