sockets

  1. Dartlec

    Sockets on a lighting circuit - C3 or C2?

    Fun EICR at an HMO today, which was installed new 5 years ago (not particularly well!) Lots of niggly things that I'll sort, but in the kitchen cupboards were two unswitched sockets which confused me for a while. Turns out they are connected to the lighting circuit, switched by their own...
  2. R

    6mm to 2.5mm for sockets

    Hi I've got a job that i've been asked to quote for and i'm struggling with how to do it the best way. It's a summerhouse and the customer only wants a couple of double sockets and a light in it. My issue is that it's a fair distance from the house where the supply will be taken from. I've...
  3. highlanders317

    Advice for home pc area and extra sockets

    Hi All, I am having fibre to the premises fitted tomorrow, much earlier than expected, supposed to be another month or so. I looking for some advice on what to get to replace the current 1x4 sockets with 3 extension leads for pc, tv and always on. I am not looking doing the work myself, just...
  4. H

    Dedicated double socket or single sockets for washing machine and a tumble dryer.

    Existing double gang socket in the corner of a kitchen on a dedicated 12m length above ceiling 2.5 final circuit to CU, was used for a WM and a tumble dryer protected by a 32amp MCB. I wish to keep this arrangement but on lifting floor boards above ceiling I noted entire run of cable/s was not...
  5. Josh555

    Blowing sockets and popping RCD

    A client asked me to add two sockets in their bedroom I took power from two sockets in the lounge which is behind the bedroom wall. I ran a cable out of each socket for the new socket The problem is it now is tripping the RCD and blowing the old Existing sockets and light switches But the...
  6. D

    Circuit Breaker Tripping - Sockets

    Hi guys, I'm a novice, so be gentle. Ok, I've attached a photo. 1) I've come home to find none of my sockets working. I've checked my circuit breaker box and as expected the 'Sockets' switch is off. 2) I flicked the switch back to 'On' however the main switch to the right will not go to 'On'...
  7. Richardcavell

    Backboxes and power sockets

    Hi. I live near Blackpool in the UK. I don’t know anything about being an electrician. I’m retired. I’ve asked a man who does home improvements to consider doing some work here. We’ve negotiated that I’m going to choose the hardware that gets installed. He is speaking as though he wants to...
  8. brokentechie

    UK Any reason why sockets can't be installed on a horizontal surface?

    As title suggests, is there any regulation that prevents sockets from being installed on a horizontal surface? Think floor sockets but installed on a flat plasterboard surface which forms a recess shelf. For clarification, I'm not doing this myself, I just wanted some information before I go...
  9. N

    Some sockets not working but no fuse blown

    2 sockets in bedroom and 2 in utility room have stopped working. No fuses have blown
  10. spectredubs

    How do I safely use a 16A 250V EU subwoofer at home with UK wall sockets?

    Hi folks, new member here. I am a DJ/electronic music producer with basically zero experience in advanced electronics. I recently bought the Presonus Eris Sub8 subwoofer, I need help using this safely at home. The appliance came with an EU plug (two circular rods) and it says 16A 250V on it...
  11. JamieD93

    Wiring Two Double Sockets

    Hello everyone, Hoping someone can help me! We are currently re-wiring our property in the form of the labour intensive element (wall chasing, installing back boxes etc.) and our family electrician will be connecting everything and installing the new consumer unit later this month (I believe...
  12. R

    UK 13A Sockets keep latching in "on" position

    Hi All, I have a random issue where switches on 13A switched sockets keep latching in the "on" position. Once it happens the sockets are kaput, with the switch contacts fused together. After removing the socket there is no change. This has happened so far on two different circuits. First...
  13. littlespark

    Modular sockets like this one….

    Been asked to fit a few double sockets. In a cupboard, but he wants the same as others in the house… they are unswitched, on numerous radial circuits… (kit house, imported from Germany and assembled here) I can’t find anything similar. ( didn’t take them off to find a maker) Same house. They...
  14. R

    Category for lack of RCD on sockets in 27 year old building

    There is a difference of opinion in that a testing company carrying out an EICR has classed lack of RCD protection as a C2 where I understand this type of fault to be a C3 according to Guidance Notes 3 Table 3.5. Their opinion has been formed in reference to a publication called EICR Code...
  15. Rednblack

    Where can you put sockets in a Utility Room

    Hi everyone, I have recently had an extension built with a new Utility room. The electrician has put the sockets for the washing machine and tumble dryer in the cupboard under the sink. This is fine, except the tumble dryer lead does not reach and is currently plugged in via an extension lead. I...
  16. S

    Cooker supply to 13 amp sockets

    I will shortly be having a range cooker installed that requires 2 x 13 amp supplies. Maximum power required is stated as 3 kW and 2.85 kW respectively. I have a redundant cooker supply on its own circuit, probably 30 amp. I would like to convert this to provide the power for the new cooker. Can...
  17. N

    is there a minimum number of sockets on a radial

    Fault finding today, no continuity on a FRC turns out to be 1 complete leg of the ring is simply not there. cant run new cable in due to decor/tiled floor I was going to split the remaining sockets into 2 radials which would mean 1 radial with 3 sockets and 1 radial with only 1 socket this...
  18. W

    BG Nexus flush sockets

    Anyone ever fitted these sockets? Was fitting them today and the back boxes weren’t straight, was absolutely no play in the sockets what’s so ever.
  19. P

    UK Adding additional sockets

    Hi, Forgive me for my ignorance, I'm looking to add 2 additional double usb sockets under my desk at home, the electrican I have had the quote from said he will wire them off the ring main, as you can only spur once off a socket. Is this safe and within regulations? Also he says that he will be...
  20. J

    Fitting sockets in loft

    Afternoon:) Could anyone tell me the best way to get socket mains into the loft , would it be taking the ring main from the bedroom below? Thanks

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock