Hi,
Very new to this forum so excuse any faux pas's.
Was wondering if anyone has come across this situation: Was doing some insulation testing as part of our planned maintenance and came across a motor that gave an odd result.
Capstan Motor 440V/60Hz, 24kW, Star/Delta configuration.
Removed...
Tweaker
Thread
across
approx
between
insulation
motor
phases
results
testing
Hey guys,
Has anyone heard of bundling two phases together at the cut out. A Guy form the energy board was moving the main cut-out and told me they used to do it years ago.
Does he mean 2 cores (in the same cable) on the same line incoming form the transformer?
Surely you cant put two...
Hi All,
Just trying to double check if there's a reg suggesting a 3phase circuit should have over-current device that disconnects all line conductors at once? Got an old rewireable board supplying 3phase motors with 3 individual fuses.
I'm looking at 530.3.1 ...................
Can anyone...
Living out in the sticks. I have come across old split phase installations a few times and done a little maintenance on them. These installations usually consist of a old 3 rewireable db with only 2 phases used.
Well for the first time I have been asked to add some circuits which requires a...
I know you should put all three phases and neutral through the same opening of enclosures and not split them(two in one hole and one and neutral in other).
But i can't find the regulation for this.
Hi all,
im pricing up a job to fit 2X 6kw systems, (one per phase)
now am i better just to use 2x single phase inverters?
or 2X 2phase inverters?
need to check the loading etc to see what will benifit them best!
also, can the be ran through one 3 phase generation meter?
thanks in advance...
Hello. I'm a bit confused with the electrics on an industrial unit I'm leasing.
Ideally I'm after 3 phase - there is 3 phase coming into the building (with a 3 phase fuse box), but the previous owners wanted single phase and created a single phase set up from one of the 3 phases.
Here's a pic...
Been to specup a new install on a Server Room. They are planning on extending the serverroom for more cabinets the problem is the current DB has no more free waysand have been ruled out upgrading the board for more capacity due to shutting thewhole system down. Have been told by the IT geek...
Hi Guys, Popped over to a bungalow yesterday that a mate of mine has bought to renovate, asked me to have a look at electrics/what might need doing and I found this... 2 phases (red and yellow) in a bungalow with 2 bedrooms?? bit ott i'm thinking? lol. Although the DNO have only supplied a meter...
Hi all.
Prospective Short Circut Curret.
Now , if you measure the impedance on a installation P to N , and get a reading of 0.21 OHMS , the max current flow between these two points P and N will be 230/0.21 = 1095A.....1KA.
Now if you have 3 phases , and each are the same impedance P to N ...
I have just installed a 2 phase system with 2 Solar Edge inverters (3.7kW per phase) Each pv system is fed through a shared Elster A1100 3 phase meter and each one runs fine on its own. When connected at the same time the RCDs on both system trip. The only way I can make it work is to bypass the...
fitzsparks
Thread
generation
meter
phase
phases
problem
rcd
rcds
single
Hi all.
We're currently wiring a large domestic dwelling that has a 3 phase supply. We would like to balance phases as accurately as possible, but due to the lighting control system we have a situation where we have a 13A socket on one phase sited next to a 5A socket on another phase. These...
jjnr78
Thread
allow
apart
different
outlet
phase
phases
socket
socket outlet
I need a solution for a problem I have, just cant seem to think at the moment.
I need to shut off a 3 phase supply when a supply to one phase has failed? Now I am thinking 4 pole contactor, but I am not sure of how to monitor the 3 individual phases on 1 control circuit? 3 control circuits perhaps?
We have some work to do at a large house in the countryside,that has a two phase supply installed .There is a standby generator being fitted next week,which requires conversion from three phase into two phase,by the generator suppliers.Does anyone know if we need two neutral cables to feed the...
Anyone with experience of this or an idea please help.
I have 2 phases going going into a cab, each one 230v. However there is a real chance someone could touch the two and get a belt from each phase at the same time.
What would be the correct type of warning sign to use? Also out of...
harrison2987
Thread
correct
high voltage
phases
please
voltage
volts
warning
Hello,
We've had an issue with a 3 phase piece of equipment that was tripping the 3 phase breaker as soon as it was turned on. On investigation (by a certified electrician) he said it was the equipment at fault. I raised a return of the equipment and the new one arrived today. To be able to...
had a last minute call out to a shop today. all electrics dead, checked db first, found a fried mouse between bus bars.
no power coming into the db, checked on the meter, nothing, checked incomer fuses (100a) they good, no power going to the fuses. advised them to call to DNO.
they said...
I am doing commercial refurb at the mo, everything is supplied from an old Memshield 3 phase board, the landlord wants the various spaces metered so he can bill the tenants separatly, at present he is just adding a flat rate to the rent, I have no issues with how to go about it however one unit...
If we have 3 x 2500wp single string arrays on a 3 phase supply (split evenly over phases) using SMA 2500HF's will we need a G59 relay for sure or is it up to DNO? The SMA's are not G59 as far as I know only G83.
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.