readings

  1. SparkyChick

    Interesting IR Readings - Any ideas?

    Hi all, Well, this one is interesting and I have absolutely no idea what could be causing this. Just added a PIR to a lighting circuit, very simple, disconnect the lamp and move the feed cables to feed a PIR and then onto the lamp itself. Nice straightforward. Doing my testing for the minor...
  2. Soulsurfer

    Renovated house low r2 readings !

    Just been sorting out a right mess during a house renovation and tests on newly installed ring final are r1 0.35 rn 0.35 & r2 was expecting around 0.58 but had consistently 0.00 Ohms. MFT was zeroed again from scratch and was still giving a zero resistance reading Almost all cable is new and...
  3. D

    high Zs readings

    Did an EICR in a domestic property, earthing arrangement was a TN-S with a Ze of 0.51 ohms. There are 2 ring final circuits protected by 32amp 60898 type B mcbs. Both circuits have additional protection from a 30mA RCD. My Zs readings for the circuits are 1.63 ohms and 1.89 ohms. My question...
  4. telectrix

    code query

    just done a EICR. good installation, approx. 10 years old. 16th ed.split board, lighting circuits non-RCD, on TT earthing. my query is this: the Zs readings are high, due to the high Ze, insofar as , e.g. lighting circuits on 6A MCB each have a Zs higher than the max. permissible . should I...
  5. J

    Insulation resistance testing Lighting circuit

    Hi everyone. I'm looking for advise on how to test IR on commercial lighting. There's so many lights on 1 circuit , do I have to take out all the lamps in all the lights to perform the test or can I simply test between LN -E ? Even though I have spent lots of time testing domestic installs and...
  6. PhilCumbria

    Off peak and standard

    Hi I have just changed both an off-peak CU and a normal CU. I have tested both. Can i put them both on the same cert or do they need to be on two different EIC's ??
  7. R

    what to suggest when no circuits have rcd protection

    I carried out an eicr and no circuits have RCD protection. There are 3 dbs all have federal elec type 3 mcbs in. Would you recommend changing each db and rcd only the sockets or rcbo everything as its all T&E less than 50mm. One db is lighting and power the other is convector heaters and hand...
  8. M

    IR testing result

    Hi all, I have come across an issue that i know others would have..... I done an Insulation resistance test on a lighting circuit with no selv or pelv just regular pendants circuit. Now the customer informed me they had a leak from a bathroom a few months ago and when i tested this particular...
  9. D

    EICR IR bad readings, any advice?!

    Hey, An EICR was under taken again on property. Insulation Resistance results on at 500V. All results in Mega Ohms LIGHTING L-N 34.80, L-E 2.05, N-E 33 LIGHTING L-N 2.47, L-E 2.97, N-E 2.81 UP POWER L-N 78, L-E 72, E-L 69 DOWN SOCKETS L-N 16.30, L-E 15.41 N-E...
  10. R

    Ze

    hi all, I posted about this recently and didn't manage to get back online till now. I've got a Fluke 1653b multi function meter. In the last few weeks it has stopped recording Ze and Zdb readings ( readings on L-E setting) are 0.00 and on L-N reading are0.00 and PFC is 10kA ( this only happens...
  11. P

    Zs Testing Tt

    Hi Guys Job - semi detached with a TT earthing arrangement. I used the Z loop function on my MFT to check the earth at the DB. Reading 164 ohms - ok. Same reading with earth reconnected. However if I do the same test with the Zs RCD function, I get 204 ohms. Why? Do I have a MFT fault? I need...
  12. leep82

    DB change/EICR

    Hi all, yesterday i went to a property to do an EICR in preparation for a DB change next weekend. The existing DB has six circuits, cooker, 2 x rings and 3 x lighting circuits. Bonding to gas and water is in place and adequately sized so providing everything tested out ok a relatively straight...
  13. A

    Very high earth loop readings

    Was out doing some defect repairs on a system with a few high earth loop readings. I had previously been on site and tested the circuits with the high readings. For one of the circuits I had a reading of 1.28 ohms for a C50 t/p mcb it was rather high. So the idea was to remove the mcb and...
  14. P

    Megger MFT1730 2016

    I am thinking about buying the Megger MFT1730, I have read bad reviews (before 2014) on the no trip test and z readings being off. Does anyone know what the 1730 is like now in 2016? is it worth buying? has there been any software upgrades to fix the issues? any info is appreciated
  15. H

    WANTED: Meter Calibration NE

    Best place to get meter calibrated NE (Durham/Newcastle) - any thoughts? It's Metrel if that makes any difference.
  16. J

    Low Insulation resistance readings when connecting final socket on ring?

    Hello All wondering if anyone could shed some light on a problem i have with my IR readings. I recently rewired a house.. took care pulling cables in etc . finished 1st fix, checked cables by looping ring main in connector blocks and doing continuity and IR test . continuity was ok, IR read...
  17. S

    Question regarding my VOC readings

    I've recently purchased 4 Helios 275 watt solar panels. My plan is to run a 48 volt system. 2 panels will be in series and both sets of 2 panels will lead into a combiner box down to my charge controller. Their specs read a VOC of 38 volts. I made the BIG mistake by not initially checking...
  18. B

    earth rod readings.

    I work for a large telecoms company in the UK, and we have a/c power that is supplied by local dno to our street cabinets. part of the stipulation is the earth rod reading should be below 150 ohms. these rods are tested and fitted by contractors, then their electrician does the electrical...
  19. gazdkw82

    Socket tester adapter thingy

    I thought having one of those socket adaptors that allows you to push your testing leads directly in. What's the general consensus? Do they conflict with testing resulting think the one Iv looked at is made by kewtech
  20. B

    Megger readings

    I am planning to Meg a 480 volt 3 phase motor leads to ground using 1000 volts DC. What are acceptable ohm values and when should I be concerned.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock