Hi everyone I've come across a weird situation where somebody has got new sockets added, but from the board it is a radial in 6mm as there is one set of cables into the breaker, then when you look at the sockets (2 double sockets) it's got 2, 2.5mm cables going into both like it's a ring
Does...
Hi I recently ripped out a ring final circuit out of an old Proteus 3ph board. Customer only wanted a single 2G socket replaced. The MCBs are obsolete so I had to re use the C32 used originally supplied the ring.
can I use 2.5mm cable?
32A radial but with 2.5mm cable- not something you would see...
Good morning all,
is it within regulations to add a spur to a radial wired in 4mm in a kitchen if the spur is also 4mm? The circuit is on a 32a rcbo.
Thank you
I currently have an integral garage fed by a radial circuit protected by a 32A MCB and wired with 4mm T&E cable. This feeds just two power points in the garage (and nothing else).
i wish to redesign this circuit to provide several more power points and would like to check whether my proposed...
Since doing a bit of digging am i right in thinking that using jb's to branch off from a radial circuit for a single switch and associated lights is considered "old hat" nowdays. ?? Ive read the 17th ed recommends jb's be of the maintenance free type is they are non accessible, which is all...
I have one single socket on its own from a consumer unit. (10A) (no ring) Can I swap this to a double and then spur off another double from it? It means there will be an equal number of spurs than there are sockets which I have been told is a no no. Is this true?
Thanks in advance
I seem to have located a radial circuit in the loft conversion. The Circuit is the Ring circuit from the Middle Floor which supplies only 4 single sockets on the Middle Floor, 2 single sockets in each room. In Each room there is a ring circuit and a spur.
My Problem is when i Removed 1 of the...
solavie
Thread
circuit
consumer
power
radialradial circuit
socket
sockets
spur
I recently read an article about the advantages of both the RFC and Radial circuits, after which I must admit that I am more swayed towards the Radial.
What are others thoughts? What do you prefer and why?
just visited a customer who requires a 7.3kw hob connected to replace existing gas hob. Currently has a 2.3kw single oven connected to a 4mm T+E cooker radial (ref method c) Protected by a 32amp MCB
i advised that for the hob to be installed the cooker radial would have to be rewired using 6mm...
Hi all,
Just wondering if anybody knew why the max number of sockets you can have on a radial circuit covered by a 20amp breaker, and fed by 2.5 T&E in order to comply with regs?
Cheers
Had a call out to a home where the RCD keeps tripping when lounge ,dinning and bed room sockets mcb is switched on. Fault traced to one of the legs from the consumer unit to 1st socket 0.2Meg ohm at best. cable size is 2.5mm T&E there are 10 double and 4 single sockets on the circuit. Reg 433.1...
Hi Guys,
I'm not into design etc and never have been really but how do you calculate volt drop on a distribution ring main circuit? Ring circuit say covering a large area supplying various loads/buildings. I was thinking split the ring and work it out as 2 x radial circuits, but 1 radial may...
Morning all, been pondering quite a bit lately about Hybrid circuits,especially 13amp socket circuits, the likes of lolly pop rings etc.
I don't want to get into arguments about the pros and cons and why people install them, that's been done to death, whether, I personally agree with this...
Hi,
I had a nice little job of cutting 20 Australian plugs off appliances etc the other day and replacing with uk plugs...
It occurred to me though, none of them had fuses?..
I have no idea how it works down under and just wondered if someone would kindly tell me why the appliances are not fused.
I went to a job that the owner felt was a bodged job. It was basically a radial circuit wired at the start in 4.0mm T&E, and then it goes to a few sockets that is supplying a washing machine and tumble drier. From there it goes upstairs to the airing cupboard where it feeds a single switched...
Hi all,
Im am soon to be installing 4 double sockets and possible 2 wall lights in a new conservatory.
Was going to extend downstairs ring but a tad awakward and I'm not a lover of junction boxes if they can be avoided. The consumer unit isn't too far so just as easy to install a new circuit...
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.