Hi, as an aspiring sparky I'm needing help with the temperature adjustment formula for Zs. I'm using GN3 (17th). I understand that the values given in Appendix A - Table A4 (for BS 60898) are assumed at a test ambient of 10C whereas the values in BS7671 are at the "normal operating temperature"...
I have a solar pv system that has an Iboost fitted to send excess generation to my hot water tank. Combined with my solid fuel back boilers we almost always have hot water.
I also have a cold mains fed 11kW shower - not a power shower. I would like to feed the shower with luke warm water via a...
Hi All,
I'm trying to calculate CCC & VD for H07RN-F Single core cable. Used for event powerlock runs.
TPN AC - Ref Method C - Flat & Touching
Table 4E1A/B covers Single Core 90*C thermosetting insulated cables, which I have used correction factors to convert these values to flexible cable but...
Can anyone give me some clarification on the following.
I am installing some Osram Planon Plus led light panels into a temporary building and have been told the transformers need to housed in an enclosure as they do not have the correct markings for BS7671 "max surface temperature under fault...
So I’ve nearly completed my
“City & Guilds 2365
Level 2 Diploma in Electrical Installations”
I’ve started to study for the electrical science exam and come to a point in the level 2 book where I am stuck and struggling to understand this part.
Can anyone help that isn’t going to judge me and...
I need to source a batten light fitting which sits over a range in a kitchen, in a big commercial extractor hood. Existing fitting has cooked and now failed.
For example, a 3 or 4ft fluorescent or LED batten, the main criteria is that it will survive being over lots of hot & steaming pans every...
Hi all plumber here...
My customer complained about fluctuating temperature at the electric shower so I removed the said shower and replaced with a new one.
They still have the problem, and a neighbour has suggested it may be "something to do with the fuse box"
Is it possible that this could be...
Hi all
I have an electric underfloor heating system in my bathroom with a Timeguard TPT88 controller:
(TPT88 - 24 Hour/7 Day Multi-Programmable Thermostat | Timeguard - http://www.timeguard.com/products/climate/thermolay-ufh-controllers/24hour-7-day-multi-programmable-thermostat)
The system as...
Hello
I'm not sure if this is the correct forum area to post this in, apologies if it isn't...
I've been working through some mock questions on-line, and found myself confused by this:
The measured value of loop impedance for a circuit is 0.83ohm.
If the temperature at the time of the test was...
I'm trying to find out the likely maximum tempertaure that will occur on a chimney breast so I can work out what type and size of cable to use for a socket, and whether I need to move some existing cables. The chimney is granite with a clay liner and will be serving a multi-fuel stove with a...
Hi,
I've posted threads related to this issue quite a few times but never got to the bottom of it, largely because of my own ignorance, but I feel like this thread might be the one!
So, I have a version of this heater: https://www.hennlich.bg/uploads/en_galmatherm.pdf
It's 1kW.
I'm putting...
I've just ordered one of these: https://www.hennlich.bg/uploads/en_galmatherm.pdf
It heats the water in my tank up to 80C in about an hour and a half.
I'd like to be able to have some temperature control, so I can set at 50C, 60C, 70C etc. What's the simplest way of doing that?
I understand that XLPE cables operate at a maximum temperature of 90c compared with 70c for PVC insulation. What I don't understand is why the increased temperature permits a reduction in conductor size if XLPE insulated cables are used in preference to cables having PVC insulation.
If the...
PLW
Thread
cables
conductor
insulation
resistance
temperature
With reference to Voltage Drop calculations and Table F4(ii) OSG page 151.
When designing an installation the cable is selected, among other factors, so that the maximum operating temperature is not exceeded, in this case 6242Y T&E = 70C.
The table, titled "Voltage Drop (per ampere per meter)...
Are dry ceramic wall heaters a modern version of storage heaters, i've just got an old cottage that i'm going to renovate, it has old storage heaters in each room aswell as an open fire (coal type).
There's no gas supply to the area as it's in the country and i didn't want to go down the route...
Hello Can I just confirm that if 90 degree cable is used in switch gear that is only ratted at 70 degrees then you use the 70 degree tables to find the maximum current carrying capacity in this case Table 4D1A
I ask this as I carried out an EICR and found 4mm 6491B cable run in trunking...
Hi All
looking for some advice again.
I got a room in a care home that is reaching 29 degrees C on a day to day basis.
There is an air conditioning unit in there but that is not making any difference.
This room is an internal room with no external walls (with another 2 floors above).
We have...
My dad is an emergency driver. All he has is a dash light that I bought him from amazon last year. Since my dad is an electrician I thought I would get him some blue LEDs so he can make his own lights as he complains about the price of emergency lighting.
JamieJ
Thread
current
diy
flashing
forward
light
lights
reverse
temperature
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.