Hi everyone...i remember reading on here not so long ago about rcd switched fused spurs not being allowed for an addition to a circuit that didnt have a rcd as the regs now require that when you have an addition to a circuit the whole circuit must be protected not just the addition,,,could...
Good morning all. Got a bit of a problem that is stumping me.
Called to investigate an external light not working. This light is on the same circuit as about 5 other lights and is controlled via a photocell which switches in a contactor to bring all lights on. Every light is working apart from...
Hi everyone,
I have recently replaced 10 old strip lights in a church hall with new LED strip lights.
I ran an insulation test and all seemed good. I switched them on and all seemed good.
I had a call from the vicar to say that they are not working so went back to site to find the MCB had...
hi
This is just a starter because I haven't done any measurements yet (I was a guest there) and what I can do will be restricted as this has never been thought to be a problem by the owner who is a relative, but I'm more concerned than he is by what I've seen.
Background: modern hugely...
I’m replacing old plastic light switches and sockets for metal ones. I’ve gone with BG Nexus range but I’m a little confused as to whether or not I need to connect a wire to the clean earth connection. Looking at the wiring diagram it is not used. I know I need to run a fly lead from the switch...
I have a Dishwasher and Washing Machine (both several years old) both plugged into a 4 way gang. They are on a 16Amp RCD with other appliances also on the same circuit.
When both are turned on at about the same time, about 5 mins after turning on they will both turn off completely, as if they...
I recently purchased a 20 watt led floodlight from b&q to put above my shed door..
Live, neutral and earth all wired up properly to the junction box.
I switch the liget on and everything works fine but when I switch it off the light doesn't not extinguish it just goes dim so obviously it's...
Hi all,
I've had a complete rewire in my house as part of a renovation. I've noticed two things that I wonder if they are in line with regs:
1) the electrician has not put the little bit of brown tape over the blue or black wires that are switched live. Is the brown tape just best practice or...
Hi all, apologies if there is a more appropriate forum, I just can't seem to find a definitive answer!
I have 2 bathrooms, each of which has a mains-wired mirror with lights, shaver socket and demister. Downstairs, the mirror lights etc. only work if the main light is switched on. Upstairs, the...
I’ve got a dishwasher from IKEA (integrated into unit) and it’s under 2 years old.
For the best part of since I’ve had it... when I go to turn it on it will beep (as if it’s picking up on the pressing) but it won’t show anything on the display etc. I have to switch it off at the wall and wait...
Hello all,
Im looking advice. I'm a diy'er. I have just replaced an old double socket and switched fcu with new stainless steel ones. My previous fcu would have the neon light lit, when switched on. My new one has the led lit when either switched on or off. It's lap brand from the screw fix...
Currently pricing up new electrics for a new kitchen. I am not a spark nor do I intend on doing the work - I am simply saving some time and money by speccing exactly what I want prior to getting quotes.
I have the following appliances on dedicated circuits:
Fridge freezer (fed from B20 MCB on...
Hi
I have an led flood light just above the door on my shed. I went out to the shed tonight and as I switched on the LED flood light I noticed that it was acting out a strobe light effect. I switched it off then on again and it was strobing again...
Anyone ever experienced this before and if so...
Hope someone can help, went to replace sensor bulbs (incandescent) with leds when the bulbs went off or switched off they stayed on but with a small glow. I disconnected feed to utility light and lights went off no problem reconnected problem started. Is there a way to fix this problem, thanks...
Hello, my mate’s asked me to look at his spotlights in the kitchen because they were temperamental for a few months going off for hours at a time then coming back on and now they just trip the MCB as soon as switched on. They’re 12v spots.
They were on a dimmer switch so I changed that first to...
This question is purely out of interest, I'm a substation apprentice while we do some LV installation work its not much and no design work fitting only.
But today I've been helping a sparkie friend do some work(just attaching conduit to wall no actually wiring) for local community group.
So...
Hi
We have two alcoves with a downward niche light in each. About 4 years old. Pic attached.
Both operate from one switch. One light is flashing like a strobe when switched on - guess needs replacing?
Appears to be a solid unit rather than containing a bulb that can be replaced.
No obvious way...
Can someone please confirm if a single spur off a ring main is allowed in a kitchen? My plumber has said you cannot have spurs in the kitchen, must all be ring main?
Use: To create an extra socket under the kitchen cabinets, 6" off ground, will be used for single ELV DC Alexa PSU as limited...
I've installed a number of dimmable LED downlights switched two ways. They're switched by one dimmer and a standard rocker.
When they are switched on with the dimmer the lights operate normally and can be dimmed however they seem to override the other switch which will not switch the lights off...
Hi
Are the USB sockets permanently powered irrespective of whether the switch is on?
Anyone done any power measurements on one when nothing is plugged into the usb?
Can they withstand insulation resistance tests? (if so up to what voltage?)